<snip>
> >On the other (AUX) side of the transformers conect 
the center taps directly to the ground panel. You don't 
care about high-voltage isolation in this application, 
so you don't need any caps. 
> 
> How do you cope with ground potential differences, 
with centre-taps
> grounded at each end of the cable?
> -- 
> Regards, John Woodgate, OOO - Own Opinions Only. 

Center taps are not grounded on each end of the cable. I 
recommended adding transformer in-line, at the location 
of the feedthrough panel.

Each device (DUT and AUX) has a transformer and high-
voltage isolation in the front end. For RF coupled on 
the Ethernet line, which you want to filter out before 
it reaches the AUX equipment, the transformer you put in 
series with line effectively brings common-mode voltage 
on the cable to the voltage of the feedthtough panel 
(hopefully close to such low voltage that can not upset 
the AUX equipment). Additionaly, common-mode chokes in 
the part will further help reduce higher-frequency 
content that might go through due to any imbalance in 
the transformer center tap.

Neven


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to