CONFLICT OF INTEREST ALERT:     
   My employer makes SMPS.

For both conducted emissions, an unit with PFC typically makes life easier.
For reduced radiated emissions, avoid the open "U" chassis units. Please
note that as customers demand greater efficiencies and reduced sizes, you
will see much higher main converter frequencies.

In any case, a supplier that (assuming your test technique is consistent)
produces units with a wide variance in emissions characteristics may be
indicative of poor design and/or no quality control.

Brian



-----Original Message-----
From: Jim Conrad [mailto:jc...@shore.net]
Sent: Tuesday, September 03, 2002 3:55 AM
To: Alex McNeil; emc-p...@majordomo.ieee.org
Subject: RE: SMPS EMC Emissions



Alex wrote:

"Do you think it is reasonable to specify in my power supply
specification
that the manufacturers SMPS should meet EN55022 Class B -6dB"

Yes.  I would ask for 6 dB margin since measurement uncertainty for
a typical conducted measurements system is 5.4 dB.   You must also
allow for unit to unit variations in manufacturing.  Sample 5 units
and apply the 80/80 rule and see if they still pass.

Jim

-----Original Message-----
From: owner-emc-p...@majordomo.ieee.org
[mailto:owner-emc-p...@majordomo.ieee.org]On Behalf Of Alex McNeil
Sent: Tuesday, September 03, 2002 4:57 AM
To: 'emc-p...@majordomo.ieee.org'
Subject: SMPS EMC Emissions


Hi Group,

First of all thank you to those who replied to my previous email. I
have not
had time to reply personally...yet.

I have noticed that the broadband noise of some SMPS are already
near to the
limits of EN55022 Class B (I tested with a max resistive load). This
gives
my product little scope for emissions at these broadband
frequencies,
especialy when my product is taking peak load e.g. printing.

The power supply manufacturer rightly claims that his product does
meet
EN55022 Class B.

Do you think it is reasonable to specify in my power supply
specification
that the manufacturers SMPS should meet EN55022 Class B -6dB or....?
Have any of you come across a similar scenario?

As usual , I look forward to your professional opinions.

Kind Regards
Alex McNeil
Principal Engineer
Tel: +44 (0)131 479 8375
Fax: +44 (0)131 479 8321
email: alex.mcn...@ingenicofortronic.com


-------------------------------------------
This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

All emc-pstc postings are archived and searchable on the web at:
    http://ieeepstc.mindcruiser.com/
    Click on "browse" and then "emc-pstc mailing list"

Reply via email to