I would recommend developing a robust program for testing electromagnetic 
susceptibility for any system that uses software for safety functions. You may 
be able to accept transient behavior for computers and other products, but not 
for safety systems. It will likely not be acceptable to have an event that 
requires user action for recovery. 

I have seen things as simple as having ESD put an IC into a latch up condition. 
ESD or EFT could cause other transient effects with undesirable results. 
Depending on the inputs to the safety system, radiated or magnetic field 
immunity tests may be required at elevated levels to ensure robustness.

I'll also add to the recommendation others have given for using a state 
machine. In my opinion, it makes review and testing much easier. You will 
likely want to make sure that if anything does go wrong, the system fails into 
a safe state, and that can be easier to check in a state machine where there 
are only a limited number of states possible. 

Ted Eckert
Microsoft Corporation
The opinions expressed are my own and do not necessarily reflect those of my 
employer.

-----Original Message-----
From: Brian O'Connell [mailto:oconne...@tamuracorp.com] 
Sent: Wednesday, August 3, 2016 12:03 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] SAFETTY FEATURES controlled by ....SOFTWARE

Would suspect principle reason is that FPGAs and ASICS, when viewed as a 'code 
block', tend to be deterministic and relatively easy to map a finite number of 
paths, so the coverage analysis comes as part of the design, and more so when 
done as a pure state machine. That said, VHDL/system C *is* code, and DO 
178/254 and EN50129 have discussed this stuff (latter is for trains).

Military software safety tends to suck, because no matter what happens, the end 
result almost always needs the weapon system to be able to say "boom". That is, 
the mission-first philosophy.

PALs and ROMs are essentially pure state machines. And Von Neumann stuff, 
cannot be eliminated for many designs, as it tends to drive or receive from a 
parallel device where you cannot keep the control loop closed. So the only 
truly non Von Neumann hardware would be ASICs and FPGAs, but there is still a 
microcontroller or DSP core in there that is a serial Von Neumann machine. So 
code safety assessment remains a dog's breakfast. Woof.

Brian


-----Original Message-----
From: Gary McInturff [mailto:gary.mcintu...@esterline.com] 
Sent: Wednesday, August 03, 2016 11:06 AM
To: Brian O'Connell; EMC-PSTC@LISTSERV.IEEE.ORG
Cc: Gary McInturff
Subject: RE: [PSES] SAFETTY FEATURES controlled by ....SOFTWARE

Well software types are devious by nature and probably one of the reasons the 
FAA kinda-sorta strong arms developers in to using ASICS, PALS and EPROMS and 
the like. The theory is that this devices are not Von Neumann architecture with 
various entry/exit decision points that lead to a plethora of test cases, and 
as such have a finite number of test vectors which have exact outputs which can 
be measured and verified. 2^N (number of data pins). Test vectors can be 
written and run which report the output state of the device exactly and 
repeatably. They also have a software standard that would be used for 
multipurpose processors etc - but as I understand it is really pretty ugly and 
intensive.
One might consider putting the safety critical features inside a PAL etc.

-----Original Message-----
From: Brian O'Connell [mailto:oconne...@tamuracorp.com] 
Sent: Wednesday, August 03, 2016 10:10 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [EXTERNAL] Re: [PSES] SAFETTY FEATURES controlled by ....SOFTWARE

Dear Hardware People on the third rock from Sol,

Software beings (self included) are idiotically clever and tend to be rather 
subversive. We can devise profoundly evil schemes that can 'go around' fault 
conditions in electrical components that forces our equipment to pump out 
giggle watts of power while the surrounding creation melts down.

Pro-tips for future compliance engineers:
0. Never trust any software types; not even a single one among us. If your 
significant other is a software engineer, learn to sleep with eyes open.
1. learn how to read code like a book (which means you will need to understand 
the language's basic syntax and structural characteristics).
2. learn how to run code in an emulator that can run under fully static clock 
conditions.
3. learn how to determine code coverage.
4. carry a large hammer to meetings with the s/w dev team.

Brian


From: Richard Nute [mailto:ri...@ieee.org] 
Sent: Wednesday, August 03, 2016 9:41 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] SAFETTY FEATURES controlled by ....SOFTWARE

I have virtually no experience in software safety.  I'm a hardware guy.

I suggest simulating failures in the sensors (hardware) that gives the software 
info about what state the battery is in.  And, simulating failures of the 
hardware controlling the charging, discharging, and overcharging the battery.  
In this way, you have accounted for the worst-case failures of both the 
hardware and the software.  

Rich


From: Bolintineanu, Constantin [mailto:cbolintine...@tycoint.com] 
Sent: Wednesday, August 03, 2016 7:33 AM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: [PSES] SAFETTY FEATURES controlled by ....SOFTWARE


Dear Colleagues,

I would like to kindly ask those who have an extensive experience regarding the 
above subject, to share their opinion about the following aspect:

Having a circuit which is charging a battery, and having it controlled and 
protected  by SOFTWARE ONLY from the point of view of CHARGING , DISCHARGING, 
OVERCHARGING,

1. How do you think that SINGLE FAULT CONDITIONS shall be applied? (without 
SOFTWARE working at all? Or by providing a fault on the component where the 
SOFTWARE is stored? OR BOTH
2. Which conditions do you think that shall be imposed to the software and/or 
to the memory in which it is stored?

Any other suggestions/observations/comments are more than welcome.

Sincerely,

Constantin Bolintineanu P.Eng.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)