andy pugh wrote:
> I think we are discussing different things.
>
> I am saying that if a motor takes 200A per phase on 3 wires out of the
> VFD and that power comes into the VFD on 2 wires, then the current in
> the 2 wires will be more than 200A each.
>   
OK, that is a whole different thing.  Induction motors draw huge 
inductive currents, worse
when idling, better when at full load, but still a lot.

So motor amps time motor volts does NOT equal Watts drawn from the mains.
The VFD recirculates this reactive current, and draws a much better 
power factor
from the mains.  So, in fact, motors running at light load will draw 
MUCH less current from the
mains when run via a VFD!  This is a significant reason industrial users 
use VFDs, it keeps them from getting in trouble with the utility, or 
having to install a huge phase correction bank with automatic controls.

At full load, then what you say will be true.

Jon

------------------------------------------------------------------------------