In my experience, a single connection point is risky as it only takes a small amount of corrosion to cause the machine to fail the 60204-1 ground bond test.
Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro, OH | 330-342-2402 From: Ken Javor <ken.ja...@emccompliance.com> Sent: Thursday, 16 June, 2022 6:37 PM To: EMC-PSTC@LISTSERV.IEEE.ORG Subject: Re: [PSES] Removable door panel grounding CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you recognize the sender and know the content is safe. I'm just curious why something like a spring-loaded captive "finger" couldn't be in contact with the door/plate when installed. I'm assuming here the grounding is for safety, not EMI. In the latter case, the gasket approach is necessary. Also, for safety I don't see the gas-tight spot as an issue: a little corrosion or "gunk" between plate and finger would break down in the event of a line-potential fault to the door/access panel. Ken Javor Phone: (256) 650-5261 ________________________________ From: John Cochran <jcoch...@strongarm.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fjcochran%40strongarm.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=qrCfIF6iRNMzdGQW7Yb5PrQjvnUV1T4%2FZAYLCXPFF1c%3D&reserved=0>> Reply-To: John Cochran <jcoch...@strongarm.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fjcochran%40strongarm.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=qrCfIF6iRNMzdGQW7Yb5PrQjvnUV1T4%2FZAYLCXPFF1c%3D&reserved=0>> Date: Thu, 16 Jun 2022 19:52:00 +0000 To: <EMC-PSTC@LISTSERV.IEEE.ORG<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2FEMC-PSTC%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=I6SChk8OAxhZgOVFUiIsIp0mzMmUb%2F%2Fc8lJn2RdAEh0%3D&reserved=0>> Subject: Re: [PSES] Removable door panel grounding >From my knowledge, the access panel will need a ground conductor or metal to >metal contact. The second is more tricky as there can be no electrical >components on the panel and no possibility of a live conductor touch it. I would find a way to keep the ground conductor connected but maybe consider ground studs at opposite corners so it has little slack when closed but allows the panel to be set aside without disconnecting the ground. John Cochran jcoch...@strongarm.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fjcochran%40strongarm.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=qrCfIF6iRNMzdGQW7Yb5PrQjvnUV1T4%2FZAYLCXPFF1c%3D&reserved=0> <mailto:jcoch...@strongarm.com> 215-443-3400 x219 From: Stultz, Mark <00000f79f2e10e47-dmarc-requ...@listserv.ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2F00000f79f2e10e47-dmarc-request%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=fM6RvWWYvuUjgRQuYEOrU78qg85NiIoe2GevdWH5Bys%3D&reserved=0>> Sent: Thursday, June 16, 2022 15:38 To: EMC-PSTC@LISTSERV.IEEE.ORG<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2FEMC-PSTC%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=I6SChk8OAxhZgOVFUiIsIp0mzMmUb%2F%2Fc8lJn2RdAEh0%3D&reserved=0> Subject: Re: [PSES] Removable door panel grounding CAUTION: This message originated from outside Strongarm. Do not open attachments or click on links if you do not recognize the sender. Hi Frank, Can you do a longer ground that allows moving the cover to the side? In my experience it is risky to design a system where the ground is routinely disconnected. If you need to design it that way, I recommend using a braided gasket that is partially compressed when the panel is installed. You'll need the panel and gasket plated so that there is no corrosion that would increase the contact resistance since this arrangement can't be considered gas-tight. Best regards, Mark Stultz | CMSE(r) | Sealed Air | Automated Packaging Systems | Streetsboro, OH | 330-342-2402 From: Frank Tang <00000d3fa4ae712a-dmarc-requ...@listserv.ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2F00000d3fa4ae712a-dmarc-request%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=nZWXnrzwOOff6kGqbo8M1I%2BBYpMsYi%2F3JHoQOfoHZUQ%3D&reserved=0>> Sent: Thursday, 16 June, 2022 3:23 PM To: EMC-PSTC@LISTSERV.IEEE.ORG<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2FEMC-PSTC%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=I6SChk8OAxhZgOVFUiIsIp0mzMmUb%2F%2Fc8lJn2RdAEh0%3D&reserved=0> Subject: [PSES] Removable door panel grounding You don't often get email from 00000d3fa4ae712a-dmarc-requ...@listserv.ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2F00000d3fa4ae712a-dmarc-request%40listserv.ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=nZWXnrzwOOff6kGqbo8M1I%2BBYpMsYi%2F3JHoQOfoHZUQ%3D&reserved=0>. Learn why this is important <https://aka.ms/LearnAboutSenderIdentification> CAUTION: This email originated from outside of the organization. Do not click links or open attachments unless you recognize the sender and know the content is safe. Hi All, In the past we have typically done a stud and nut grounding for removable lift-off access panels, but this is an inconvenience to disconnect the ground cable. What are other methods for grounding large panel doors (3ft x 7ft) if any? -- Thank you and best regards. - Frank - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Femc-pstc%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=BUsDtQr%2BJwFuRaGPVl%2FkHEXIlHwMgEB%2FGHVntRd3EGU%3D&reserved=0>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1G4OU7kkvNCrHRYDfoIhMDsYiUr8DQULJlNkJP8GH4o%3D&reserved=0> <https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C08c36d1e9b45484e6e8508da4fcd9b88%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910041749840006%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kCYBUZ9eiCkvKJTfXcfWnx0fBXLmTN7hyfUqMmg3%2Bc4%3D&reserved=0<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1G4OU7kkvNCrHRYDfoIhMDsYiUr8DQULJlNkJP8GH4o%3D&reserved=0>> Website: http://www.ieee-pses.org/<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=YGQZgs%2F9xQgJLzvefeoPZgIKLsbmjNFPx1%2F4ngc1hHg%3D&reserved=0> <https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C08c36d1e9b45484e6e8508da4fcd9b88%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910041749840006%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=ZHUArJed%2BRerA5uSlON%2BAe95UfnixpX4%2FSZGJunFJz0%3D&reserved=0<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=YGQZgs%2F9xQgJLzvefeoPZgIKLsbmjNFPx1%2F4ngc1hHg%3D&reserved=0>> Instructions: http://www.ieee-pses.org/list.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584124332%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=UBaayV%2BoF1sZGUD1FkeZza29pJ2HgBHZ5EsgfhQdm%2Fc%3D&reserved=0> (including how to unsubscribe) <https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C08c36d1e9b45484e6e8508da4fcd9b88%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910041749840006%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=Qi9GTrZiw0sbVS9XRINZwj8iiJzUpYglR5hR9bcq7uo%3D&reserved=0<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0>> List rules: http://www.ieee-pses.org/listrules.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2FxtYITKlu50l3vmheUteYI6Pa0YAT0uaSH6QdCvnD%2BE%3D&reserved=0> <https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C08c36d1e9b45484e6e8508da4fcd9b88%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910041749840006%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=BL22A18SxgdIge83TVbLu6S32O4Bd36PL9gGGaedb%2BU%3D&reserved=0<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2FxtYITKlu50l3vmheUteYI6Pa0YAT0uaSH6QdCvnD%2BE%3D&reserved=0>> For help, send mail to the list administrators: Mike Cantwell <mcantw...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fmcantwell%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=L8bMMo1avMZbsv3J4GDgR7oRmMdhFKGnfV6Q59A8Bo0%3D&reserved=0>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fj.bacher%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=yxDXrT8uDkRNzQ27Z%2FCo7JDHvtxnMYDyBgCnmeolMn4%3D&reserved=0>> David Heald <dhe...@gmail.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fdheald%40gmail.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=7EpLktkPmi0kF6fko%2FuHdz2z4GyA5UH3ZUsyxWUIFoQ%3D&reserved=0>> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://nam10.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=TZKGXLOYj7DcHNHGYdCtQNqaUn7kE2zNAv%2FP8yxgjVk%3D&reserved=0> - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Femc-pstc%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=9bAWIEEPwiC2AQNOheRde2IxyZCQDBDsvIP4BFSO4nc%3D&reserved=0>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kDMlVWfcHFyaoPAuDhjojiCSYq6%2FOeJCOyWpu52gl0M%3D&reserved=0> Website: http://www.ieee-pses.org/<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=26qY3ye9F%2B1blYTCJC8Fvbjk3ct7mZGKpMEqaGg45lI%3D&reserved=0> Instructions: http://www.ieee-pses.org/list.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0> (including how to unsubscribe) <http://www.ieee-pses.org/list.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0>> List rules: http://www.ieee-pses.org/listrules.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2FxtYITKlu50l3vmheUteYI6Pa0YAT0uaSH6QdCvnD%2BE%3D&reserved=0> For help, send mail to the list administrators: Mike Cantwell <mcantw...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fmcantwell%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=L8bMMo1avMZbsv3J4GDgR7oRmMdhFKGnfV6Q59A8Bo0%3D&reserved=0>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fj.bacher%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=yxDXrT8uDkRNzQ27Z%2FCo7JDHvtxnMYDyBgCnmeolMn4%3D&reserved=0>> David Heald <dhe...@gmail.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fdheald%40gmail.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=7EpLktkPmi0kF6fko%2FuHdz2z4GyA5UH3ZUsyxWUIFoQ%3D&reserved=0>> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://nam10.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=TZKGXLOYj7DcHNHGYdCtQNqaUn7kE2zNAv%2FP8yxgjVk%3D&reserved=0> - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Femc-pstc%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=9bAWIEEPwiC2AQNOheRde2IxyZCQDBDsvIP4BFSO4nc%3D&reserved=0>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kDMlVWfcHFyaoPAuDhjojiCSYq6%2FOeJCOyWpu52gl0M%3D&reserved=0> Website: http://www.ieee-pses.org/<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=26qY3ye9F%2B1blYTCJC8Fvbjk3ct7mZGKpMEqaGg45lI%3D&reserved=0> Instructions: http://www.ieee-pses.org/list.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0> (including how to unsubscribe) <http://www.ieee-pses.org/list.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0>> List rules: http://www.ieee-pses.org/listrules.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2FxtYITKlu50l3vmheUteYI6Pa0YAT0uaSH6QdCvnD%2BE%3D&reserved=0> For help, send mail to the list administrators: Mike Cantwell <mcantw...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fmcantwell%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=L8bMMo1avMZbsv3J4GDgR7oRmMdhFKGnfV6Q59A8Bo0%3D&reserved=0>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fj.bacher%40ieee.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=yxDXrT8uDkRNzQ27Z%2FCo7JDHvtxnMYDyBgCnmeolMn4%3D&reserved=0>> David Heald <dhe...@gmail.com<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fdheald%40gmail.com%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=7EpLktkPmi0kF6fko%2FuHdz2z4GyA5UH3ZUsyxWUIFoQ%3D&reserved=0>> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1<https://nam10.safelinks.protection.outlook.com/?url=https%3A%2F%2Flistserv.ieee.org%2Fcgi-bin%2Fwa%3FSUBED1%3DEMC-PSTC%26A%3D1&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=TZKGXLOYj7DcHNHGYdCtQNqaUn7kE2zNAv%2FP8yxgjVk%3D&reserved=0> - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org<mailto:emc-p...@ieee.org>> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Femc-pstc.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=kDMlVWfcHFyaoPAuDhjojiCSYq6%2FOeJCOyWpu52gl0M%3D&reserved=0> Website: http://www.ieee-pses.org/<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2F&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=26qY3ye9F%2B1blYTCJC8Fvbjk3ct7mZGKpMEqaGg45lI%3D&reserved=0> Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flist.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1CnZntzd39cnbcgjzzWYFTnkharO7noJA7WuUvHTR4c%3D&reserved=0> List rules: http://www.ieee-pses.org/listrules.html<https://nam10.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.ieee-pses.org%2Flistrules.html&data=05%7C01%7Cmark.stultz%40sealedair.com%7C5195441dc5e341a87b6b08da4fe8cf6d%7C2691a2514c384643af0b0c0982f197bd%7C0%7C0%7C637910158584280222%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=%2FxtYITKlu50l3vmheUteYI6Pa0YAT0uaSH6QdCvnD%2BE%3D&reserved=0> For help, send mail to the list administrators: Mike Cantwell <mcantw...@ieee.org<mailto:mcantw...@ieee.org>> For policy questions, send mail to: Jim Bacher <j.bac...@ieee.org<mailto:j.bac...@ieee.org>> David Heald <dhe...@gmail.com<mailto:dhe...@gmail.com>> ________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1 - ---------------------------------------------------------------- This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <emc-p...@ieee.org> All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html Website: http://www.ieee-pses.org/ Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe) List rules: http://www.ieee-pses.org/listrules.html For help, send mail to the list administrators: Mike Cantwell <mcantw...@ieee.org> For policy questions, send mail to: Jim Bacher: <j.bac...@ieee.org> David Heald: <dhe...@gmail.com> _________________________________________________ To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1