Dear Boštjan:

You said:

Input voltage above 60Vdc can be treated as TNV-2 circuit and according to the 
standard, it is enough to have basic insulation input to output, however, fault 
condition tests still need to be conducted.

So basic + supplementary is not always required if input is >60VDC.

A TNV-2 circuit can be up to 71 volts peak or 120 volts d.c., but it cannot be 
accessible (to an ordinary person) or connected to a SELV circuit.  The 
separation requirements between TNV-2 and SELV/accessible parts is basic 
insulation and, if necessary, fault tests.

If a dc/dc converter generates greater than SELV in its operation but less than 
71 volts peak or 120 volts d.c., I suppose the circuit can be classed as TNV-2, 
although this seems strange to me.  Same for 71 volts peak or 120 volts d.c 
supply circuit to the converter.

(If the output remains SELV during and after a fault test of basic insulation, 
the test proves that the basic insulation is not necessary; this is a flaw in 
the standard.)


Best regards,
Rich



-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to