I was just perusing some of the EMC docs, and wound up on the PID
hal component docs and source.  I have never quite understood the 
behavior of
the D term.

To (over) simplify:
error = commanded - feedback
errorD = error - previous error
output = error * P + errorI * I + errorD * D

Let's look at a couple cases :
1.  commanded pos is 5.0, feedback is now 4.8, it was 4.8 last servo cycle.

So, error is -0.1, previous error is -.2, so
errorD is -0.1 - (-0.2) = +.1
Now, errorD is multiplied by the P term and adds a positive value to
the output.  This seems wrong, as the error is decreasing with movement
in the positive direction, so you would
actually want to add a negative adjustment to the output to avoid 
overshooting
the commanded position.

Here's another:
commanded position is 5.0, and not changing.  A disturbance
has occurred, and the feedback is now 4.9, so the machine just
bumped in the minus direction.
error is -0.1, previous error was zero.

errorD is -0.1 -(0) = -0.1
This adds a negative adjustment to the output, which is forcing it in
the wrong direction.  It should be moved to the positive to correct
the disturbance.

Any comments on this?  This was mostly derived from the comments,
as the actual code is a bit more complex, and seems to involve
derivatives of both commanded and feedback, rather than looking
at just error and previous error.

I will have to try negative D values to see what they might do.

Jon

------------------------------------------------------------------------------