I needed to add to my previous contribution to that the  parameter that 
controls this is called TCL value.
(John et all: = Transferse Conversion Loss ;<)) . The EMC world has been using 
LISNS
for decades now that simulate a LCL  (Longitudinal Conversion Loss) value of 
the connected mains cable of -6 dB.
(for a cable LCL and TCL are normally the same)
Something to think about...

Regards,

Ing. Gert Gremmen
Approvals manager
------------------------------------------------------------------------------------


+ ce marking of electrical/electronic equipment
+ Independent Consultancy Services
+ Compliance Testing and Design for CE marking
     according to EC-directives:
        - Electro Magnetic Compatibility 2004/108/EC
        - Electrical Safety 2006/95/EC
        - Medical Devices 93/42/EC
        - Radio & Telecommunication Terminal Equipment 99/5/EC
+ Improvement of Product Quality and Reliability testing
+ Education

Web:    www.cetest.nl (English) 
Phone :  +31 10 415 24 26
-------------------------------------------------------------------
This e-mail and any attachments thereto may contain information 
that is confidential and/or protected by intellectual property rights 
and are intended for the sole use of the recipient(s) named above. 
Any use of the information contained herein (including, but not 
limited to, total or partial reproduction, communication or 
distribution in any form) by persons other than the designated 
recipient(s) is prohibited. If you have received this e-mail in error, 
please notify the sender either by telephone or by e-mail and 
delete the material from any computer. 
Thank you for your co-operation.

From: Richard Marshall [mailto:richard.marshal...@btinternet.com] 
Sent: Friday 1 April 2016 11:48
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

Ken says
       "I seem to recall Michel Mardiguian writing that the relaxed dm could 
transform into cm causing big problems.  That seems counter-intuitive at best."


        Think about it this way.  DM is being transmitted along a wire PAIR 
that we must view as an rf transmission line, which is balanced UNTIL it meets 
some discontinuity.

( What discontinuity? 
- A branch cable with a single-pole switch that is open, leaving a branch wire 
hanging on the other pole.
- A device with a single class X capacitor from neutral to ground.
- A solid ground connection to the neutral wire.
- A wide separation between Line and Neutral conductor (Think 2-way light 
switching)
- - etc )

At a discontinuity that is unbalanced relative to ground (as all the above 
are), there is conversion of DM power into CM because unequal amounts of the 
balanced power in each wire are diverted to ground. 
The maths. are complicated because of the various and different values of 
Characteristic impedance Zo between wires and from each wire to ground, but the 
mechanism for power transfer is clear.

There have been studies of this in the last 10/15 years suggesting that typical 
power transfer coupling from DM to CM in a real mains power network at 230 
volts ( I do not know of any at 115 volts, perhaps others do...) involves only 
about 10dB power loss at some frequencies where the wiring is resonant.

So whilst there may be a case for allowing a bit more DM than CM, there can be 
no technical case for allowing 20dB or more of excess DM.  Not on ordinary 
power distribution circuits.


Richard

Richard Marshall Laboratories,
30 Ox Lane, Harpenden, Herts.,    AL5 4HE, UK 
+44 (0)1582 460815     www.design-emc.co.uk
Member of the EMC Industry Association

From: Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent: 30 March 2016 21:59
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

With the dm limit 20 dB relaxed, the dm filter design would be simplified.  As 
I said, an industry study said it would save $35 million a year for the power 
supply industry. I'm not sure if it was Art Wall as much as the old guard who 
were involved in the original work not liking a fresh look at it.

I seem to recall Michel Mardiguian writing that the relaxed dm could transform 
into cm causing big problems.  That seems counter-intuitive at best. The 
opposite is way more likely. So my takeaway was that they didn't want to 
consider a change to how they had set thing up.

Ken Javor
Ph. (256) 650-5261 

________________________________________
From: "Grasso, Charles" <charles.gra...@echostar.com>
Date: Wed, 30 Mar 2016 19:01:00 +0000
To: Ken Javor <ken.ja...@emccompliance.com>, "EMC-PSTC@LISTSERV.IEEE.ORG" 
<EMC-PSTC@LISTSERV.IEEE.ORG>
Conversation: [PSES] Commom mode current vs. differential mode current and LISN
Subject: RE: [PSES] Commom mode current vs. differential mode current and LISN

Hello Ken - I remember the setup and demo to Art Wall of the FCC during the 
1999 EMC Symposium here in Denver.
In spite of your best efforts it was clear that Art was not "persuaded" !!
 
The impact on the industry (as I recall) would be much cheaper filters...(if 
any).
 
 

Best Regards
Charles Grasso
Compliance Engineer
Echostar Communications
(w) 303-706-5467
(c) 303-204-2974
(t) 3032042...@vtext.com
(e) charles.gra...@echostar.com
(e2) chasgra...@gmail.com
 

From: Ken Javor [mailto:ken.ja...@emccompliance.com] 
Sent: Tuesday, March 29, 2016 3:48 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

The report on which the old 48 dBuV class B CE limit was based did develop that 
based on the conducted susceptibility of AM and shortwave radios, but it also 
noted that limit functioned as an adequate control for common mode noise that 
would radiate as per Doug's observation. Back in the late '90s I presented a 
detailed test report to TC77 showing that if instead of controlling conducted 
emissions at each LISN port, they instead controlled by modes, that dm could be 
relaxed 20 dB to 68 dBuV and the committee took an action item and back then 
said if that were implemented, it would save the power supply industry $35 
million a year.  The work I did was based on using the LISNMATE / LISNMARK 
technology as injection tools injecting pure cm and dm and showing that the 
susceptibility to dm was 20 dB less, because of bulk filter caps on the 
secondary of power supplies, whereas there were no Y-caps and no cm filtering. 
The reason this was missed back in 1977/78 when the report was w!
 ritten was they used a single LISN with neutral through the case.  CM and DM 
flowed in the same path.

Ken Javor
Ph. (256) 650-5261 
________________________________________
From: Doug Smith <d...@emcesd.com>
Reply-To: <d...@emcesd.com>
Date: Tue, 29 Mar 2016 14:31:20 -0700
To: <EMC-PSTC@LISTSERV.IEEE.ORG>, Ken Javor <ken.ja...@emccompliance.com>
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

Hi Ken and the group,

 

I always thought that the FCC measures the wrong quantity for conducted 
emmissions. What shoud be measured is all conductors (two or three including 
phase/neutral/protective earth) together as common mode current as that is what 
radiates from the long power lines causing problems for shortwave receivers and 
Amateur Radio Operators. The old demonstration of conducted EMI into AM radios 
is not so useful, especially today.

 

Below 30 MHz, most devices are not large enough to radiate efficiently, but the 
power wiring is long enough to radiate. I have a case of EMI in my house from 
two Feit Electric LED floodlights that meet conducted emissions, but I can't 
use a hand held, battery powered, shortwave receiver when the two are on except 
to walk quite a distance from that part of the house. The FCC test may catch 
this case, but apparently not for me, as there are only two wires but that is 
not the case for other devices.

 

So phase+neutral could be noisy with respect to protective earth but as long as 
it is balanced by an opposite current on protective earth, radiation should be 
low.

 

Any other Amateur Radio operators want to weigh in on this?

 

Doug (K4OAP, since 1959)

 






On Tue, 29 Mar 2016 16:13:58 -0500, Ken Javor <ken.ja...@emccompliance.com> 
wrote:

Re: [PSES] Commom mode current vs. differential mode current and LISN Disagree. 
Westin had it right. A current probe can be used to isolate either cm or dm 
current. If at any frequency the signal amplitude on individual line and 
neutral conductors are very close, then all you can say is that at that 
frequency either cm or dm predominates, but you can't say which.  With a LISN, 
a separate device must be used. Mark Nave of EMC Services designed a three port 
device (connects to each LISN port and to the EMI receiver) trademarked 
LISNMATE in the 1980s to isolate common mode, and sometime later he produced 
LISNMARK, which isolated DM.  Within the past decade, Ray Adams while at 
Fischer Custom Communications packed both functions in one piece of equipment, 
which if memory serves was named LISNUP.

 EMC Services, Mark Nave's company, is no longer producing his products, but I 
believe the FCC product is still available.

 Ken Javor
 Ph. (256) 650-5261 
________________________________________
From: Elliott Martinson <elliott.martin...@etcconnect.com>
Reply-To: Elliott Martinson <elliott.martin...@etcconnect.com>
Date: Tue, 29 Mar 2016 20:36:18 +0000
To: <EMC-PSTC@LISTSERV.IEEE.ORG>
Conversation: [PSES] Commom mode current vs. differential mode current and LISN
Subject: Re: [PSES] Commom mode current vs. differential mode current and LISN

http://www.hottconsultants.com/techtips/CM_vs_DM%20Conducted_Emission.html
This is a great resource for your question.
  
 Your second point kind of contradicts your first, if it's trying to say what I 
think it is. DM and CM each show up on L, but the same is true for N. It's a 
linear combination of both, so even if L and N are almost equal, you can't say 
anything about the proportion of DM to CM currents.
  
 If they are not equal, then this implies current is travelling back via the 
ground conductor and/or energy's being lost to radiated emissions.
  
 What you need is a physical circuit to do the adding/subtracting of the LISN 
outputs. (otherwise your 3rd bullet point is correct)
  
 Your 4th bullet, well I refer you to the link above.
  

Elliott Martinson
Product Assurance Specialist I
Electronic Theatre Controls
3031 N PLEASANT VIEW RD
 MIDDLETON WI 53562-4809
Work: 608.824.5696 / Cell: 608.209.9897
elliott.martin...@etcconnect.com <elliott.martin...@etcconnect.com> 
  

From: Amund Westin [mailto:am...@westin-emission.no] 
<mailto:am...@westin-emission.no%5D>  
Sent: Tuesday, March 29, 2016 1:23 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] Commom mode current vs. differential mode current and LISN

Please correct me, if I am wrong (that happens quite often ...):

·        Let one wire (L) pass through a current clamp, and you measure the 
combination of current mode and differential mode currents

·        Do the same with wire N. If L and N are (almost) equal, you either 
have major part of DM currents or major part of CM current

·        Let both wire (L and N) pass through a current clamp, and you measure 
the only CM current (DM is canceled)

·         When doing conducted emission test by LISN, you actually get what you 
get. LISN do not see the difference between CM or DM. From LISN measurements, 
you can't say if noise is CM or DM.

B.regards

Amund













 -
----------------------------------------------------------------
 This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

 All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

 Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

 Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
 List rules: http://www.ieee-pses.org/listrules.html 

 For help, send mail to the list administrators:
 Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 

 For policy questions, send mail to:
 Jim Bacher <j.bac...@ieee.org>
 David Heald <dhe...@gmail.com> 
 -
----------------------------------------------------------------

 This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

 All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

 Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

 Website:      http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to 
unsubscribe) <http://www.ieee-pses.org/list.html> 
 List rules:     http://www.ieee-pses.org/listrules.html 

 For help, send mail to the list administrators:
 Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 

 For policy questions, send mail to:
 Jim Bacher  <j.bac...@ieee.org>
 David Heald <dhe...@gmail.com> 

 -
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;emc-p...@ieee.org&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
 Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe) <http://www.ieee-pses.org/list.html> 
 List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
 Scott Douglas &LT;sdoug...@ieee.org&GT;
 Mike Cantwell &LT;mcantw...@ieee.org&GT;

For policy questions, send mail to:
 Jim Bacher &LT;j.bac...@ieee.org&GT;
David Heald &LT;dhe...@gmail.com&GT;

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) 
<http://www.ieee-pses.org/list.html> 
List rules: http://www.ieee-pses.org/listrules.html 

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 
-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>
All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html
Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.
Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html 
For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org> 
For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org>
David Heald <dhe...@gmail.com> 

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to