This is a multi-part message in MIME format.
Brian, You are absolutely correct, once you have a reliable encapsulant then the spacings problem becomes one of solid insulation or distance through insulation. The trick is, as you mentioned, is the reliable adherence to the PWB itself.
As it turns out a "pancake void" along a surface is the worst kind and if you are dealing with any appreciable voltage at all, then you may have a significant problem corona in the circuit. I've seen problems manifest even after 6 months of operation. The test is the same for solid insulation, Partial Discharge and/or Impulse testing. If PD becomes a problem, a possible fix is to specify a bead-blast (no sand-blast please) of the surface prior to mounting parts and no solder mask. This removes any release compounds or contaminants that may still be present on the surface of the laminate. Naturally if you fully encapsulate a PCB then there is no need for component designators or silkscreen. There is also the issue of doing repairs and restoring the encapsulant to its previous capability. -doug From: owner-emc-p...@listserv.ieee.org [mailto:owner-emc-p...@listserv.ieee.org] On Behalf Of Brian O'Connell Sent: Wednesday, January 05, 2005 9:53 AM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: Potted components For UL I.T., the materials must be approved for the operating conditions, IP, and WV. IEC 60950-1, 2.10.8 Spacings filled by insulating compound Where distances between conductive parts are filled with insulating compound, including where insulation is reliably cemented together with insulating compound, so that CLEARANCES and CREEPAGE DISTANCES do not exist, only the requirements for distance through insulation of 2.10.5.1 apply. luck, Brian > -----Original Message----- > From: Doug Beckwith [mailto:dougbeckw...@yahoo.ca] > Sent: Wednesday, January 05, 2005 8:44 AM > To: emc-p...@ieee.org > Subject: Potted components > > > Hi Everyone, > A happy new year to you all. > > Now for my question. I am looking at a unit that has mains and > SELV circuits that is encapsulated (potted). Am I correct in > assuming that creepage and clearance distances on the PCB for a > potted unit become the same as that for distance through > insulation, as when the traces are buried in a multilayer PCB? > > Regards > > Doug > > > ______________________________________________________________________ > Post your free ad now! http://personals.yahoo.ca > > ---------------------------------------------------------------- > This message is from the IEEE Product Safety Engineering Society > emc-pstc discussion list. Website: http://www.ieee-pses.org/ > > To post a message to the list, send your e-mail to emc-p...@ieee.org > > Instructions: > http://listserv.ieee.org/listserv/request/user-guide.html > > List rules: http://www.ieee-pses.org/listrules.html > > For help, send mail to the list administrators: > > Scott Douglas emcp...@ptcnh.net > Mike Mcantwell mcantw...@ieee.org > > For policy questions, send mail to: > > Richard Nute: ri...@ieee.org > Jim Bacher: j.bac...@ieee.org > > All emc-pstc postings are archived and searchable on the web at: > > http://www.ieeecommunities.org/emc-pstc > This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. Website: http://www.ieee-pses.org/ To post a message to the list, send your e-mail to emc-p...@ieee.org Instructions: http://listserv.ieee.org/listserv/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@ptcnh.net Mike Mcantwell mcantw...@ieee.org For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstc This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. Website: http://www.ieee-pses.org/ To post a message to the list, send your e-mail to emc-p...@ieee.org Instructions: http://listserv.ieee.org/listserv/request/user-guide.html List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Scott Douglas emcp...@ptcnh.net Mike Mcantwell mcantw...@ieee.org For policy questions, send mail to: Richard Nute: ri...@ieee.org Jim Bacher: j.bac...@ieee.org All emc-pstc postings are archived and searchable on the web at: http://www.ieeecommunities.org/emc-pstcTitle: RE: Potted components
Brian,
You are absolutely correct, once you have a reliable encapsulant then
the spacings problem becomes one of solid insulation or distance through
insulation. The trick is, as you mentioned, is the reliable adherence
to the PWB itself.
As it turns out a "pancake void" along a surface is the worst kind and
if you are dealing with any appreciable voltage at all, then you may
have a significant problem corona in the circuit. I've seen problems
manifest even after 6 months of operation. The test is the same for
solid insulation, Partial Discharge and/or Impulse testing.
If PD becomes a problem, a possible fix is to specify a bead-blast (no
sand-blast please) of the surface prior to mounting parts and no solder
mask. This removes any release compounds or contaminants that may still
be present on the surface of the laminate. Naturally if you fully
encapsulate a PCB then there is no need for component designators or
silkscreen.
There is also the issue of doing repairs and restoring the encapsulant
to its previous capability.
-doug
-----Original Message-----
From: owner-emc-p...@listserv.ieee.org
[mailto:owner-emc-p...@listserv.ieee.org] On Behalf Of Brian O'Connell
Sent: Wednesday, January 05, 2005 9:53 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: Potted components
For UL I.T., the materials must be approved for the operating
conditions,
IP, and WV.
IEC 60950-1, 2.10.8 Spacings filled by insulating compound
Where distances between conductive parts are filled with insulating
compound, including where insulation is reliably cemented together with
insulating compound, so that CLEARANCES and CREEPAGE DISTANCES do not
exist,
only the requirements for distance through insulation of 2.10.5.1 apply.
luck,
Brian
> -----Original Message-----
> From: Doug Beckwith [mailto:dougbeckw...@yahoo.ca]
> Sent: Wednesday, January 05, 2005 8:44 AM
> To: emc-p...@ieee.org
> Subject: Potted components
>
>
> Hi Everyone,
> A happy new year to you all.
>
> Now for my question. I am looking at a unit that has mains and
> SELV circuits that is encapsulated (potted). Am I correct in
> assuming that creepage and clearance distances on the PCB for a
> potted unit become the same as that for distance through
> insulation, as when the traces are buried in a multilayer PCB?
>
> Regards
>
> Doug
>
>
> ______________________________________________________________________
> Post your free ad now! http://personals.yahoo.ca
>
> ----------------------------------------------------------------
> This message is from the IEEE Product Safety Engineering Society
> emc-pstc discussion list. Website: http://www.ieee-pses.org/
>
> To post a message to the list, send your e-mail to emc-p...@ieee.org
>
> Instructions:
> http://listserv.ieee.org/listserv/request/user-guide.html
>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
>
> Scott Douglas emcp...@ptcnh.net
> Mike Mcantwell mcantw...@ieee.org
>
> For policy questions, send mail to:
>
> Richard Nute: ri...@ieee.org
> Jim Bacher: j.bac...@ieee.org
>
> All emc-pstc postings are archived and searchable on the web at:
>
> http://www.ieeecommunities.org/emc-pstc
>
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/
To post a message to the list, send your e-mail to emc-p...@ieee.org
Instructions: http://listserv.ieee.org/listserv/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Mcantwell mcantw...@ieee.org
For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society
emc-pstc discussion list. Website: http://www.ieee-pses.org/
To post a message to the list, send your e-mail to emc-p...@ieee.org
Instructions: http://listserv.ieee.org/listserv/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html
For help, send mail to the list administrators:
Scott Douglas emcp...@ptcnh.net
Mike Mcantwell mcantw...@ieee.org
For policy questions, send mail to:
Richard Nute: ri...@ieee.org
Jim Bacher: j.bac...@ieee.org
All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
ATT31800.txt
Description: Binary data