Hubert,

The term PWM as discussed here is referring to the
signal from the parallel port to the device used to
set the motor speed. In the case of the X2 and 
many other DC motor drivers, the current supply
into the motor is also controlled by PWM, but it
is generated and controlled by the motor driver
speed control circuits, not directly by the parallel 
port. The "gain" that Gene referred to is the
ability of the motor driver to regulate the motor
speed under varying mechanical loads. The motor
driver senses the motor back EMF while the PWM
drive is turned off and uses that as a feedback
signal representing the actual motor speed. There
is a small pot within the drive to adjust the "gain"
on this feedback and thus the stiffness of the
speed regulation control loop.

The G540 speed control output is isolated already. I am
not sure if the X2 violates the 12 volt maximum control
voltage imposed by the G540. The signals you need
will be obtained by removing the wires from the pot
in the X2 and connecting them as follows:

Pos 7 VFD GROUND from X2 pot counterclockwise terminal
Pos 8 VFD OUTPUT from X2 pot wiper terminal
Pos 9 VFD +10VDC from X2 pot clockwise terminal

You can check the X2 control voltage by measuring
carefully across the pot with power applied. Remember
that these signals are floating at line voltage!!

You will also need to provide a relay to replace the
switch on the back of the pot. The Output-1 and 
Output-2 terminals on the G540 can drive a suitable
relay, but the relay will require a power source for
its coil because the G540 provides only a transistor
switch to ground.

The X2 motor control is a little unusual. You cannot
just switch the AC mains coming into it to start and
stop the motor. The switch on the back of the pot
must also cycle. Additionally, the motor driver should
not be started at speed, it must be ramped up from
zero or you will blow fuses. The ramping can be
done with HAL. Lastly, if you require reversing, a
large DPDT relay will be needed to swap the motor
leads. This relay can be switched ONLY when the
motor is fully stopped.

Before you start rewiring, I recommend carefully
documenting the connections inside your X2 motor
control box. It is easy to assume that you can
remember where the wires go, but then find that
you had too many things going on and forget.

Regards,
Steve Stallings
www.PMDX.com



> -----Original Message-----
> From: Hubert Bahr [mailto:h...@hbahr.org] 
> Sent: Saturday, October 10, 2009 3:26 AM
> To: Enhanced Machine Controller (EMC)
> Subject: Re: [Emc-users] Spindle Control
> 
> Gene
> When you say micromill are you referring to the X2. I have 
> one of these as well. I am running it with EMC2 though the 
> parallel port with a G540 driver. It accepts a VFD PWM signal 
> and has an op-isolated 0 to 10 volt analog output for a VFD. 
> It also has 2 uncommitted output pins. It looks like I could 
> take the VFD PWM signals in parallel to feed the PMDX-106 or 
> I may not need it if the VFD output will work for the mill 
> motor controller. So how did you hook up the VSD to the PMDX. 
> From a quick review of the PMDX-106 manual you can use the 
> pot to set the speed through the PMDX but it uses an analog 
> voltage out to set the VSD speed. 
> You certainly seem to have put me on the right track. It 
> looks like I need to break out the meter and read the values 
> across the pot. It is starting to look like the G540 already 
> almost everything I need except for the relays and signal 
> conditioning for a sync signal. Reviewing the StepConf 
> portion of the getting started guide makes me believe I have 
> a chance for a first order solution in its spindle control 
> section. Down stream I may want to achieve a more robust 
> solution with something like the Mesa cards.
> 
> Jon
> Warning noted. It looks like my driver may have already 
> considered that and provides an optical isolated output and 
> uses a PWM input.
> 
> Thanks
> Hubert


------------------------------------------------------------------------------
Come build with us! The BlackBerry(R) Developer Conference in SF, CA
is the only developer event you need to attend this year. Jumpstart your
developing skills, take BlackBerry mobile applications to market and stay 
ahead of the curve. Join us from November 9 - 12, 2009. Register now!
http://p.sf.net/sfu/devconference
_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to