> I've got some single power supply equipment (Cisco switches) in a rack
> with PDUs which have 120V C13 receptacles. I'm looking for an automatic
> transfer switch which I can plug into a C13 receptacle on either side of
> the rack, and feed the single power cables so that either side of the
> rack's power can be removed while the switches stay up.

We use the Servertech failsafe pdu*, but as a 3U pdu, it doesn't
fit your specific requirements of a single-unit device.  (But it does
do 120v and modular power cords)

A heads up though: Something that we only picked up on at the last
minute - for some ATS units out there, your input power feeds must be
phase synced, or you could pass a nice voltage spike down the line
which the power feed is switched. This can be interesting to deal with
if you use multiple UPSes.

* - http://www.servertech.com/products/dual-feed-ptxl-ptxm-hd16/

-- 

  