>This lab area has surge protection, so again, we believe the problem is 
some kind of low voltage transient, voltage dropout, or >waveform 
distortion that we have been unable to detect and simulate.

Was it tested against IEC 61000-4-11 (voltage dips, short interruptions, 
variations ) ? 
_______________________________________________________________________________ 


Ralph McDiarmid  |   Schneider Electric   |  Solar Business  |   CANADA  | 
  Regulatory Compliance Engineering 
 



From:
"Kunde, Brian" <brian_ku...@lecotc.com>
To:
EMC-PSTC@LISTSERV.IEEE.ORG, 
Date:
09/17/2015 06:40 AM
Subject:
Re: [PSES] Unexplained High Fallout of Power Supplies



Bob and all.

Good question. Before I answer your questions, let me describe the typical 
architecture of the products that we make.

Our instruments (laboratory equipment) are single phase 230VAC 50/60hz 
which powers two separate internal circuits; one being a relatively low 
current electronics powered by a purchased over-the-shelf 24Vdc power 
supply, and second, a high current furnace of some type; inductive, 
electrode, resistive heating elements, etc.. Because of the high overall 
current of the instruments, typically between 30A and 50A, the instrument 
is plugged into a high current branch circuit with a huge high current 
line filter. Internally, we usually have a smaller supplementary 
over-current protector (5, 10 or 15 amp) driving the lower current 
non-furnace electronics such as the dc power supply, cooling fans and 
blowers, etc..

The issues we are having are with these purchased power supplies blowing 
up. And because we pre-test power supplies and our finished products so 
extensively and we are not able to cause a power supply failure with the 
same damage pattern as we are seeing in the field, we believe that in the 
real world our products are seeing some kind of condition that we are not 
able to simulate in our EMC Lab. Identifying and understanding such 
conditions is our goal at this time.

We use no additional inrush limiting other that what is built into the 
power supplies themselves. Other than a thermistor of some kind, how can 
the inrush be limited?

We have also seen on several occasions in the field where a power supply 
will blow up in one instrument which causes the power supply in a nearby 
instrument to also fail.

Two weeks ago we had an "event" occur right here at our own campus in our 
Application Lab where 40-50 instruments of different models and ages are 
being used daily to develop test methods. An instrument was power on but 
was not running an analysis (high current furnace wasn't running in what 
we call Standby-mode). BAM!! The 24Vdc power supply blew up. We sent two 
R&D engineers who have been working on our fallout problem in the field to 
investigate. They found the power supply had failed in the same way as 
those in the field. No other failed component in the instrument was found. 
The power supply was replaced and the instrument was once again 
functional. AS THE Engineers turned to walk back to their office, BAM!! 
The power supply blew up in the instrument installed NEXT to the one they 
just repaired. This second instrument is a different model with a 
different manufacturer of power supply. An AC Power Line monitor/analyzer 
was installed on the AC Mains circuit and has been c!
 hecked every morning since. No unusual transients or power dropouts have 
been detected.

This lab area has surge protection, so again, we believe the problem is 
some kind of low voltage transient, voltage dropout, or waveform 
distortion that we have been unable to detect and simulate.

Thanks to all.

The Other Brian

-----Original Message-----
From: Bob LaFrance [mailto:b...@creare.com]
Sent: Thursday, September 17, 2015 8:46 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Unexplained High Fallout of Power Supplies

I am curious to what you are using for inrush limiting.  Sorry if you 
already told us but I missed that.

Regards,
Bob LaFrance
N9NEO
Design Engineer
Creare Inc.
16 Great Hollow Road
Hanover, NH
603-640-2539





-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to