Hello Alessio,
If the problem is in Karaf, you probably aren't doing a clean boot, so you
should be using the unmodified version as noted in the previous post.
1. Make sure you compiled the PLC4X project with the modification in clean
form ("> mvn clean install -DskipTests").
2. Perform a clean boot of Karaf, or preferably delete the "data" and
"system" directories of your installation and run "> karaf clean"
3. Install the feature and your application.
4. If it fails you should verify that your Maven installation uses
SNAPSHOTs only from your local repository.
At this point It should work,
I'll be waiting for your confirmation,
Best regards,
El jue., 11 jun. 2020 a las 7:27, Alessio Bernesco Làvore (<
[email protected]>) escribió:
> Hello Julian,
>
> providing the complete connection string the error is still present:
>
> karaf@root()> plc4x:read modbus modbus:tcp://192.168.70.73 coil:1
>
>
> Find driver service: Modbus
> Error executing command: Unsupported transport tcp
>
> During the other test, for example running a local class, the string
> without the transport code works flawlessly.
>
> Greetings,
> Alessio
>
>
> On Thu, Jun 11, 2020 at 1:05 PM Julian Feinauer <
> [email protected]> wrote:
>
> > I guess its in your config. If I remember correctly you have to state the
> > transport layer.
> > So in your case:
> >
> > Modbus:tcp://xxx
> >
> > Does that help?
> >
> > Am 11.06.20, 12:13 schrieb "Alessio Bernesco Làvore" <
> > [email protected]>:
> >
> > Thank you very much Cesar for your insight and your detailed
> > explanation,
> > much appreciated.
> > I've used your feature to enable your example and my works, now they
> > both
> > find the Modbus driver and all the flow seems clear to me.
> >
> > Running your command, but also running my test using an activator,
> > there's
> > a transport error:
> >
> > karaf@root()> plc4x:read modbus modbus://192.168.70.73 coil:1
> >
> >
> > Find driver service: Modbus
> > Error executing command: Unsupported transport tcp
> >
> > I cannot understand if it's still related to a misconfiguration on my
> > side
> > or with the driver.
> >
> > Greetings,
> > Alessio
> >
> >
> >
> >
> > On Wed, Jun 10, 2020 at 8:25 AM Cesar Garcia <
> [email protected]
> > >
> > wrote:
> >
> > > Hello Alessio,
> > >
> > > As I pointed out, with the new design of the drivers it is
> necessary
> > to
> > > make a few modifications so that the system allows communication
> > with the
> > > OSGi container.
> > >
> > > In a default installation, the load of services in the SPI services
> > are not
> > > seen between the different bundles, and that is the problem that is
> > > happening to you and, as Julian pointed out in his email, the
> Apache
> > Aries
> > > Fly project solves it.
> > >
> > > By default Karaf does not integrate the Aries Fly project (although
> > the
> > > page indicates that it does), it can be added in a feature or you
> can
> > > generate your own version of Karaf (I always start from a minimal
> > > installation), so I complement the feature you published and you
> > can see
> > > in[1].
> > >
> > > Now each service / consumer must indicate within the manifest the
> > methods
> > > that it export or import as appropriate. In your case you need to
> > specify
> > > the transport services, specifically "PLC4J: Transports: TCP" and
> the
> > > consumer "PLC4J: SPI", which are what cause the problem.
> > Modifications in
> > > [2] and [3] are made in the POMs.
> > >
> > > At this point you should already see the transport and the
> > registered by
> > > spifly like in [4].
> > >
> > > Well, here you can already use PLC4X in your bundle, in [5] leave
> an
> > > example code, creating a Karaf command with which you can access
> the
> > Modbus
> > > or S7 driver indifferently (Just test the Modbus).
> > >
> > > This could somehow be treated as a PR for the project, it should be
> > > evaluated.
> > >
> > > My grain of sand.
> > >
> > > 1. The feature
> > >
> > > <feature name='${project.artifactId}' description='${
> > project.name}'
> > > version='${project.version}'>
> > > <details>${project.description}</details>
> > > <details>Implementation of the protocol adapters for usage
> > as Java
> > > library.</details>
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-osgi/0.8.0-SNAPSHOT</bundle>
> > > <bundle>mvn:org.osgi/osgi.core/6.0.0</bundle>
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-api/0.8.0-SNAPSHOT</bundle>
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-spi/0.8.0-SNAPSHOT</bundle>
> > > <bundle>mvn:io.netty/netty-codec/4.1.47.Final</bundle>
> > > <bundle>mvn:io.netty/netty-common/4.1.47.Final</bundle>
> > > <bundle>mvn:io.netty/netty-transport/4.1.47.Final</bundle>
> > > <bundle>mvn:io.netty/netty-resolver/4.1.47.Final</bundle>
> > >
> > <bundle>mvn:commons-beanutils/commons-beanutils/1.9.4</bundle>
> > > <bundle>mvn:commons-logging/commons-logging/1.2</bundle>
> > >
> > <bundle>mvn:commons-collections/commons-collections/3.2.2</bundle>
> > > <bundle>mvn:com.github.jinahya/bit-io/1.4.3</bundle>
> > > <bundle>mvn:commons-codec/commons-codec/1.12</bundle>
> > >
> > >
> <bundle>mvn:org.apache.plc4x/plc4j-driver-s7/0.8.0-SNAPSHOT</bundle>
> > >
> > >
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-driver-modbus/0.8.0-SNAPSHOT</bundle>
> > >
> > >
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-transport-tcp/0.8.0-SNAPSHOT</bundle>
> > >
> > >
> > >
> >
> <bundle>mvn:com.fasterxml.jackson.core/jackson-annotations/2.10.0</bundle>
> > > <bundle>mvn:org.apache.commons/commons-lang3/3.9</bundle>
> > > <bundle>mvn:io.netty/netty-buffer/4.1.47.Final</bundle>
> > > <bundle>mvn:io.vavr/vavr/0.10.2</bundle>
> > > <bundle>mvn:io.vavr/vavr-match/0.10.2</bundle>
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > >
> > > * <bundle>mvn:org.ow2.asm/asm/8.0.1</bundle>
> > > <bundle>mvn:org.ow2.asm/asm-util/8.0.1</bundle>
> > > <bundle>mvn:org.ow2.asm/asm-tree/8.0.1</bundle>
> > > <bundle>mvn:org.ow2.asm/asm-commons/8.0.1</bundle>
> > > <bundle>mvn:org.ow2.asm/asm-analysis/8.0.1</bundle> <!--
> > > <bundle>mvn:biz.aQute.bnd/aQute.libg/5.0.1</bundle>
> > > <bundle>mvn:biz.aQute.bnd/biz.aQute.bndlib/5.0.1</bundle>
> -->
> > >
> > >
> >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.weaver-internal/1.3.0</bundle>
> > >
> > >
> > >
> >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.core-internal/1.3.0</bundle>
> > >
> > >
> > >
> >
> <bundle>mvn:org.apache.aries.spifly/org.apache.aries.spifly.dynamic.bundle/1.3.0</bundle>
> > > *
> > >
> > > </feature>
> > >
> > > [2] "PLC4J: Transports: TCP"
> > >
> > > <plugin>
> > > <groupId>org.apache.felix</groupId>
> > > <artifactId>maven-bundle-plugin</artifactId>
> > > <extensions>true</extensions>
> > > <configuration>
> > > <instructions>
> > >
> > >
> > >
> >
> <Bundle-SymbolicName>${project.groupId}.${project.artifactId}</Bundle-SymbolicName>
> > >
> > >
> > >
> >
> <Bundle-Activator>org.apache.plc4x.java.osgi.TransportActivator</Bundle-Activator>
> > >
> > >
> > >
> >
> <Export-Service>org.apache.plc4x.java.spi.transport.Transport,org.apache.plc4x.java.transport.tcp.TcpTransport</Export-Service>
> > > * <SPI-Provider>*</SPI-Provider>*
> > > </instructions>
> > > </configuration>
> > > </plugin>
> > >
> > > [3] "PLC4J: SPI"
> > > <plugin>
> > > <groupId>org.apache.felix</groupId>
> > > <artifactId>maven-bundle-plugin</artifactId>
> > > <extensions>true</extensions>
> > > <configuration>
> > > <instructions>
> > > <Export-package>io.netty.bootstrap,*</Export-package>
> > > *<SPI-consumer>*</SPI-consumer>*
> > > </instructions>
> > > </configuration>
> > > </plugin>
> > > </plugins>
> > >
> > > [4] karaf@root()> service:list Transport
> > > [org.apache.plc4x.java.spi.transport.Transport]
> > > -----------------------------------------------
> > > org.apache.plc4x.transport.code = tcp
> > > org.apache.plc4x.transport.name = IP/TCP Transport
> > > service.bundleid = 89
> > > service.id = 207
> > > service.scope = singleton
> > > Provided by :
> > > PLC4J: Transports: TCP (89)
> > > Used by:
> > > TestPLC4XOsgiWay Blueprint Bundle (51)
> > >
> > > [org.apache.plc4x.java.spi.transport.Transport]
> > > -----------------------------------------------
> > > .org.apache.aries.spifly.provider.discovery.mode =
> > SPI_PROVIDER_HEADER
> > > .org.apache.aries.spifly.provider.implclass =
> > > org.apache.plc4x.java.transport.tcp.TcpTransport
> > > service.bundleid = 89
> > > service.id = 208
> > > service.scope = bundle
> > > serviceloader.mediator = 45
> > > Provided by :
> > > PLC4J: Transports: TCP (89)
> > >
> > > [5] *https://github.com/glcj/TestPLC4X <
> > https://github.com/glcj/TestPLC4X
> > > >*
> > >
> > >
> > > El mar., 9 jun. 2020 a las 5:23, Alessio Bernesco Làvore (<
> > > [email protected]>) escribió:
> > >
> > > > Thank you Cesar,
> > > > thanks for your insight, but i think i'm still lost somewhere.
> > > >
> > > > I've registered the driver inside my bundle context, at least i
> > think so:
> > > >
> > > > [org.apache.plc4x.java.api.PlcDriver]
> > > > -------------------------------------
> > > > org.apache.plc4x.driver.code = modbus
> > > > org.apache.plc4x.driver.name = Modbus
> > > > service.bundleid = 165
> > > > service.id = 247
> > > > service.scope = singleton
> > > > Provided by :
> > > > PLC4J: Driver: Modbus (165)
> > > > Used by:
> > > > edgecontroller Bundle (164) <--
> > > >
> > > > Anyway starting the bundle the PLC Driver Manager is unable to
> > find the
> > > > driver:
> > > >
> > > > 2020-06-09T09:17:50,132 | INFO | pipe-bundle:update
> > edgecontroller |
> > > > PlcDriverManager | 152 -
> > org.apache.plc4x.plc4j-api -
> > > > 0.8.0.SNAPSHOT | Instantiating new PLC Driver Manager with class
> > loader
> > > > sun.misc.Launcher$AppClassLoader@764c12b6
> > > > 2020-06-09T09:17:50,132 | INFO | pipe-bundle:update
> > edgecontroller |
> > > > PlcDriverManager | 152 -
> > org.apache.plc4x.plc4j-api -
> > > > 0.8.0.SNAPSHOT | Registering available drivers...
> > > > 2020-06-09T09:17:50,133 | ERROR | pipe-bundle:update
> > edgecontroller |
> > > > Activator | 164 - edgecontroller - 1.0.0 |
> > Unable
> > > to
> > > > find driver for protocol 'modbus'
> > > >
> > > > Greetings,
> > > > Alessio
> > > >
> > > > On Mon, Jun 8, 2020 at 10:52 PM Cesar Garcia <
> > [email protected]>
> > > > wrote:
> > > >
> > > > > Hello Alessio,
> > > > >
> > > > > Perform the test with the "feature" that you put online, and I
> > can see
> > > > that
> > > > > the services associated with the drivers are active.
> > > > >
> > > > > karaf@root()> service:list PlcDriver
> > > > > [org.apache.plc4x.java.api.PlcDriver]
> > > > > -------------------------------------
> > > > > org.apache.plc4x.driver.code = modbus
> > > > > org.apache.plc4x.driver.name = Modbus
> > > > > service.bundleid = 59
> > > > > service.id = 98
> > > > > service.scope = singleton
> > > > > Provided by :
> > > > > PLC4J: Driver: Modbus (59)
> > > > >
> > > > > [org.apache.plc4x.java.api.PlcDriver]
> > > > > -------------------------------------
> > > > > org.apache.plc4x.driver.code = s7
> > > > > org.apache.plc4x.driver.name = Siemens S7 (Basic)
> > > > > service.bundleid = 60
> > > > > service.id = 97
> > > > > service.scope = singleton
> > > > > Provided by :
> > > > > PLC4J: Driver: S7 (Step7) (60)
> > > > >
> > > > > The solution is to use the "BundleContext" with a filter and
> > take the
> > > > field
> > > > > "org.apache.plc4x.driver.name " or the field
> > > > > "org.apache.plc4x.driver.code" ( They are the same ). I think
> > that is
> > > the
> > > > > way to do it in an OSGi environment.
> > > > >
> > > > > Loading the services with SPI is redundant, and it may happen
> > that the
> > > > SPI
> > > > > service does not see the PlcDriver Services (typical OSGi
> > problem).
> > > > >
> > > > > My grain of sand,
> > > > >
> > > > > Best regards,
> > > > >
> > > > >
> > > > >
> > > > >
> > > > > El lun., 8 jun. 2020 a las 15:41, Alessio Bernesco Làvore (<
> > > > > [email protected]>) escribió:
> > > > >
> > > > > > Thank you Julian,
> > > > > > i've tried to install th Aries SPI Bundle:
> > > > > >
> > > > > > 176 │ Active │ 80 │ 1.3.0 │ Apache Aries SPI
> > Fly
> > > > Dynamic
> > > > > > Weaving Bundle
> > > > > >
> > > > > > But i'm still unable to resolve the drivers.
> > > > > >
> > > > > > Ale
> > > > > >
> > > > > > On Mon, Jun 8, 2020 at 8:13 PM Julian Feinauer <
> > > > > > [email protected]>
> > > > > > wrote:
> > > > > >
> > > > > > > Hi Alessio,
> > > > > > >
> > > > > > > if I remember correctly you need the Aries SPI Fly package
> > loaded.
> > > > > > > In Plain PLC4X we use ServiceLoader to discover drivers.
> > > > > > > If you have nothing like Aries SPI Fly which mediates and
> > > "immitates"
> > > > > the
> > > > > > > ServiceLoader then you dont get a wiring between the
> > DriverManager
> > > > and
> > > > > > the
> > > > > > > driver.
> > > > > > > But I don’t checked the lastst implementation to be honest.
> > > > > > >
> > > > > > > Perhaps @Robinet, Etienne can help?
> > > > > > >
> > > > > > > Julian
> > > > > > >
> > > > > > > Am 08.06.20, 20:00 schrieb "Alessio Bernesco Làvore" <
> > > > > > > [email protected]>:
> > > > > > >
> > > > > > > Hello everyone,
> > > > > > > i've created a simple class reading values from a
> ModBus
> > PLC.
> > > > > > >
> > > > > > > I'm trying to use it inside Karaf, but at start the
> > class is
> > > > unable
> > > > > > to
> > > > > > > find
> > > > > > > the modbus driver. I've compiled and installed in Karaf
> > the
> > > > > > > "driver-s7-feature", with added the modbus driver:
> > > > > > >
> > > > > > > <?xml version="1.0" encoding="UTF-8" standalone="yes"?>
> > > > > > > <features xmlns="
> > http://karaf.apache.org/xmlns/features/v1.6.0
> > > "
> > > > > > > name="driver-s7-feature">
> > > > > > > <feature name="driver-s7-feature"
> description="PLC4J:
> > > > > > > Karaf-Features:
> > > > > > > S7" version="0.8.0.SNAPSHOT">
> > > > > > > <details>Implementation of the protocol
> adapters
> > for
> > > > usage
> > > > > as
> > > > > > > Java
> > > > > > > library.</details>
> > > > > > >
> > > > > >
> > <bundle>mvn:org.apache.plc4x/plc4j-osgi/0.8.0-SNAPSHOT</bundle>
> > > > > > > <bundle>mvn:org.osgi/osgi.core/6.0.0</bundle>
> > > > > > >
> > > > > >
> <bundle>mvn:org.apache.plc4x/plc4j-api/0.8.0-SNAPSHOT</bundle>
> > > > > > >
> > > > > >
> <bundle>mvn:org.apache.plc4x/plc4j-spi/0.8.0-SNAPSHOT</bundle>
> > > > > > >
> > <bundle>mvn:io.netty/netty-codec/4.1.47.Final</bundle>
> > > > > > >
> > <bundle>mvn:io.netty/netty-common/4.1.47.Final</bundle>
> > > > > > >
> > > > <bundle>mvn:io.netty/netty-transport/4.1.47.Final</bundle>
> > > > > > >
> > > <bundle>mvn:io.netty/netty-resolver/4.1.47.Final</bundle>
> > > > > > >
> > > > > >
> <bundle>mvn:commons-beanutils/commons-beanutils/1.9.4</bundle>
> > > > > > >
> > > <bundle>mvn:commons-logging/commons-logging/1.2</bundle>
> > > > > > >
> > > > > > >
> > <bundle>mvn:commons-collections/commons-collections/3.2.2</bundle>
> > > > > > >
> > <bundle>mvn:com.github.jinahya/bit-io/1.4.3</bundle>
> > > > > > >
> > <bundle>mvn:commons-codec/commons-codec/1.12</bundle>
> > > > > > >
> > > > > > >
> > >
> <bundle>mvn:org.apache.plc4x/plc4j-driver-s7/0.8.0-SNAPSHOT</bundle>
> > > > > > >
> > > > > > >
> > > > > > >
> > > > >
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-driver-modbus/0.8.0-SNAPSHOT</bundle>
> > > > > > >
> > > > > > >
> > > > > > >
> > > > >
> > >
> > <bundle>mvn:org.apache.plc4x/plc4j-transport-tcp/0.8.0-SNAPSHOT</bundle>
> > > > > > >
> > > > > > >
> > > > > > >
> > > > > >
> > > > >
> > > >
> > >
> >
> <bundle>mvn:com.fasterxml.jackson.core/jackson-annotations/2.10.0</bundle>
> > > > > > >
> > > <bundle>mvn:org.apache.commons/commons-lang3/3.9</bundle>
> > > > > > >
> > <bundle>mvn:io.netty/netty-buffer/4.1.47.Final</bundle>
> > > > > > > <bundle>mvn:io.vavr/vavr/0.10.2</bundle>
> > > > > > > <bundle>mvn:io.vavr/vavr-match/0.10.2</bundle>
> > > > > > > </feature>
> > > > > > > </features>
> > > > > > >
> > > > > > > Inside Karaf i can find all the active bundles:
> > > > > > >
> > > > > > > 152 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J: API
> > > > > > > 153 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J:
> > Driver: S7
> > > > > (Step7)
> > > > > > > 154 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J: OSGi
> > > > > > > 155 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J: SPI
> > > > > > > 156 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J:
> > Transports:
> > > > TCP
> > > > > > > 157 │ Active │ 80 │ 6.0.0.201403061837 │ osgi.core
> > > > > > > 164 │ Active │ 80 │ 1.0 │
> > edgecontroller
> > > Bundle
> > > > > > > 165 │ Active │ 80 │ 0.8.0.SNAPSHOT │ PLC4J:
> > Driver:
> > > Modbus
> > > > > > >
> > > > > > > Anyway at startup the bundle doesnt find any driver:
> > > > > > >
> > > > > > > 2020-06-08T17:47:43,391 | INFO | FelixStartLevel |
> > > > > PlcDriverManager
> > > > > > > | 152 - org.apache.plc4x.plc4j-api -
> > 0.8.0.SNAPSHOT |
> > > > > > > Instantiating new PLC Driver Manager with class loader
> > > > > > > sun.misc.Launcher$AppClassLoader@764c12b6
> > > > > > > 2020-06-08T17:47:43,391 | INFO | FelixStartLevel |
> > > > > PlcDriverManager
> > > > > > > | 152 - org.apache.plc4x.plc4j-api -
> > 0.8.0.SNAPSHOT |
> > > > > > > Registering
> > > > > > > available drivers...
> > > > > > > 2020-06-08T17:47:43,392 | ERROR | FelixStartLevel |
> > Activator
> > > > > > > | 164 - edgecontroller - 1.0.0 | Unable to
> > find
> > > driver
> > > > > for
> > > > > > > protocol 'modbus'
> > > > > > >
> > > > > > > edgecontroller is my bundle, looking at the Karaf log
> the
> > > > > > > PlcDriverManager
> > > > > > > is unable to find any driver.
> > > > > > >
> > > > > > > I cannot understand were i'm failing, could anyone
> > provide some
> > > > > > > insight?
> > > > > > >
> > > > > > > Thank you,
> > > > > > > Ale
> > > > > > >
> > > > > > >
> > > > > >
> > > > >
> > > > >
> > > > > --
> > > > > *CEOS Automatización, C.A.*
> > > > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
> > > > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
> > > > >
> > > > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
> > > > > *Ing. César García*
> > > > >
> > > > > *Cel: +58 414-760.98.95*
> > > > >
> > > > > *Hotline Técnica SIEMENS: 0800 1005080*
> > > > >
> > > > > *Email: [email protected]
> > > > > <[email protected]>*
> > > > >
> > > >
> > >
> > >
> > > --
> > > *CEOS Automatización, C.A.*
> > > *GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
> > > *PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
> > >
> > > *FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
> > > *Ing. César García*
> > >
> > > *Cel: +58 414-760.98.95*
> > >
> > > *Hotline Técnica SIEMENS: 0800 1005080*
> > >
> > > *Email: [email protected]
> > > <[email protected]>*
> > >
> >
> >
>
--
*CEOS Automatización, C.A.*
*GALPON SERVICIO INDUSTRIALES Y NAVALES FA, C.A.,*
*PISO 1, OFICINA 2, AV. RAUL LEONI, SECTOR GUAMACHITO,*
*FRENTE A LA ASOCIACION DE GANADEROS,BARCELONA,EDO. ANZOATEGUI*
*Ing. César García*
*Cel: +58 414-760.98.95*
*Hotline Técnica SIEMENS: 0800 1005080*
*Email: [email protected]