So in this context, what does “transportable” mean?  I always thought it meant 
tools that are used on the move, but I cannot image using a table saw while it 
is moving.
Thanks,
The Other Brian

From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Wednesday, January 31, 2018 2:37 PM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] GFCI vs GFPE


No, It isn't all about hand-held. The list of Sections dropped below my screen. 
The relevant standard is probably:

IEC 62841-3-1:2014<https://webstore.iec.ch/publication/7454>

Edition 1.0 (2014-06-04)

Electric motor-operated hand-held tools, transportable tools and lawn and 
garden machinery - Safety - Part 3-1: Particular requirements for transportable 
table saws



John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates www.woodjohn.uk<http://www.woodjohn.uk>

Rayleigh, Essex UK
On 2018-01-31 18:57, John Woodgate wrote:

IEC 62841 is a multi-part standard with 23 documents. But it's all about 
'hand-held', so unless the 300 lb product is intended for Superman or King 
Kong. they don't apply.

Wiring codes do not specify requirements for load products, except in very 
general terms. Safety requirements for products are in product safety standards.

In Europe, a cut-off saw is a 'machine', so the Machinery Directive applies. 
This influences which safety standard is permitted to be applied to the product.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates www.woodjohn.uk<http://www.woodjohn.uk>

Rayleigh, Essex UK
On 2018-01-31 18:38, Kunde, Brian wrote:
Most interesting.  Thanks.

From: msherma...@comcast.net<mailto:msherma...@comcast.net> 
[mailto:msherma...@comcast.net]
Sent: Wednesday, January 31, 2018 1:27 PM
To: Kunde, Brian
Cc: EMC-PSTC
Subject: [BULK] Re: [PSES] GFCI vs GFPE
Importance: Low

IEC TC 116 in in the process of folding the 60745-1 (hand held motor operated 
tool) standards into the 62841 series (Electric motor-operated hand-held tools, 
transportable tools and lawn and garden machinery). See their dashboard at:
http://www.iec.ch/dyn/www/f?p=103:30:13397277133783::::FSP_ORG_ID,FSP_LANG_ID:4112,25

My reference was not from a part 2, but actually from section 21.16 of 60745-1:
"

Tools employing liquid systems shall protect the user against the increased 
risk of
shock due to the presence of liquid under conditions of normal use and the 
faults of the liquid
system.
Tools employing liquid systems shall be either:
• of class III construction;
• of class I or class II construction and be provided with a residual current 
device and comply
with 14.4, 14.5 and 14.6; or
• of class I or class II construction and be designed for use in combination 
with an isolating
transformer and comply with 14.4 and 14.5.
"
Section 14.4 describes using a salt water mix to simulate overfilling or 
misassembling and then testing for leakage.

I do not know whether your product falls within scope of 62841; perhaps your 
favorite NRTL could help. Your favorite NRTL might even have someone on the 
committee who could help with a question.

Mike

________________________________
From: "Brian Kunde" <brian_ku...@lecotc.com<mailto:brian_ku...@lecotc.com>>
To: msherma...@comcast.net<mailto:msherma...@comcast.net>
Cc: "EMC-PSTC" <EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>>
Sent: Wednesday, January 31, 2018 11:58:25 AM
Subject: RE: [PSES] GFCI vs GFPE

Mike,

Thanks for your offer. I assume the requirement for RCD is limited to hand-held 
or portable power tools that uses water. This is interesting because I didn’t 
know this was a requirement.

In our case, the cut-off saw we are looking at weighs over 300 lbs. Defiantly 
not hand-held any probably not considered portable (depending on your 
definition).

Do you know if there are similar requirements for non-hand-held electric 
saws/tools?

Thanks,
The Other Brian

From: msherma...@comcast.net<mailto:msherma...@comcast.net> 
[mailto:msherma...@comcast.net]
Sent: Wednesday, January 31, 2018 12:29 PM
To: Kunde, Brian
Cc: EMC-PSTC
Subject: Re: [PSES] GFCI vs GFPE

Brian --
I think I've seen a Part 2 standard for 60745-1, as I recall, that required a 
RCD if the tool used water and the water ended up in the wrong place 
electrically. If you'd like a screen shot of the section, I can probably find 
it for you.
Mike Sherman
Graco Inc.

________________________________
From: "Brian Kunde" <brian_ku...@lecotc.com<mailto:brian_ku...@lecotc.com>>
To: "EMC-PSTC" <EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>>
Sent: Wednesday, January 31, 2018 11:06:36 AM
Subject: Re: [PSES] GFCI vs GFPE

Where Pete stated, “The Euro systems use of RCDs require this protection in 
many installations (but I’m not familiar with the installation code details)”. 
This “Code” is probably what I am seeking.

Has anyone run across a Code rule that requires the Product to employ a RCCB 
within the product?  If the local electrical code requires a RCCB, cannot this 
protection be provided as part of the site protection?  Why burden the cost of 
a product where such a requirement may only be necessary in a small percentage 
of installations?

The main purpose of my question on this topic is cost.  Here in the USA, a GFCI 
receptacle is very inexpensive; costing around $10 at most home stores.  But a 
3-phase RCD Circuit Breaker can cost $300-$400.  On some products, such as a 
tile saw that uses water, this can more than double the cost of the entire 
product.  So knowing when and where they are required is very important.

Thanks again to everyone for your consideration.  From what I have read so far 
on this topic, it is a moving target as electric codes from different states 
and countries are always evolving and the code governing the requirements of 
RCDs and GFCIs are common to change.

Thanks,
Brian


From: John Woodgate [mailto:j...@woodjohn.uk]
Sent: Wednesday, January 31, 2018 11:13 AM
To: Kunde, Brian; EMC-PSTC@LISTSERV.IEEE.ORG<mailto:EMC-PSTC@LISTSERV.IEEE.ORG>
Subject: Re: [PSES] GFCI vs GFPE


You can rely on the recent post in this thread by Pete Perkins.

John Woodgate OOO-Own Opinions Only

J M Woodgate and Associates www.woodjohn.uk<http://www.woodjohn.uk>

Rayleigh, Essex UK
On 2018-01-31 15:52, Kunde, Brian wrote:
Thanks for the input everyone.

I know that GFCI protectors in North America will trip between 4-6mA.  Do other 
countries, such as Europe, have the same requirements?
Or are 30mA protectors used in Europe? If so, does Europe use 30mA ground fault 
protectors because of nuisance tripping even though the studies have shown that 
30mA can be fatal?

These 3-phase cut-off saws that I’m evaluating comes with a power cord, but no 
plug. They can be field wired or a plug could be added and plugged it into a 
receptacle.  The choice is left up to the customer.

The saw uses water but the work environment would not normally be considered a 
“wet location”.  It would not be used in a construction location.

So again, I’m trying to figure out why the saw manufacturer used the expensive 
30mA ground fault breakers in their product.

Thanks,
The Other Brian





________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
&LT;emc-p...@ieee.org<mailto:emc-p...@ieee.org>&GT;

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas &LT;sdoug...@ieee.org<mailto:sdoug...@ieee.org>&GT;
Mike Cantwell &LT;mcantw...@ieee.org<mailto:mcantw...@ieee.org>&GT;

For policy questions, send mail to:
Jim Bacher &LT;j.bac...@ieee.org<mailto:j.bac...@ieee.org>&GT;
David Heald &LT;dhe...@gmail.com<mailto:dhe...@gmail.com>&GT;

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.
-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org<mailto:emc-p...@ieee.org>>

All emc-pstc postings are archived and searchable on the web at: 
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to 
unsubscribe)<http://www.ieee-pses.org/list.html>
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org<mailto:sdoug...@ieee.org>>
Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>>

For policy questions, send mail to:
Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>>
David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>>


________________________________
LECO Corporation Notice: This communication may contain confidential 
information intended for the named recipient(s) only. If you received this by 
mistake, please destroy it and notify us of the error. Thank you.

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to