Hello Julian,

providing the complete connection string the error is still present:

karaf@root()> plc4x:read modbus modbus:tcp://192.168.70.73 coil:1


Find driver service: Modbus
Error executing command: Unsupported transport tcp

During the other test, for example running a local class, the string
without the transport code works flawlessly.

Greetings,
Alessio


On Thu, Jun 11, 2020 at 1:05 PM Julian Feinauer <
[email protected]> wrote:

> I guess its in your config. If I remember correctly you have to state the
> transport layer.
> So in your case:
>
> Modbus:tcp://xxx
>
> Does that help?
>
> Am 11.06.20, 12:13 schrieb "Alessio Bernesco Làvore" <
> [email protected]>:
>
>     Thank you very much Cesar for your insight and your detailed
> explanation,
>     much appreciated.
>     I've used your feature to enable your example and my works, now they
> both
>     find the Modbus driver and all the flow seems clear to me.
>
>     Running your command, but also running my test using an activator,
> there's
>     a transport error:
>
>     karaf@root()> plc4x:read modbus modbus://192.168.70.73 coil:1
>
>
>     Find driver service: Modbus
>     Error executing command: Unsupported transport tcp
>
>     I cannot understand if it's still related to a misconfiguration on my
> side
>     or with the driver.
>
>     Greetings,
>     Alessio
>
>
>
>
>     On Wed, Jun 10, 2020 at 8:25 AM Cesar Garcia <[email protected]
> >
>     wrote:
>
>     >  Hello Alessio,
>     >
>     > As I pointed out, with the new design of the drivers it is necessary
> to
>     > make a few modifications so that the system allows communication
> with the
>     > OSGi container.
>     >
>     > In a default installation, the load of services in the SPI services
> are not
>     > seen between the different bundles, and that is the problem that is
>     > happening to you and, as Julian pointed out in his email, the Apache
> Aries
>     > Fly project solves it.
>     >
>     > By default Karaf does not integrate the Aries Fly project (although
> the
>     > page indicates that it does), it can be added in a feature or you can
>     > generate your own version of Karaf (I always start from a minimal
>     > installation), so I complement the feature you published  and you
> can see
>     > in[1].
>     >
>     > Now each service / consumer must indicate within the manifest the
> methods
>     > that it export or import as appropriate. In your case you need to
> specify
>     > the transport services, specifically "PLC4J: Transports: TCP" and the
>     > consumer "PLC4J: SPI", which are what cause the problem.
> Modifications in
>     > [2] and [3] are made in the POMs.
>     >
>     > At this point you should already see the transport and the
> registered by
>     > spifly like in [4].
>     >
>     > Well, here you can already use PLC4X in your bundle, in [5] leave an
>     > example code, creating a Karaf command with which you can access the
> Modbus
>     > or S7 driver indifferently (Just test the Modbus).
>     >
>     > This could somehow be treated as a PR for the project, it should be
>     > evaluated.
>     >
>     > My grain of sand.
>     >
>     > 1. The feature
>     >
>     >     <feature name='${project.artifactId}' description='${
> project.name}'
>     > version='${project.version}'>
>     >         <details>${project.description}</details>
>     >         <details>Implementation of the protocol adapters for usage
> as Java
>     > library.</details>
>     >
>  <bundle>mvn:org.apache.plc4x/plc4j-osgi/0.8.0-SNAPSHOT</bundle>
>     >         <bundle>mvn:org.osgi/osgi.core/6.0.0</bundle>
>     >
>  <bundle>mvn:org.apache.plc4x/plc4j-api/0.8.0-SNAPSHOT</bundle>
>     >
>  <bundle>mvn:org.apache.plc4x/plc4j-spi/0.8.0-SNAPSHOT</bundle>
>     >         <bundle>mvn:io.netty/netty-codec/4.1.47.Final</bundle>
>     >         <bundle>mvn:io.netty/netty-common/4.1.47.Final</bundle>
>     >         <bundle>mvn:io.netty/netty-transport/4.1.47.Final</bundle>
>     >         <bundle>mvn:io.netty/netty-resolver/4.1.47.Final</bundle>
>     >
>  <bundle>mvn:commons-beanutils/commons-beanutils/1.9.4</bundle>
>     >         <bundle>mvn:commons-logging/commons-logging/1.2</bundle>
>     >
>  <bundle>mvn:commons-collections/commons-collections/3.2.2</bundle>
>     >         <bundle>mvn:com.github.jinahya/bit-io/1.4.3</bundle>
>     >         <bundle>mvn:commons-codec/commons-codec/1.12</bundle>
>     >
>     > <bundle>mvn:org.apache.plc4x/plc4j-driver-s7/0.8.0-SNAPSHOT</bundle>
>     >
>     >
>     >
> <bundle>mvn:org.apache.plc4x/plc4j-driver-modbus/0.8.0-SNAPSHOT</bundle>
>     >
>     >
>     >
> <bundle>mvn:org.apache.plc4x/plc4j-transport-tcp/0.8.0-SNAPSHOT</bundle>
>     >
>     >
>     >
> <bundle>mvn:com.fasterxml.jackson.core/jackson-annotations/2.10.0</bundle>
>     >         <bundle>mvn:org.apache.commons/commons-lang3/3.9</bundle>
>     >         <bundle>mvn:io.netty/netty-buffer/4.1.47.Final</bundle>
>     >         <bundle>mvn:io.vavr/vavr/0.10.2</bundle>
>     >         <bundle>mvn:io.vavr/vavr-match/0.10.2</bundle>
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     >
>     > *        <bundle>mvn:org.ow2.asm/asm/8.0.1</bundle>
>     > <bundle>mvn:org.ow2.asm/asm-util/8.0.1</bundle>
>     > <bundle>mvn:org.ow2.asm/asm-tree/8.0.1</bundle>
>     > <bundle>mvn:org.ow2.asm/asm-commons/8.0.1</bundle>
>     > <bundle>mvn:org.ow2.asm/asm-analysis/8.0.1</bundle>        <!--
>     > <bundle>mvn:biz.aQute.bnd/aQute.libg/5.0.1</bundle>
>     > <bundle>mvn:biz.aQute.bnd/biz.aQute.bndlib/5.0.1</bundle>        -->
>     >
>     >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.weaver-internal/1.3.0</bundle>
>     >
>     >
>     >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.core-internal/1.3.0</bundle>
>     >
>     >
>     >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.dynamic.bundle/1.3.0</bundle>
>     >      *
>     >
>     >     </feature>
>     >
>     > [2] "PLC4J: Transports: TCP"
>     >
>     >       <plugin>
>     >         <groupId>org.apache.felix</groupId>
>     >         <artifactId>maven-bundle-plugin</artifactId>
>     >         <extensions>true</extensions>
>     >         <configuration>
>     >           <instructions>
>     >
>     >
>     >
> <Bundle-SymbolicName>${project.groupId}.${project.artifactId}</Bundle-SymbolicName>
>     >
>     >
>     >
> <Bundle-Activator>org.apache.plc4x.java.osgi.TransportActivator</Bundle-Activator>
>     >
>     >
>     >
> <Export-Service>org.apache.plc4x.java.spi.transport.Transport,org.apache.plc4x.java.transport.tcp.TcpTransport</Export-Service>
>     >            * <SPI-Provider>*</SPI-Provider>*
>     >           </instructions>
>     >         </configuration>
>     >       </plugin>
>     >
>     > [3] "PLC4J: SPI"
>     >       <plugin>
>     >         <groupId>org.apache.felix</groupId>
>     >         <artifactId>maven-bundle-plugin</artifactId>
>     >         <extensions>true</extensions>
>     >         <configuration>
>     >           <instructions>
>     >             <Export-package>io.netty.bootstrap,*</Export-package>
>     >             *<SPI-consumer>*</SPI-consumer>*
>     >           </instructions>
>     >         </configuration>
>     >       </plugin>
>     >     </plugins>
>     >
>     > [4] karaf@root()> service:list Transport
>     > [org.apache.plc4x.java.spi.transport.Transport]
>     > -----------------------------------------------
>     >  org.apache.plc4x.transport.code = tcp
>     >  org.apache.plc4x.transport.name = IP/TCP Transport
>     >  service.bundleid = 89
>     >  service.id = 207
>     >  service.scope = singleton
>     > Provided by :
>     >  PLC4J: Transports: TCP (89)
>     > Used by:
>     >  TestPLC4XOsgiWay Blueprint Bundle (51)
>     >
>     > [org.apache.plc4x.java.spi.transport.Transport]
>     > -----------------------------------------------
>     >  .org.apache.aries.spifly.provider.discovery.mode =
> SPI_PROVIDER_HEADER
>     >  .org.apache.aries.spifly.provider.implclass =
>     > org.apache.plc4x.java.transport.tcp.TcpTransport
>     >  service.bundleid = 89
>     >  service.id = 208
>     >  service.scope = bundle
>     >  serviceloader.mediator = 45
>     > Provided by :
>     >  PLC4J: Transports: TCP (89)
>     >
>     > [5] *https://github.com/glcj/TestPLC4X <
> https://github.com/glcj/TestPLC4X
>     > >*
>     >
>     >
>     > El mar., 9 jun. 2020 a las 5:23, Alessio Bernesco Làvore (<
>     > [email protected]>) escribió:
>     >
>     > > Thank you Cesar,
>     > > thanks for your insight, but i think i'm still lost somewhere.
>     > >
>     > > I've registered the driver inside my bundle context, at least i
> think so:
>     > >
>     > > [org.apache.plc4x.java.api.PlcDriver]
>     > > -------------------------------------
>     > >  org.apache.plc4x.driver.code = modbus
>     > >  org.apache.plc4x.driver.name = Modbus
>     > >  service.bundleid = 165
>     > >  service.id = 247
>     > >  service.scope = singleton
>     > > Provided by :
>     > >  PLC4J: Driver: Modbus (165)
>     > > Used by:
>     > >  edgecontroller Bundle (164) <--
>     > >
>     > > Anyway starting the bundle the PLC Driver Manager is unable to
> find the
>     > > driver:
>     > >
>     > > 2020-06-09T09:17:50,132 | INFO  | pipe-bundle:update
> edgecontroller |
>     > > PlcDriverManager                 | 152 -
> org.apache.plc4x.plc4j-api -
>     > > 0.8.0.SNAPSHOT | Instantiating new PLC Driver Manager with class
> loader
>     > > sun.misc.Launcher$AppClassLoader@764c12b6
>     > > 2020-06-09T09:17:50,132 | INFO  | pipe-bundle:update
> edgecontroller |
>     > > PlcDriverManager                 | 152 -
> org.apache.plc4x.plc4j-api -
>     > > 0.8.0.SNAPSHOT | Registering available drivers...
>     > > 2020-06-09T09:17:50,133 | ERROR | pipe-bundle:update
> edgecontroller |
>     > > Activator                        | 164 - edgecontroller - 1.0.0 |
> Unable
>     > to
>     > > find driver for protocol 'modbus'
>     > >
>     > > Greetings,
>     > > Alessio
>     > >
>     > > On Mon, Jun 8, 2020 at 10:52 PM Cesar Garcia <
> [email protected]>
>     > > wrote:
>     > >
>     > > >  Hello Alessio,
>     > > >
>     > > > Perform the test with the "feature" that you put online, and I
> can see
>     > > that
>     > > > the services associated with the drivers are active.
>     > > >
>     > > > karaf@root()> service:list PlcDriver
>     > > > [org.apache.plc4x.java.api.PlcDriver]
>     > > > -------------------------------------
>     > > >  org.apache.plc4x.driver.code = modbus
>     > > >  org.apache.plc4x.driver.name = Modbus
>     > > >  service.bundleid = 59
>     > > >  service.id = 98
>     > > >  service.scope = singleton
>     > > > Provided by :
>     > > >  PLC4J: Driver: Modbus (59)
>     > > >
>     > > > [org.apache.plc4x.java.api.PlcDriver]
>     > > > -------------------------------------
>     > > >  org.apache.plc4x.driver.code = s7
>     > > >  org.apache.plc4x.driver.name = Siemens S7 (Basic)
>     > > >  service.bundleid = 60
>     > > >  service.id = 97
>     > > >  service.scope = singleton
>     > > > Provided by :
>     > > >  PLC4J: Driver: S7 (Step7) (60)
>     > > >
>     > > > The solution is to use the "BundleContext" with a filter and
> take the
>     > > field
>     > > > "org.apache.plc4x.driver.name " or  the field
>     > > > "org.apache.plc4x.driver.code" ( They are the same ). I think
> that is
>     > the
>     > > > way to do it in an OSGi environment.
>     > > >
>     > > > Loading the services with SPI is redundant, and it may happen
> that the
>     > > SPI
>     > > > service does not see the PlcDriver Services (typical OSGi
> problem).
>     > > >
>     > > > My grain of sand,
>     > > >
>     > > > Best regards,
>     > > >
>     > > >
>     > > >
>     > > >
>     > > > El lun., 8 jun. 2020 a las 15:41, Alessio Bernesco Làvore (<
>     > > > [email protected]>) escribió:
>     > > >
>     > > > > Thank you Julian,
>     > > > > i've tried to install th Aries SPI Bundle:
>     > > > >
>     > > > > 176 │ Active   │  80 │ 1.3.0              │ Apache Aries SPI
> Fly
>     > > Dynamic
>     > > > > Weaving Bundle
>     > > > >
>     > > > > But i'm still unable to resolve the drivers.
>     > > > >
>     > > > > Ale
>     > > > >
>     > > > > On Mon, Jun 8, 2020 at 8:13 PM Julian Feinauer <
>     > > > > [email protected]>
>     > > > > wrote:
>     > > > >
>     > > > > > Hi Alessio,
>     > > > > >
>     > > > > > if I remember correctly you need the Aries SPI Fly package
> loaded.
>     > > > > > In Plain PLC4X we use ServiceLoader to discover drivers.
>     > > > > > If you have nothing like Aries SPI Fly which mediates and
>     > "immitates"
>     > > > the
>     > > > > > ServiceLoader then you dont get a wiring between the
> DriverManager
>     > > and
>     > > > > the
>     > > > > > driver.
>     > > > > > But I don’t checked the lastst implementation to be honest.
>     > > > > >
>     > > > > > Perhaps @Robinet, Etienne can help?
>     > > > > >
>     > > > > > Julian
>     > > > > >
>     > > > > > Am 08.06.20, 20:00 schrieb "Alessio Bernesco Làvore" <
>     > > > > > [email protected]>:
>     > > > > >
>     > > > > >     Hello everyone,
>     > > > > >     i've created a simple class reading values from a ModBus
> PLC.
>     > > > > >
>     > > > > >     I'm trying to use it inside Karaf, but at start the
> class is
>     > > unable
>     > > > > to
>     > > > > > find
>     > > > > >     the modbus driver. I've compiled and installed in Karaf
> the
>     > > > > >     "driver-s7-feature", with added the modbus driver:
>     > > > > >
>     > > > > >     <?xml version="1.0" encoding="UTF-8" standalone="yes"?>
>     > > > > >     <features xmlns="
> http://karaf.apache.org/xmlns/features/v1.6.0
>     > "
>     > > > > >     name="driver-s7-feature">
>     > > > > >         <feature name="driver-s7-feature" description="PLC4J:
>     > > > > > Karaf-Features:
>     > > > > >     S7" version="0.8.0.SNAPSHOT">
>     > > > > >             <details>Implementation of the protocol adapters
> for
>     > > usage
>     > > > as
>     > > > > > Java
>     > > > > >     library.</details>
>     > > > > >
>     > > > >
> <bundle>mvn:org.apache.plc4x/plc4j-osgi/0.8.0-SNAPSHOT</bundle>
>     > > > > >             <bundle>mvn:org.osgi/osgi.core/6.0.0</bundle>
>     > > > > >
>     > > > >  <bundle>mvn:org.apache.plc4x/plc4j-api/0.8.0-SNAPSHOT</bundle>
>     > > > > >
>     > > > >  <bundle>mvn:org.apache.plc4x/plc4j-spi/0.8.0-SNAPSHOT</bundle>
>     > > > > >
>  <bundle>mvn:io.netty/netty-codec/4.1.47.Final</bundle>
>     > > > > >
>  <bundle>mvn:io.netty/netty-common/4.1.47.Final</bundle>
>     > > > > >
>     > >  <bundle>mvn:io.netty/netty-transport/4.1.47.Final</bundle>
>     > > > > >
>     >  <bundle>mvn:io.netty/netty-resolver/4.1.47.Final</bundle>
>     > > > > >
>     > > > >  <bundle>mvn:commons-beanutils/commons-beanutils/1.9.4</bundle>
>     > > > > >
>     >  <bundle>mvn:commons-logging/commons-logging/1.2</bundle>
>     > > > > >
>     > > > > >
> <bundle>mvn:commons-collections/commons-collections/3.2.2</bundle>
>     > > > > >
>  <bundle>mvn:com.github.jinahya/bit-io/1.4.3</bundle>
>     > > > > >
>  <bundle>mvn:commons-codec/commons-codec/1.12</bundle>
>     > > > > >
>     > > > > >
>     > <bundle>mvn:org.apache.plc4x/plc4j-driver-s7/0.8.0-SNAPSHOT</bundle>
>     > > > > >
>     > > > > >
>     > > > > >
>     > > >
>     >
> <bundle>mvn:org.apache.plc4x/plc4j-driver-modbus/0.8.0-SNAPSHOT</bundle>
>     > > > > >
>     > > > > >
>     > > > > >
>     > > >
>     >
> <bundle>mvn:org.apache.plc4x/plc4j-transport-tcp/0.8.0-SNAPSHOT</bundle>
>     > > > > >
>     > > > > >
>     > > > > >
>     > > > >
>     > > >
>     > >
>     >
> <bundle>mvn:com.fasterxml.jackson.core/jackson-annotations/2.10.0</bundle>
>     > > > > >
>     >  <bundle>mvn:org.apache.commons/commons-lang3/3.9</bundle>
>     > > > > >
>  <bundle>mvn:io.netty/netty-buffer/4.1.47.Final</bundle>
>     > > > > >             <bundle>mvn:io.vavr/vavr/0.10.2</bundle>
>     > > > > >             <bundle>mvn:io.vavr/vavr-match/0.10.2</bundle>
>     > > > > >         </feature>
>     > > > > >     </features>
>     > > > > >
>     > > > > >     Inside Karaf i can find all the active bundles:
>     > > > > >
>     > > > > >     152 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J: API
>     > > > > >     153 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J:
> Driver: S7
>     > > > (Step7)
>     > > > > >     154 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J: OSGi
>     > > > > >     155 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J: SPI
>     > > > > >     156 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J:
> Transports:
>     > > TCP
>     > > > > >     157 │ Active   │  80 │ 6.0.0.201403061837 │ osgi.core
>     > > > > >     164 │ Active   │  80 │ 1.0                │
> edgecontroller
>     > Bundle
>     > > > > >     165 │ Active   │  80 │ 0.8.0.SNAPSHOT     │ PLC4J:
> Driver:
>     > Modbus
>     > > > > >
>     > > > > >     Anyway at startup the bundle doesnt find any driver:
>     > > > > >
>     > > > > >     2020-06-08T17:47:43,391 | INFO  | FelixStartLevel  |
>     > > > PlcDriverManager
>     > > > > >               | 152 - org.apache.plc4x.plc4j-api -
> 0.8.0.SNAPSHOT |
>     > > > > >     Instantiating new PLC Driver Manager with class loader
>     > > > > >     sun.misc.Launcher$AppClassLoader@764c12b6
>     > > > > >     2020-06-08T17:47:43,391 | INFO  | FelixStartLevel  |
>     > > > PlcDriverManager
>     > > > > >               | 152 - org.apache.plc4x.plc4j-api -
> 0.8.0.SNAPSHOT |
>     > > > > > Registering
>     > > > > >     available drivers...
>     > > > > >     2020-06-08T17:47:43,392 | ERROR | FelixStartLevel  |
> Activator
>     > > > > >                | 164 - edgecontroller - 1.0.0 | Unable to
> find
>     > driver
>     > > > for
>     > > > > >     protocol 'modbus'
>     > > > > >
>     > > > > >     edgecontroller is my bundle, looking at the Karaf log the
>     > > > > > PlcDriverManager
>     > > > > >     is unable to find any driver.
>     > > > > >
>     > > > > >     I cannot understand were i'm failing, could anyone
> provide some
>     > > > > > insight?
>     > > > > >
>     > > > > >     Thank you,
>     > > > > >     Ale
>     > > > > >
>     > > > > >
>     > > > >
>     > > >
>     > > >
>     > > > --
>     > > > *CEOS Automatización, C.A.*
>     > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
>     > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
>     > > >
>     > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
>     > > > *Ing. César García*
>     > > >
>     > > > *Cel: +58 414-760.98.95*
>     > > >
>     > > > *Hotline Técnica SIEMENS: 0800 1005080*
>     > > >
>     > > > *Email: [email protected]
>     > > > <[email protected]>*
>     > > >
>     > >
>     >
>     >
>     > --
>     > *CEOS Automatización, C.A.*
>     > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
>     > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
>     >
>     > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
>     > *Ing. César García*
>     >
>     > *Cel: +58 414-760.98.95*
>     >
>     > *Hotline Técnica SIEMENS: 0800 1005080*
>     >
>     > *Email: [email protected]
>     > <[email protected]>*
>     >
>
>

Reply via email to