GFCI = Ground Fault Circuit Interrupter

RCD  = Residual Current Device

 

In North America, GFCI’s typically are included in an outlet that is part of a 
branch circuit.  The GFCI may have a number of outlets downstream.  Under 
normal conditions, the residual leakage current in the downstream outlets and 
equipment connected to them is not zero, and can be a significant portion of 
the 5 mA (nominal) trip current.  So, when a person gets across the 
GFCI-protected branch circuit and causes a trip, the current through the body 
is the difference between the residual leakage current and the 5 ma trip 
current.  So, in such cases, the body current can be much less than the 5 mA 
trip current.

 

The same is the case for the 30 mA RCD in Europe.  However, the RCD is 
installed in the breaker panel for an entire branch circuit, not a portion of 
the branch circuit.  So, the residual leakage current is higher, maybe as much 
as twice that of North America.  And, the voltage, 230, is about twice, so the 
leakage current due to the higher voltage is almost twice that of North 
America.  Using these numbers, the European trip equivalent to the 5 mA trip 
would be about 20 mA or more.   However, the RCD is rated at 30 mA, so when a 
person gets across an RCD-protected circuit, the body current will be much less 
than the 30 mA trip current.

 

Rich

 

 

From: Pete Perkins <00000061f3f32d0c-dmarc-requ...@listserv.ieee.org> 
Sent: Thursday, February 3, 2022 1:58 PM
To: EMC-PSTC@LISTSERV.IEEE.ORG
Subject: Re: [PSES] Machinery Leakage Current

 

Mike, et al,         Thanx for mentioning my name; by now you should be able to 
tell the stories as we’ve talked thru these things before.  

 

               From my experience, protection is primarily needed for cord and 
plug connected equipment where the earthing/grounding is not considered 
reliable – which includes North America.  Most such equipment is allowed to 
have higher touch current under fault conditions, where the fault current 
exceeds 5ma the GFCI provides the needed protection

 

               Since GFCIs look for the ‘lost to ground current’, the 
differential current in the power cord, they also work in circumstances where 
the earth/ground doesn’t exist  (a 2-wire installation) or where it should 
exist but doesn’t.  Many are installed in older 2-wire installations because of 
this in the USA. 

 

               RCDs rated to trip at 30mA are working right at the c1 
Ventricular Fibrillation level of IEC 60479-1 so should provide that protection 
for most people.  

 

               Not sure if RCDs are tested or rated for catching performance 
degradation in machines but you apparently have experience with that.  It would 
be nice to see a paper on that performance feature.  

 

               North American GFCIs are rated at 5mA which is the 
letgo-immobilization limit specified in IEC 60479-1.  (Yes, I know the 
allowable range is not trip at 4mA but must trip at 6mA; the rated trip current 
is still 5mA.)  You can still disengage from the current at that level, 
providing that level of protection.  

 

               Both North American GFCIs and Euro RCDs are not rated to deal 
well with high frequency signals generated by Switch Mode Power Supplies and 
Variable Speed Drives for motors.  Lots of ‘nuisance tripping’ results.  There 
is an ongoing UL project to get a handle on this and get it fixed here in NA.  

 

               Yes, EV chargers are being provided with GFCIs at higher levels, 
depending upon the installation/application parameters. 

 

:>)     br,      Pete

 

Peter E Perkins, PE

Principal Product Safety & Regulatory Affairs Consultant

PO Box 1067

Albany, ORe  97321-0413

 

503/452-1201

 

IEEE Life Fellow

IEEE PSES 2020 Distinguished Lecturer

 <http://www.researchgate.net/Peter%20Perkins> www.researchgate.net search my 
name

 <mailto:p.perk...@ieee.org> p.perk...@ieee.org

 

 

Entropy ain’t what it used to be

 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<emc-p...@ieee.org>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <sdoug...@ieee.org>
Mike Cantwell <mcantw...@ieee.org>

For policy questions, send mail to:
Jim Bacher:  <j.bac...@ieee.org>
David Heald: <dhe...@gmail.com>

Reply via email to