Peter,

Per IEC 60364 and BS 7671, you select wire and circuit breakers in
accordance with Chapter 43 (IEC 60364-4-43), "Protection Against
Overcurrent", and Chapter 52 (IEC 60364-5-52), "Selection and Erection of
Wiring Systems."   I have used these references enough to notice no
reference to sizing branch circuits to "the noncontinuous load plus 125
percent of the continuous load."

Moreover, back when times were good, I was able to get approval to take the
IEE Design Course for BS 7671, Requirements for Electrical Installation in
London.   I still have the course material, and looking through the sections
on wire systems, fuses, and circuit breakers, there is no analogy to sizing
the overcurrent protection to 125% of the continuous load like there is in
the US and Canadian electrical codes.  

The analysis of the circuit breaker and fuses and situations are quite a bit
different at times from analysis in North America.  In general, you look at
the time/current curves of the types of circuit breakers and fuses more
closely, and do more math.

Also, in Europe, you can use breakers and fuses as a means of protection
against shock with 411 - Protective Measure:  Automatic Disconnection of
Supply.   Here, you have a measurement of the earth fault loop impedance
(Zs)  co-ordinated with time/current characteristics of fuses and breakers,
with the fuse/breaker opening quickly enough to protect against shock.  This
is generally not possible in North America.

Best regards,

DON GIES 
ALCATEL-LUCENT
SENIOR PRODUCT COMPLIANCE ENGINEER
BELL LABS - GLOBAL PRODUCT COMPLIANCE LABORATORY
600-700 Mountain Avenue
Room 5B-104
Murray Hill, NJ 07974-0636 USA   
Phone: +1 908 582 5978
Fax: +1 908 582 0582
 <mailto:don.g...@alcatel-lucent.com> don.g...@alcatel-lucent.com

MEMBER, ALCATEL-LUCENT TECHNICAL ACADEMY

-----Original Message-----
From: Peter Tarver [mailto:ptar...@enphaseenergy.com] 
Sent: Thursday, May 03, 2012 5:12 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: Circuit breakers in Europe

 

> From: Brian Oconnell  <mailto:[mailto:oconne...@tamuracorp.com]>
[mailto:oconne...@tamuracorp.com]

> Sent: Thursday, May 03, 2012 08:36

> 

> Not certain what OP is attempting, as wire gage is dependent on the 

> fault calc found in electric code, and breaker rating is related to 

> the distribution.

 

In North America, barring circumstances requiring deeper engineering
calculations and supervision, a circuit sized for and protected by a 20 A
breaker cannot carry long continuous currents larger than 16 A.

 

My preexisting notion (for lack of better understanding) for Europe has been
that a 16 A breaker is used to protect a 16 A circuit.  (The "80% Rule" or a
similar rule does not apply in Europe and overcurrent protection is
generally matched to the circuit size.)

 

I'm looking for either confirmation of or contradiction of that notion.

So far, one vote received confirming.

 

 

Regards,

 

Peter L. Tarver

 

 

This email message is for the sole use of the intended recipient(s) and may
contain confidential and/or privileged information. If you are not an
intended recipient, you may not review, use, copy, disclose or distribute
this message. If you received this message in error, please contact the
sender by reply email and destroy all copies of the original message. 

 

-

----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc
discussion list. To post a message to the list, send your e-mail to <
<mailto:emc-p...@ieee.org> emc-p...@ieee.org>

 

All emc-pstc postings are archived and searchable on the web at:

 <http://www.ieee-pses.org/emc-pstc.html>
http://www.ieee-pses.org/emc-pstc.html

 

Attachments are not permitted but the IEEE PSES Online Communities site at
<http://product-compliance.oc.ieee.org/>
http://product-compliance.oc.ieee.org/ can be used for graphics (in
well-used formats), large files, etc.

 

Website:   <http://www.ieee-pses.org/> http://www.ieee-pses.org/

Instructions:   <http://listserv.ieee.org/request/user-guide.html>
http://listserv.ieee.org/request/user-guide.html

List rules:  <http://www.ieee-pses.org/listrules.html>
http://www.ieee-pses.org/listrules.html

 

For help, send mail to the list administrators:

Scott Douglas < <mailto:emcp...@radiusnorth.net> emcp...@radiusnorth.net>

Mike Cantwell < <mailto:mcantw...@ieee.org> mcantw...@ieee.org>

 

For policy questions, send mail to:

Jim Bacher:  < <mailto:j.bac...@ieee.org> j.bac...@ieee.org>

David Heald: < <mailto:dhe...@gmail.com> dhe...@gmail.com>


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://listserv.ieee.org/request/user-guide.html
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to