I'd restate Dave's case below to say:  PE's are really only required for 
Public Sector work.  Industrial/commercial products are certified (where 
necessary) by NRTL testing, and - as Brian has noted - by application of 
CEC/NEC. Brian Kunde's situation appears to be that NEC and CEC have 
conflicting interpretations of what allows for a safe installation. 1.  "dry 
type" is any transformer not encased in oil or other cooling dielectric media.  
It can be encapsulated.  See UL 5085 or CSA C22.2 No.66.1 to be sure.2.  
Ideally, the vendor has guidelines backed up by test data, or if it's CSA 
listed, their file provides guidance;  but that may not be judged suitable to 
your application.  When confronted with a picky inspector (right or wrong), you 
get into a difficult place.  I agree with you that a 2 or 2.25 A slo-blow fuse 
is best, esp. when the vendor says 1.8 is too small and you have to go looking 
look for special long-delay types (which will vary, thereby pose reliability 
problems).  However, an inspector is difficult to outflank, for reasons which 
are generally all good. So, if #2 (mfr. test data) doesn't resolve the 
situation, I see two alternatives:  2a:  have test data showing that ~2A 
"sustained"** current does not lead to temperatures that lead to an insulation 
breakdown, and present that to the inspector.2b:  have an NRTL do a field label 
of the equipment to allow the inspector to "hang his safety hat" on the NRTL 
report.  **  The time that this current needs to be sustained would be in 
either UL 5085-3 or C22.2 #66.1 under temperature or abnormal testing (sorry, 
don't have them handy) in real world terms, this is 10~15 min. but in some 
cases is stretched out until the XF gets to a stable temperature. Good luck! 
Brian Gregory
720-450-4933

---------- Original Message ----------
From: "Nyffenegger, Dave" <dave.nyffeneg...@bhemail.com>
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] NEC vs CEC for Transformer Protection
Date: Sun, 29 Mar 2015 16:03:28 +0000

"Engineers" doing any sort of direct public work in the U.S. must be licensed 
or working under a (licensed) PE (in which case they are not an engineer in the 
eyes of the law) regardless of the discipline.  This applies to private 
consulting firms doing public work or within government agencies.  The same 
"industrial exception" exists in the US and this does carry through to products 
for sale.

-Dave


From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Friday, March 27, 2015 1:27 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] NEC vs CEC for Transformer Protection
 
Please help.
 
We have a product, laboratory equipment, that has a 330 watt 1:1 230Vac 
isolation transformer.  330w / 230V = 1.34 amps.
 
To protect this transformer we applied the US-NEC table 450.3(B) to where the 
primary protector can be up to 300% of the of 1.34 amps. The transformer 
manufacturer recommended a 2.25A time lag circuit breaker to handle the inrush 
current from this transformer. Life is good.
 
Then, we had this product inspected in Canada to which they apply the Canadian 
Electric Code section 26-256, &ldquo;Overcurrent protection for dry=type 
transformer circuits rated 750V or less&rdquo;, which states the primary 
overcurrent protection device cannot exceed 125% of the transformer current 
rating. That&rsquo;s 134 amps * 1.25 (125%) = 1.78 amps. Rounded up, the 
inspector said we had to use a fuse or breaker no larger than 1.8 amps.
 
We notified the transformer manufacturer who said (and we confirmed) that 1.8 
amp protection device will nuisance trip due to Inrush Currents.
 
The transformer CSA inspector and a representative from Littelfuse both are 
telling us that the inspector applied the wrong section of the Electric Code 
and that section 26-254, &ldquo;Overcurrent protection for power and 
distribution transformer circuits rated 750 V or less, other than dry-type 
transformers&rdquo; should be applied.  This section of the CEC does alien 
better with the US-NEC.
 
However, what is a &ldquo;dry-type transformer&rdquo;??  From my understanding, 
our transformer is not an oil or dielectric cooled transformer and it should be 
considered a &ldquo;Dry-Type&rdquo; transformer which would make the inspector 
correct in applying section 26-256.
 
Am I missing something here?  It makes sense that the NEC and CEC should track 
closely in this regard but it appears as Canada&rsquo;s requirement for 
dry-type transformers trump these low current transformers that would be 
impossible to properly protect according to their code.
 

----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to