Hello Dwight,

There is an ETSI standard which defines the mechanical dimensions and
form factor for racking systems housing Telecom equipment within the
public network and customer premises, I think this would also apply to
your products.

ETS 300 119 is a four part standard...
   ETS 300 119-1: "Equipment Engineering (EE); European
telecommunication standard for equipment practice Part 1: Introduction
and terminology".

   ETS 300 119-2: "Equipment Engineering (EE); European
telecommunication standard for equipment practice Part 2: Engineering
requirements for racks and cabinets".

   ETS 300 119-3: "Equipment Engineering (EE); European
telecommunication standard for equipment practice Part 3: Engineering
requirements for miscellaneous racks and cabinets".

   ETS 300 119-4: "Equipment Engineering (EE); European
telecommunication standard for equipment practice Part 4: Engineering
requirements for subracks in miscellaneous racks and cabinets".

There are different configurations allowed and so I've only copied the
text from Part 2, you can freely download the most recent updates of
each directly from ETSI (the updates may have been renumbered as ENs so
you will also need to search on EN 300 119-x).

>From previous experience you'll have to come up with a rack mounting kit
arrangement which will cover each of the various rack standards - EIA,
NEBS and ETSI if you're building a system for use everywhere.

I hope this helps.

Best regards, Edward

Edward Fitzgerald
International Approvals Consultant
Direct Tel. : +44 1202 20 09 22
GSM Tel. : +44 4685 33 100

European Technology Services
Specialist Global Compliance Consultancy
Offices in Australia, Canada and the UK.
http://www.ets-tele.com


[ Extracted from ETS 300 119-2 - Equipment Engineering (EE); European
telecommunication standard for equipment practice Part 2: Engineering
requirements for racks and cabinets]
3 Coordination dimensions for racks/cabinets

3.1 Height
The height dimension (H) includes covers, feet or castors if these are
an integral part of the rack/cabinet structure.
For telecommunication centres, H shall be 2 200 mm.
For customer sites, H may be at any preferred height, as defined in IEC
Publication 917-2 (see Annex B), up to 2 200 mm. Provision shall be made
for the possible fitment of height adaptors (for interfacing with
overhead structures) as illustrated in Annex A, figure A.1.
The racks/cabinets shall also be provided with devices which can be
height-adjusted to compensate for any unevenness in the floor. The scope
for height adjustment shall be at least 25 mm. The nominal rack/cabinet
height shall be measured when the adjustment devices are at their fully
retracted positions.

3.2 Width
The width dimension (W) includes covers if they are an integral part of
the rack/cabinet.
W shall be one of four permitted dimensions: 150 mm, 300 mm, 600 mm, or
900 mm.
The sides of any rack/cabinet shall not interfere with the assembly of
adjacent racks/cabinets (into a straight line-up). The suppliers must
ensure that the rack/cabinet will fit into the space between the grid
lines, as illustrated in Annex A, figure A.3. Manufacturing tolerances
shall therefore be so arranged that this objective will always be
achieved, even when racks/cabinets are delivered from different
suppliers.
NOTE: If additional equipment at the end(s) of a suite of racks/cabinets
is required, the
associated coordination dimensions shall be specified as an integer
multiple of the
mounting pitch of 25 mm for each side during equipment practice design
and should be
agreed between supplier and user.

3.3 Depth
The depth dimension (D) includes:
a) doors or covers of the rack/cabinet if present;
b) all protruding parts e.g. switches, lamps, hinges, locks,
electrostatic discharge points, etc.;
c) connectors, cabling, cooling fins, etc.
For the doors or covers, a minimum reference value for aisle width shall
be 750 mm. Doors or covers which are in the open position shall protrude
from the front/rear line of racks/cabinets by a maximum of 150 mm.
Doors or covers shall be designed so that when open, they do not in any
way restrict access to the equipment for essential maintenance and
installation operations.
D shall be 300 mm or 600 mm.

-----Original Message-----
From: Dwight Hunnicutt [mailto:dwight.hunnic...@vina-tech.com]
Sent: 01 July 1999 21:46
To: EMC PSTC; TREG Newsgroup
Subject: 21" rack for Europe



In the U.S., 19" and 23" racks are pretty much the standard (and don't
forget the Bellcore hole spacing), yes?  

How about in Europe?  I've heard they use 19" and 21" racks (or their
metric equivalent).  Is one size typical for data applications, and the
other typical to telecom applications?  How about hole spacing?


-- 
___________________________
  DWIGHT HUNNICUTT
  Sr. Compliance Engineer
  VINA Technologies, Inc.
  510-771-3349
  520-244-2721 fax
  www.vina-tech.com

---------
This message is coming from the emc-pstc discussion list.
To cancel your subscription, send mail to majord...@ieee.org
with the single line: "unsubscribe emc-pstc" (without the
quotes).  For help, send mail to ed.pr...@cubic.com,
jim_bac...@monarch.com, ri...@sdd.hp.com, or
roger.volgst...@compaq.com (the list administrators).

Reply via email to