I read in !emc-pstc that Peter L. Tarver <peter.tar...@sanmina-sci.com>
wrote (in <nebbkemlgllmjofmoplekehbedaa.peter.tar...@sanmina-sci.com>)
about 'Circuit Breaker Tripping Dring Fault Tests' on Thu, 30 Jan 2003:
>
>John -
>
>That impedance value is suprisingly high, 


It applies to 230 V 50 Hz systems only. SC77A/WG2 has been given a too
limited amount of data on 120 V 60 Hz systems to deduce a reference
value, but it seems to be rather less than half the 230 V value, because
permitted voltage tolerances in 120 V systems tend to be +/-5%, less
than in Europe (6 to 10%).

>but tends to
>support the contention that the fault current at an outlet
>will be much lower than was suggested (65kA, which, to me,
>appeared more like a peak surge current than a fault
>current).

Yes, 65 kA is way too high.
>
>For those interested, below are what the IEC Web Store has
>to say about IEC 60725.
>
>Title: Considerations on reference impedances for use in
>determining the disturbance characteristics of household
>appliances and similar electrical equipment
>
>Abstract: Records the information that was available and the
>factors that were taken into account in arriving at the
>reference impedance of 0.4+ j 0.25 ohm which has been
>incorporated in IEC 60555. Has the status of a technical
>report.

A revision is under way. Postpone your buying decision.(;-)

It doesn't alter the reference impedance but adds information of
calculating the impedances of (particularly) higher-current services,
applicable to any system voltage and permitted voltage variation.
>
>0.5 Ohm seems large for a flexible cord.
>
0.5 ohms is 0.2 ohm total for the two conductors of the flexible plus
0.3 ohm total for the two conductors of the feed to the wall socket. All
in a 230 V system. It's just an example. 
-- 
Regards, John Woodgate, OOO - Own Opinions Only. http://www.jmwa.demon.co.uk 
Interested in professional sound reinforcement and distribution? Then go to 
http://www.isce.org.uk
PLEASE do NOT copy news posts to me by E-MAIL!


This message is from the IEEE EMC Society Product Safety
Technical Committee emc-pstc discussion list.

Visit our web site at:  http://www.ewh.ieee.org/soc/emcs/pstc/

To cancel your subscription, send mail to:
     majord...@ieee.org
with the single line:
     unsubscribe emc-pstc

For help, send mail to the list administrators:
     Ron Pickard:              emc-p...@hypercom.com
     Dave Heald:               davehe...@attbi.com

For policy questions, send mail to:
     Richard Nute:           ri...@ieee.org
     Jim Bacher:             j.bac...@ieee.org

Archive is being moved, we will announce when it is back on-line.
All emc-pstc postings are archived and searchable on the web at:
    http://www.ieeecommunities.org/emc-pstc

Reply via email to