John,

One transformer I’m currently looking at has the following specs:

Input = 80-300V (230V Nom) 50/60hz
Output = (@ 230V input) 2 x 5.0V @ 0.0025A
Output Power = 0.025 VA
Insulation Class “F” (155ºC).

I don’t currently have a sample transformer to measure the primary impedance.

It would be nice if the manufacturer would provide information on how to 
properly protect this device.  Any suggestions?

Thanks,
Brian


From: John Woodgate [mailto:jmw1...@btinternet.com]
Sent: Monday, October 31, 2016 12:54 PM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: RE: [PSES] Low current Transformer OC Protection

This is why small transformers that don't need a fuse were developed. They have 
a special type of coated wire for the primary winding, which goes quietly 
open-circuit if it gets too hot. However, I suppose your product standard might 
not allow them.

The limits based on load current are technically  indefensible, but that may 
not help. The right way to determine what fuse you want is to take account of 
the worst-case inrush current, which occurs when the core is left fully 
magnetized at switch-off and the supply is switched on at the point where it is 
trying to magnetize it further. The current is then limited only by the DC 
resistance of the primary winding, and you need to look at the fuse I^2T curves 
to select one (usually it needs a T-type) that doesn't fail on inrush but does 
fail on about 1.5 times the full-load current of the transformer.

That is most unlikely to be the 1.1 mA you mention (32 mA being 3000% of it).  
I doubt you can get a transformer rated at less than about 1.5 VA, which with 
120 V input means a full-load primary current of  12.5 mA. I measured one like 
that and the primary resistance is 600 ohms, so the inrush current could be 200 
mA. That means that you need a fuse that will pass 200 mA for at least half a 
cycle of 60 Hz, while breaking within an acceptable time at, say,  2 x 12.5 mA. 
It may indeed be difficult to find one, but at least you know what the 
component is actually required to do.

I suspect that you can find a fuse that works for a 3 VA transformer; 1.5 VA is 
very extreme.

With best wishes DESIGN IT IN! OOO – Own Opinions Only
www.jmwa.demon.co.uk<http://www.jmwa.demon.co.uk/> J M Woodgate and Associates 
Rayleigh England

Sylvae in aeternum manent.

From: Kunde, Brian [mailto:brian_ku...@lecotc.com]
Sent: Monday, October 31, 2016 3:59 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: [PSES] Low current Transformer OC Protection

Greeting Experts.

I often run into issues with safety inspectors during Field Evaluations 
regarding overcurrent protection of small transformers that are not thermally 
protected.

These small transformers can draw such small amounts of current on both the 
primary and secondary, that finding a fuse within 300% (250%) of the primary or 
167% of the secondary max load current is impossible.

Even if we use the smallest fuse we can find (Littelfuse 218 series is 0.032A), 
this value can be over 3000% of the load current.

Even if we provide thermal test data to an inspector, they will reply that our 
data is worthless to them as they only accept data from their own lab or other 
NRTLs.

So am I missing something here?  The NEC says I can use the next highest common 
fuse value. Is this acceptable even if the value is exceeds 1000% of the load 
current?

Has anyone ran across this issue with inspectors?  How best do we protect small 
transformers and meet the electric codes?

Thanks in advance.
The Other Brian



________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to