Chris,

If the product is designed for use in the Industrial sector, use of the colour
codes given in EN 60204-1 is advisable. Here is the relevant text from the
2006 edition of the standard:

13.2.2 Identification of the protective conductor
The protective conductor shall be readily distinguishable by shape, location,
marking, or
colour. When identification is by colour alone, the bicolour combination
GREEN-ANDYELLOW
shall be used throughout the length of the conductor. This colour
identification is
strictly reserved for the protective conductor.


For insulated conductors, the bicolour combination GREEN-AND-YELLOW shall be
such that
on any 15 mm length, one of the colours covers at least 30 % and not more than
70 % of the
surface of the conductor, the other colour covering the remainder of the
surface.
Where the protective conductor can be easily identified by its shape,
position, or constrljction
(for example a braided conductor, uninsulated stranded conductor), or where
the insulated
conductor is not readily accessible, colour coding throughout its length is
not necessary but
the ends or accessible locations shall be clearly identified by the graphical
symbol
IEC 60417-5019 (OB:2002-10) or by the bicolour combination GREEN-AND-YELLOW.


13.2.3 Identification of the neutral conductor
Where a circuit includes a neutral conductor that is identified by colour
alone, the colour used
for this conductor shall be BLUE. In order to avoid confusion with other
colours, it is
recommended that an unsaturated blue be used, called here "light blue" (see
3.2.2 of
IEC 60446). Where the selected colour is the sole identification of the
neutral conductor, that
colour shall not be used for identifying any other conductor where confusion
is possible.
Where identification by colour is used, bare conductors used as neutral
conductors shall be
either coloured by a stripe, 15 mm to 100 mm wide in each compartment or unit
and at each
accessible location, or coloured throughout their length.


13.2.4 Identification by colour
Where colour-coding is used for identification of conductors (other than the
protective
conductor (see 13.2.2) and the neutral conductor (see 13.2.3)), the following
colours may be
used:


BLACK, BROWN, RED, ORANGE, YELLOW, GREEN, BLUE (including LIGHT BLUE),
VIOLET, GREY, WHITE, PINK, TURQUOISE.


NOTE This list of colours is derived from lEC 60757.


It is recommended that, where colour is used for identification, the colour be
used throughout
the length of the conductor either by the colour of the insulation or by
colour markers at
regular intervals and at the ends or accessible location.


For safety reasons, the colour GREEN or the colour YELLOW should not be used
where
there is a possibility of confusion with the bicolour combination
GREEN-AND-YELLOW (see
13.2.2).


Colour identification using combinations of those colours listed above may be
used provided
there can be no confusion and that GREEN or YELLOW is not used except in the
bicolour
combination GREEN-AND-YELLOW.


Where colour-coding is used for identification of conductors, it is
recommended that they be
colour-coded as follows:


- BLACK: a.c. and d.c. power circuits;
- RED: a.c. and d.c. control circuits;
- BLUE: d.c. control circuits;
- ORANGE: excepted circuits in accordance with 5.3.5.


Exceptions: to the above are permitted where:


- insulation is used that is not available in the colours recommended; or
- multiconductor cable is used, but not the bicolour combination
GREEN-AND-YELLOW.


5.3.5 Excepted circuits 
The following circuits need not be disconnected by the supply disconnecting
device: 



*       lighting circuits for lighting needed during maintenance or repair;  
*       plug and socket outlets for the exclusive connection of repair or
maintenance tools and equipment (for example hand drills, test equipment); 
*       undervoltage protection circuits that are only provided for automatic
tripping in the event of supply failure; 
*       circuits supplying equipment that should normally remain energized for
correct operation (for example temperature controlled measuring devices,
product (work in progress) heaters, program storage devices); 
*       control circuits for interlocking. 



It is recommended, however, that such circuits be provided with their own
disconnecting device. 


Where such a circuit is not disconnected by the supply disconnecting device: 

*       permanent warning label(s) in accordance with 16.1 shall be 
appropriatelY
placed in proximity to the supply disconnecting device; 
*       a corresponding statement shall be included in the maintenance manual, 
and
one or more of the following shall apply; 
*       a permanent warning label in accordance with 16.1 is affixed in 
proximity to
each excepted circuit, or 
*       the excepted circuit is separated from other circuits, or 
*       the conductors are identified by colour taking into account the
recommendation of 13.2.4. (bolding added here by DN for emphasis)


-- 
Doug Nix, A.Sc.T.
IEEE PSES Toronto Chapter 
Toronto Section, Ontario, Canada

d...@ieee.org 
mobile (519) 729-5704
fax (519) 653-1318

Find me LinkedIn at http://www.linkedin.com/in/dougnix


Fostering Technological Innovation and Excellence for the Benefit of Humanity.
Celebrating 125 Years of Engineering the Future. http://www.ieee125.org

On 16-Dec-09, at 09:10 , chris_al...@3com.com wrote:


        Hi, 
        
        Does anyone know if there is a harmonised standard for the colours of
external DC wiring (mains supply) in Europe? 
        
        Particularly interested in the colours for 2 wire earthed DC power 
circuits
with positive earth. 
        
        Thanks,

         Chris Allen
          Compliance Specialist
        
          3Com Europe Ltd
          Peoplebuilding 2, Peoplebuilding Estate, Maylands Avenue, Hemel 
Hempstead ,
Hertfordshire HP2 4NW
          T:    44-1442-438308  
          F:    44-1442-438333  
          M:   44-7768-806801  
          E:   chris_al...@3com.com <mailto: chris_al...@3com.com>   
          www.3com.co.uk
          _______________________________________________________
          www.h3cnetworks.com | www.3com.com | www.tippingpoint.com  
        
Please consider the environment before printing this e-mail.
________________
CONFIDENTIALITY NOTICE: This e-mail message, including any attachments,
is being sent by 3Com for the sole use of the intended recipient(s) and
may contain confidential, proprietary and/or privileged information.
Any unauthorized review, use, disclosure and/or distribution by any 
recipient is prohibited.  If you are not the intended recipient, please
delete and/or destroy all copies of this message regardless of form and
any included attachments and notify 3Com immediately by contacting the
sender via reply e-mail or forwarding to 3Com at postmas...@3com.com. 



-

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at
http://www.ieeecommunities.org/emc-pstc
Graphics (in well-used formats), large files, etc. can be posted to that URL. 

Website: http://www.ieee-pses.org/
Instructions: http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <emcp...@socal.rr.com>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 


Reply via email to