I also have a couple of tripplite PDUMH15ATNET ATS boxes. Purchased for
the same purpose as the OP. They seem to work, but their web interface
is awful. 

It's so badly designed, it's comical. It's all done with webforms, and
pressing <return> in most of them maps to "shut everything down right
now with no confirmation". Not to mention the bit where it's got
frames designed to be larger than then their layout resulting in weird
wrapping.

I'd look at BayTech or APC over tripplite.

seph

[email protected] writes:

> In the message dated: Thu, 13 Aug 2009 16:58:03 EDT,
> The pithy ruminations from Allan West on 
> <[lopsa-discuss] automatic transfer switch for single power supply gear> were:
> => I've got some single power supply equipment (Cisco switches) in a rack
> => with PDUs which have 120V C13 receptacles. I'm looking for an automatic
> => transfer switch which I can plug into a C13 receptacle on either side of
> => the rack, and feed the single power cables so that either side of the
> => rack's power can be removed while the switches stay up.
> => 
> => Can anyone recommend something which fits this niche? I'm not at liberty
>
> Sort of.
>
> I'm using a TrippLite PDUMH15ATNET PDU. It does what you want, and
> also has an LED showing amperage, and is IP accessible to configure
> and power up/down the outlets.
>
> Sounds nifty? Well, it would probably meet your requirements just
>fine.