Thanks to all who replied to my earlier email.

 

It would help me understand the intent of the harmonic standards if I knew
what the goal of these standards were.  Are they to limit the actual harmonic
current or only the harmonic current in reference to the overall load?  Does a
higher fundamental load make the affects of harmonic emissions less of a
problem on a public low-voltage ac distribution system?

 

Several replies have suggested we test the instrument in different current
load modes. Here is the problem with that.

 

Let’s say we have an instrument that under full load draws 2 amps at the 3rd
harmonic and 25 amps at the fundamental. 2 amps is only 8% of the fundamental,
which is passing the 61000-3-12 test (table 2 limit is 21.6% at the 3rd
harmonic). In a different mode of operation, the instrument again draws 2 amps
at the 3rd harmonic but the fundamental is only 5 amps, which is 40% and would
Fail the 61000-3-12 test, yet the harmonic current is exactly the same in both
modes.  Another strange thing is that in this mode of operation it would pass
the Class A limits of the 61000-3-2 test which is 2.3 amps at the 3rd
harmonic. 

 

In the above example, we can claim compliance with the 61000-3-12 test IF we
declare a Short Circuit Ratio of 350. This translates into requiring a very
low system impedance which seems strange to me that it would be required only
in a mode where the instrument is drawing little overall current.

 

Another question is how common are the terms Short Circuit Ratio and Short
Circuit Power to the people in Europe?  If we put such a statement in our
documentation is anyone going to know what this means and know what to do
about it?  A short Circuit Ratio of 350 on a 230VAC system would have a Short
Circuit Power of something like 7 megawatts. I asked an electrician here in
the US if our mains system can handle this and he started to hyperventilate.
Obviously his wasn’t familiar with the terms. 

 

This is another topic I’m finding very interesting. Again, I’m a newbie
and though I have read through the standards several times lacking the
background and experience on this topic I’m sure there are huge gaps in my
understanding.

 

Thanks to all,

The Other Brian

 

________________________________

From: emc-p...@ieee.org [mailto:emc-p...@ieee.org] On Behalf Of
ralph.mcdiar...@ca.schneider-electric.com
Sent: Thursday, April 22, 2010 7:39 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Harmonic Emissions Testing

 


Would it be sensible to test it in both transient (warm up) and in steady
state operation?    If the transient operating condition was brief (say < 5
minutes) then I would argue that it could be waived as a mode of operation
needing 61000-3-2 evaluation.  A minimum period of 'disturbance' likely needs
to be defined. 
_______________________________________
_____________________________________________ 

Ralph McDiarmid  |   Schneider Electric   |  Renewable Energies Business  |  
CANADA  |   Compliance Engineer




From: 

John Woodgate <j...@jmwa.demon.co.uk> 

To: 

EMC-PSTC@LISTSERV.IEEE.ORG 

List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
List-Post: emc-pstc@listserv.ieee.org
Date: 

04/22/2010 12:40 AM 

Subject: 

Re: [PSES] Harmonic Emissions Testing

 

________________________________




In message 
<0ed66cd2c9bd0a459d54fb9119a605670168d...@mailserver.lecotc.com>, dated 
Wed, 21 Apr 2010, "Kunde, Brian" <brian_ku...@lecotc.com> writes:

>If an instrument could operate in different modes at different current 
>levels, what do you use as the Reference Fundamental Current in the 
>61000-3-12 test?  The maximum Fundamental Current of the instrument in 
>any mode?
>
> 
>
>In section 4.1a of the 61000-3-12 test, it says, ?During the 
>measurement of the reference fundamental current, the r.m.s. line 
>current shall be equal to the rated line current Iequ stated by the 
>manufacturer?.  I?m not really sure what this means unless they are 
>saying it is measured when the device is drawing maximum current.

This issue has already been raised and will be discussed at a meeting of 
the IEC committee next week. I cannot predict the outcome, but there is 
wide agreement that 'something must be done'.
-- 
OOO - Own Opinions Only. Try www.jmwa.demon.co.uk and www.isce.org.uk
John Woodgate, J M Woodgate and Associates, Rayleigh, Essex UK
I should be disillusioned, but it's not worth the effort.

-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieeecommunities.org/emc-pstc
<http://www.ieeecommunities.org/emc-pstc> 
Graphics (in well-used formats), large files, etc. can be posted to that URL.

Website:  http://www.ieee-pses.org/ <http://www.ieee-pses.org/> 
Instructions:  http://listserv.ieee.org/request/user-guide.html
<http://listserv.ieee.org/request/user-guide.html> 
List rules: http://www.ieee-pses.org/listrules.html
<http://www.ieee-pses.org/listrules.html> 

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

________________________________________________________________________
This email has been scanned for SPAM content and Viruses by the MessageLabs
Email Security System.
________________________________________________________________________


-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 

_________________________ 

LECO Corporation Notice: This communication may contain confidential
information intended for the named recipient(s) only. If you received this by
mistake, please destroy it and notify us of the error. Thank you. 
-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 


Reply via email to