Hi Ski,

I'm pretty sure you can use Cat6 (not 6a), but it requires extra testing
and the length is limited to no more than 55m, and likely less, based on
the site conditions. Cat6a is supports runs out to 100m.

FWIW, we use Cat6 for 10GBASE-T for runs out to 10m. Runs longer than that
we run over multi-mode OM3/4 fiber with SFP+ transceivers.

Skylar

On Mon, Dec 7, 2015 at 10:35 AM, Ski Kacoroski <[email protected]> wrote:

> Hi,
>
> We are rewiring our server room to support 10GB.  The folks we talked to
> initially said that for the relatively short distances in the server room
> (less that 100ft) we can get by with cat 6 cabling for the patch cables
> from device to patch panel and probably even between patch panels because
> the distance is so short.  The installer is saying that he will not certify
> that we will get 10GB unless we use cat 6A every where because of its
> shielding that stops alien crosstalk.
>
> Comments on these two view points.
>
> cheers,
>
> ski
>
> --
> "When we try to pick out anything by itself, we find it
>   connected to the entire universe"            John Muir
>
> Chris "Ski" Kacoroski, [email protected], 206-501-9803
> or ski98033 on most IM services
> _______________________________________________
> Discuss mailing list
> [email protected]
> https://lists.lopsa.org/cgi-bin/mailman/listinfo/discuss
> This list provided by the League of Professional System Administrators
> http://lopsa.org/
>
_______________________________________________
Discuss mailing list
[email protected]
https://lists.lopsa.org/cgi-bin/mailman/listinfo/discuss
This list provided by the League of Professional System Administrators
 http://lopsa.org/

Reply via email to