In general, ok. And this is what the OP should be able to discern. WV is 
deceptively simple. The sqrrt(2) factor should be relied upon to only to 
provide the equivalent DC test voltage, not in calculating WV. In my world of 
power conversion there are some very hi crest factors, and some equipment 
environments depend too much on the 'standard ' 2500V impulse (OV II, 240 
mains) for determination of test level and spacing. And as a cable is external 
to equipment, there could be many other considerations for spacing and 
materials selection. Finally, the mfr has to be able to provide complete 
conditions of acceptability for the equipment that his 1120V cable is connected 
to.

BTW, did Mr. Perkins or Mr. Nute do some seminars for this year's ISPCE? They 
typically talk about this stuff.

Brian


From: Doug Powell [mailto:doug...@gmail.com] 
Sent: Monday, May 12, 2014 11:15 AM
To: Brian Oconnell
Cc: emc-pstc
Subject: Re: [PSES] Creepage and RMS

Something to keep in mind,

Peak Voltages (spikes, impulses, flyback, laser ignition, etc.) are more a 
concern for clearances than for creepage.  Committees build creepage tables in 
slightly different ways and they sometimes ignore the relationships of Vrms, 
Vpk and Vdc which are often related by 1.414 and so on.  On the clearance 
tables this is a somewhat less common practice, especially in secondary 
circuits where interpolation is allowed.  One of the main keys is if you make 
allowance for high peak voltage values in clearance, the rule "creepage cannot 
be less than clearance" applies.  On occasion, creepage calculations will come 
in lower than clearance in which case the creepage number must be automatically 
bumped up to match the clearance.

thanks, -doug

Douglas E Powell
http://www.linkedin.com/in/dougp01 

On Mon, May 12, 2014 at 11:45 AM, Brian Oconnell <oconne...@tamuracorp.com> 
wrote:
The issue with some 60664 tables is that it is (for 0 to 2km) based on 
Paschen's Law, which is for a simple homogenous e-field. So creepage via RMS is 
an incomplete analysis.

As others have stated, spacing should be determined by both peak and RMS. And 
because too many do not measure WV correctly, I strongly suggest reading papers 
and articles by P. Perkins and R. Nute on this subject, and "The physical 
fundamentals of low-voltage insulation co-ordination" by Klaus Stimper.

In a very nutty shell, you need to determine the following for the intended 
end-use environment:
 - OV category
 - CTI of materials
 - pollution degree
 - atmospheric chemistry
 - frequency-based di-electric heating
 - WV for the complete range of rated operating conditions

Have rejected more than one component mfr's CB reports due to incorrect 
interpretations of IEC60664 and calculations of 'RMS' (am looking at you people 
in NRTLs/SCCs/NBs). Finally, the OP indicated that "Creepage is based on the 
RMS value of the voltage so is based on 1120 V", which indicates a reference a 
particular safety standard. What does that standard say about WV measurements 
for the determination of spacing and test voltages ?

Brian

----- Original Message -----
From: ce-test, qualified testing bv - Gert Gremmen
Sent: 05/12/14 03:20 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Creepage and RMS
 
I have a question on creepage distances.
A product creates a saw tooth High voltage
of 2000 Vpeak  The VRMS measured on the scope
on a full period equals 1120 V

Creepage is based on the RMS value of the voltage
so is based on 1120 V.

Now the frequency of the sawtooth is 3 Hz.
Should I still consider the RMS value,
and at what frequency should I consider this
as a DC value in regard to creepage....

Anyone aware of the IEC 60664 standard in respect
to low frequency signals ??

Regards,

Ing.  Gert Gremmen, BSc

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <emcp...@radiusnorth.net>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to