From: Gregg Kervill Sent: Tuesday, January 28, 2003 3:21 PM > Like most regulatory issues the answer is YES and NO. > > Therefore it is dangerous and extremely misleading (to many > lurkers) to apply a general answer to all conditions: > > Generally the equipment is expected to protect itself with > internal over current and short-circuit protection.
I disagree. It may be possible for equipment to possess inherent features that do not require supplementary protection or that a piece of equipment is adequately protected by the branch circuit protection. Much depends on the application and design. > The equipment will be tested with the worst case fault > condition – 60 kAmp or more is not uncommon This value may be true for equipment installed in Category IV and possibly Category III environments (per IEC60664-1), but is neither the general case nor very common for equipment installed in Category II environments. Consider that every finite (though minute) impedance at every electrical connection will serve to limit the fault current available at equipment. Impedances will also exist at each switchable contact (molded case switches and circuit breakers) and each wiping contact (fuse holders for replaceable cartridge fuses, outlets/plugs, knife switches). For North America: In a typical household operating at 120V, it's unlikely that a fault current available to Pluggable Equipment Type A will be much above 5kA, even if the outlet supplying the equipment is within 5 ft. of the service entrance. In a typical household operating at 240V, the available fault current will be somewhat higher (approximately doubled +). This is also, in large measure, due to the relatively small last distribution transformer before the household and other loads on the transformer from other households supplied by the same transformer. In a typical business the fault current available will be larger, due largely to a larger transformer connected to the service entrance and that the service entrance voltages are greater (480V three phase is not uncommon for larger facilities; 120/208V is most common). I'm not certain of the typical fault currents available at an outlet in this case, but I'd venture a guess that its not more than 25kA at a ANSI/NEMA 5-15 outlet. I'm interested in hearing typical values for other regions of the world, so if anyone has any data or reasonable guesses, please let us all know. > Where we rely upon the ‘breaker’ for - non-domestic > equipment - it is ALWAYS mandatory (and common sense) > to specify the characteristics of that breaker in > terms of ‘tripping (operating) current’ – time > characteristics (Type I, II or III) and Breaking > Current 2,500 Amps is low for most domestic situations. This must be for Europe. In the US (and I believe Canada is the same), 5kA is a gimme interrupting rating for molded case switches and circuit breakers. The minimum interrupting rating for branch circuit fuses is 10kA. > A failure to provide the necessary information > WILL eventually result in a fire or nuisance tripping. Or not, depending on the installation environment. > Best regards > Gregg Regards, Peter L. Tarver, PE Product Safety Manager Sanmina-SCI Homologation Services San Jose, CA peter.tar...@sanmina-sci.com This message is from the IEEE EMC Society Product Safety Technical Committee emc-pstc discussion list. Visit our web site at: http://www.ewh.ieee.org/soc/emcs/pstc/ To cancel your subscription, send mail to: majord...@ieee.org with the single line: unsubscribe emc-pstc For help, send mail to the list administrators: Ron Pickard: emc-p...@hypercom.com Dave Heald: davehe...@attbi.com For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org Archive is being moved, we will announce when it is back on-line. All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc