Hi Doug;
Have you taken a look at IEC 60664 to see if has a similar statement or
provides any clarification?  Maybe what you're seeing is just a mistake in
60950-1, 2nd ed...

-Ken

On Wed, Mar 29, 2017 at 8:48 PM, Doug Powell <doug...@gmail.com> wrote:

> All,
>
> I am reviewing the requirements of "*2.10.3.3 Clearances in primary
> circuits" *and it seems interesting to me that the math is off by just a
> little bit.  In particular "For an AC MAINS SUPPLY not exceeding 300 V
> r.m.s. (420 V peak)". When in actuality the calculated peak of 300 Vrms is
> 424 Vpeak.  Using three significant digits instead of two.  This value is
> important to spacings determination in that it invokes using tables 2K plus
> 2L instead of table 2K alone.  I checked the Edition 2 of IEC, ANSI/UL and
> CSA standards and they all have the same statement.  Edition 1 of IEC
> 60950-1 does not include this value within parenthesis which tells me it
> was probably added as a clarification by the committee in Edition 2.
>
> I am one to build excel-based spacings calculators and this has changed
> the math somewhat, rounding up to the nearest 10 Volts
>
> =IF(10*ROUNDUP(Vrms*SQRT(2)/10,0)>420,"Tables 2K + 2L","Table 2K")
>
> instead of using
>
> =IF(Vrms*SQRT(2))>424,"Tables 2K & 2L","Table 2K")
>
>
> (Note: use of =MROUND() could potentially round down and not up)
>
> In several other sections of the standard another pair of voltages appear
> together in at least 8 locations and are rendered *"42,4 V peak, or 60 V
> d.c"*; which is correct for three significant digits.  I know the
> consequences are probably minimal and it has raised my curiosity as to why
> this happened. Was anyone in this forum present during this part of the
> revision discussions and can shed some light?
>
>
> thanks Doug
>
>
> --
>
> Douglas E Powell
>
> doug...@gmail.com
> http://www.linkedin.com/in/dougp01
> -
> ----------------------------------------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to &LT;
> emc-p...@ieee.org&GT;
>
> All emc-pstc postings are archived and searchable on the web at:
> http://www.ieee-pses.org/emc-pstc.html
>
> Attachments are not permitted but the IEEE PSES Online Communities site at
> http://product-compliance.oc.ieee.org/ can be used for graphics (in
> well-used formats), large files, etc.
>
> Website: http://www.ieee-pses.org/
> Instructions: http://www.ieee-pses.org/list.html (including how to
> unsubscribe) <http://www.ieee-pses.org/list.html>
> List rules: http://www.ieee-pses.org/listrules.html
>
> For help, send mail to the list administrators:
> Scott Douglas &LT;sdoug...@ieee.org&GT;
> Mike Cantwell &LT;mcantw...@ieee.org&GT;
>
> For policy questions, send mail to:
> Jim Bacher &LT;j.bac...@ieee.org&GT;
> David Heald &LT;dhe...@gmail.com&GT;
>

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to