On Sat, 3 Oct 2009 23:29:15 +0100, you wrote:

>Are RFI filters for inverters generally incompatible with RCDs? I
>fitted one to my machine today to try to get rid of the noise from the
>VFD which seems to interfere with my encoders and limit switches,
>however every time I power up the VFD the lights go out and the power
>goes off.
>
>The garage and shed are fed though a 30mA RCD (a requirement for power
>to a shed AFAIK) and that seems to take offence to the Filter. The
>filter is marked "nominal leakage curent 20mA" which might be a clue.

I just use a 40A Type 3 MCB, on the circuit for the machines, works
fine. I have a 20A RCD which just goes to one double socket near the
shop door, that's used for outdoor or portable equipment.

Steve Blackmore
--

------------------------------------------------------------------------------