It seems that the diffferent safety standards have different mains supply tolerance.
IEC 950/1991 (including amendment 1-4) says "Equipment intended to operate directly from the mains supply shall be designed for a minimum supply tolerance of +6%, -10%. If the rated voltage is 230 V single phase or 400 V three phase, the equipment shall operate safely within a minimum supply tolerance of +10% and -10%". (point 1.6.5) The EN60950 has no national deviation at this point. The new IEC950/1999 has a little different wording, but the same meaning. Regards Niels Hougaard EMC and Safety BARCO AS/Communication Systems Denmark > -----Original Message----- > From: raymond...@dixonsasia.com.hk [SMTP:raymond...@dixonsasia.com.hk] > Sent: 3. august 2000 04:16 > To: James, Chris > Cc: emc-p...@ieee.org > Subject: RE: Test voltage for products to the U.K. > > > > > Chris, > > According to the Minister for Energy from DTI, the nominal mains voltage > is > 230Vac. The designer designs the products for 230Vac following such > official > information. The BS EN 60065 requires the test to the product +6 or -10% > of > rated voltage. It appears they are legally right and it seems the memo > mentioned earlier (I have not seem the HD doc) is just a recommendation. > Testing to +6% of 240Vac is just an option and not all test laboratories > implement mandatorily. That is the reason I bring up this subject for > open > discussion. Is there any way in existence to block this loose hole? > > Regards, > > Raymond Li > > ======================================================= > > > > "James, Chris" <c...@dolby.co.uk> on 02/08/2000 11:14:26 p > Please respond to "James, Chris" <c...@dolby.co.uk> > To: Raymond Li/DixonsNotes@DixonsNotes > cc: emc-p...@ieee.org > Subject: RE: Test voltage for products to the U.K. > > > > > Equipment must be marked to include 230Vac in the supply range. For a wide > input range PSU it is permissable to put say 90-240Vac as 230Vac falls > within this range. For selectable ranges then 230Vac must appear as one of > those ranges although it is acceptable to say 100/120/220/230-240. > > Section 4 of EN60065 says equipment must be tested at .9 and 1.06 times > the > RATED SUPPLY VOLTAGE, where RATED SUPPLY VOLTAGE is defined as the voltage > for which the manufacturer has designed the apparatus. > > Thus if you spec/mark it to work at 240Vac then it will be tested at 254.4 > and if you spec/mark it to work at 230Vac then I read it as only being > tested at 243.8Vac. However the test house (part of a world wide group) we > use say they use 230 +10% or 240 +6% which is approximately the same > thing. > > Chris > > > > -----Original Message----- > From: raymond...@dixonsasia.com.hk > Sent: Wednesday, August 02, 2000 9:52 AM > To: James, Chris > Cc: emc-p...@ieee.org > Subject: RE: Test voltage for products to the U.K. > > > Chris, > > Thanks for your comments. > > Generally, the product is marked 230Vac in order to comply with harmonised > standard but for the products to the U.K., they should be tested at 207Vac > (-10% of 230Vac) and 254.4Vac (+6% of 240Vac). Is it a normal practise or > agreed > procedure used in all accredited laboratories in the U.K. and/or elsewhere > in the world? > > Best regards, > > Raymond > > ========================================= > > "James, Chris" <c...@dolby.co.uk> on 01/08/2000 09:44:20 p > To: Raymond Li/DixonsNotes@DixonsNotes, emc-p...@ieee.org > Subject: RE: Test voltage for products to the U.K. > > > Spec on mains is 230 +/- 6% so as 240 falls within that range, then that > is > where the reference regard the UK staying at 240Vac came from. > > We used to see voltages several % above 240Vac in the past. In my > particular area they used to stay spot on 240V most of the time. I note > however that in the last 6 months the local voltage has dropped to 235Vac, > although the generating board won't admit to having consciously made this > change! > > We here continue to design for 264Vac max. > > Chris > > -----Original Message----- > From: raymond...@dixonsasia.com.hk > Sent: Tuesday, August 01, 2000 10:53 AM > To: emc-p...@ieee.org > Subject: Test voltage for products to the U.K. > > A few years ago, BEAMA or other similar body has issued a memo to public > laboratories about testing voltage for products selling in the U.K. The > memo > says the U.K. mains is still 240Vac although the rated voltage is agreed > to be > 230Vac and the products have to be taken care the safety at 240Vac. Can > anyone tell me where I can find a copy of this memo and if there is any > updated > version to replace this one. > > Thanks and regards, > > Raymond Li > Dixons Asia Ltd. ------------------------------------------- This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Jim Bacher: jim_bac...@mail.monarch.com Michael Garretson: pstc_ad...@garretson.org For policy questions, send mail to: Richard Nute: ri...@ieee.org