In my experience, the high-end VFDs also show filters on input and
output.  However, the ones I've taken apart seem to have some output
filtering

On Thu, Jan 28, 2016 at 11:39 AM, Dave Cole <[email protected]> wrote:
> The GS1 and even the GS2 are basic VFDs which do what they say and then
> some.
> I've used them in control boxes with PLCs and PCs but they are usually
> the number 1 noise producers in the panel.
> If you look at their installation instructions they usually include a
> filter on the input of the drive and I believe for European
> installations they say that
> an output filter/choke is required to meet European requirements.
> That makes the inexpensive GS drives not so inexpensive after all of the
> filters are installed.
> On the otherhand, I have used the GS2 drives on some standalone
> installations without a PLC or PC nearby and they have worked fine
> without complications.    However, YMMV.
> The built in PID loop along with a dancer arm and pot can make for a
> really cheap unwinder for reeled products, like rubber extrusions etc.
> Andy doesn't miss much.   I wonder if he is good at picking lottery
> ticket numbers??  ;-)
>
> Dave
>
> On 1/28/2016 9:14 AM, Jim Craig wrote:
>> An update and semi success story.
>>
>> After dinking with the noise from the GS1 VFD for way to many hours. I
>> was finally able to get rid of the noise. I removed the drive. I put in
>> a run capacitor and have the coolant pump running off the original
>> contactor. I wound up using a 3uf capacitor.  I tried a 2uf and it ran
>> but it ran smoother with a 3uf.
>>
>> I can run the machine will all features running and I don't have any
>> noise at all.
>>
>> Based on my experience I would not recommend the GS1 drive at all.
>> However if you have a need for a 1/4hp VFD let me know. I have one I
>> will sell cheap.
>>
>> Thanks for all of the advice.
>>
>> Andy, Does it hurt to be right all the time? LOL!
>>
>> Later,
>>
>> Jim
>>
>> On 1/23/2016 6:22 AM, Dave Cole wrote:
>>> You don't need to disconnect the shields at one end on the power
>>> conductor shields.
>>> Those are normally connected at each end.
>>>
>>> Dave
>>>
>>> On 1/22/2016 5:23 PM, Jim Craig wrote:
>>>> I spent all afternoon looking for and trying to remove ground loops. I
>>>> think I found all that I can eliminate. I have a couple minor ones due
>>>> to the mounting of my PC motherboard/SSD that I don't think I can remove
>>>> without making new mounting fixtures.
>>>>
>>>> I did find one that I was sure was going to fix the issue. My encoder
>>>> breakout board that converts the honda connectors to RJ45 connectors had
>>>> the power ground going to chassis ground due to the mounting bolts. I
>>>> fixed that and removed that ground loop. I was sure that would fix the
>>>> issue but it did not.
>>>>
>>>> Also the shields on the servo motor power cables are grounded at both
>>>> ends in the motor and at the drive side. I disconnected the drive side.
>>>> I am not sure if this is a good idea or not as It could pose a safety
>>>> hazard.
>>>>
>>>> And for everyone's information the encoder cables are shielded, shields
>>>> grounded at the control board only, the signals are differential and I
>>>> am STILL having this issue.
>>>>
>>>> Anyway after all of this the noise is still present when running the GS1
>>>> drive for the coolant pump. I think I will try to source a run capacitor
>>>> and switch back to a contactor for start stop on the coolant pump.
>>>>
>>>> The filter that I am using on the GS1 drive is a Tyco Corcom 5VB1. I
>>>> don't have an operating scope to look at the noise on the lines.
>>>>
>>>> Thanks for the feedback everyone. Should have listened to Andy 6 months
>>>> ago and went with the run capacitor then! ; )         : (
>>>>
>>>> Jim
>>>>
>>>> On 1/22/2016 3:52 PM, Dave Cole wrote:
>>>>> Are you using decent filters??
>>>>>
>>>>> GS1 and GS2 drives tend to pump a lot of RF noise up the power supply 
>>>>> line.
>>>>> I've used the AD filters with good success.   I think the one I used was
>>>>> about $80.
>>>>> If you are using cheap Ebay filters....  sometimes you get what you pay 
>>>>> for.
>>>>>
>>>>> Have you put a scope on your AC lines to see if the filters are
>>>>> effective??  I suspect they are not.
>>>>> Re-routing your drive to motor leads is also sometimes effective.   Keep
>>>>> them as far away from low voltage wiring as possible.
>>>>>
>>>>> Dave
>>>>>
>>>>> On 1/22/2016 12:51 PM, Jim Craig wrote:
>>>>>> Hey all,
>>>>>>
>>>>>> I have been troubleshooting some noise that I have on my servo encoders.
>>>>>> I have isolated the noise source to be the 1/4hp Automation Direct GS1
>>>>>> VFD that I have running my coolant pump. If the coolant pump is not
>>>>>> running then there is no noise on the encoders and the machine maintains
>>>>>> correct positioning. If I turn the coolant pump on then the encoders get
>>>>>> false signal that in turn changes where the machine thinks it is. This
>>>>>> problem showed up immediately after I retrofitted the machine this last
>>>>>> summer. I have just now been able to diagnose where the issue is
>>>>>> originating.
>>>>>>
>>>>>> In attempts to improve the situation I have done the following.
>>>>>>           Installed EMI filters on the supply lines to both the coolant 
>>>>>> and
>>>>>> spindle vfds.
>>>>>>           worked on ground system to try to isolate the noise.
>>>>>>           rerouted the coolant pump motor power cable completely away 
>>>>>> from
>>>>>> any other cables and completely away from the machine.
>>>>>>
>>>>>> All of these things have failed to improve the noise issue.
>>>>>>
>>>>>> I also tried the following to try and diagnose the issue. I disconnected
>>>>>> the coolant pump motor cable from the coolant pump vfd. Disconnected the
>>>>>> spindle motor from the spindle vfd. Connected the coolant pump to the
>>>>>> spindle vfd. Note that the spindle vfd is a 3.0hp Automation direct GS2
>>>>>> drive.
>>>>>>
>>>>>> When I did this and ran the coolant pump via the spindle vfd there was
>>>>>> no noise on the encoders.
>>>>>>
>>>>>> Does anyone have any ideas on how to get rid of this issue.  I really
>>>>>> want to make some parts but I can't with the noise issue.
>>>>>>
>>>>>> I talked to a EE buddy of mine and he mentioned running both motors
>>>>>> (spindle and coolant pump) off the same 3.0hp GS2 drive just to get me
>>>>>> going. What do you think about this? Will running two different sized
>>>>>> motors on the same VFD cause any issue. Right now I don't run my spindle
>>>>>> in reverse so I would not have any trouble with the coolant pump running
>>>>>> backwards.
>>>>>>
>>>>>> I talked to Automation Direct and they said that the GS1 is more prone
>>>>>> to noise than the GS2. I am contemplating getting a 1/2hp GS2 to replace
>>>>>> the GS1.
>>>>>>
>>>>>> So frustrated right now.
>>>>>>
>>>>>> Let me know if you have any ideas.
>>>>>>
>>>>>> Thanks,
>>>>>>
>>>>>> Jim
>>>>>>
>>>>>> ------------------------------------------------------------------------------
>>>>>> Site24x7 APM Insight: Get Deep Visibility into Application Performance
>>>>>> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
>>>>>> Monitor end-to-end web transactions and take corrective actions now
>>>>>> Troubleshoot faster and improve end-user experience. Signup Now!
>>>>>> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
>>>>>> _______________________________________________
>>>>>> Emc-users mailing list
>>>>>> [email protected]
>>>>>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>>>> ------------------------------------------------------------------------------
>>>>> Site24x7 APM Insight: Get Deep Visibility into Application Performance
>>>>> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
>>>>> Monitor end-to-end web transactions and take corrective actions now
>>>>> Troubleshoot faster and improve end-user experience. Signup Now!
>>>>> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
>>>>> _______________________________________________
>>>>> Emc-users mailing list
>>>>> [email protected]
>>>>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>>>>
>>>> ------------------------------------------------------------------------------
>>>> Site24x7 APM Insight: Get Deep Visibility into Application Performance
>>>> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
>>>> Monitor end-to-end web transactions and take corrective actions now
>>>> Troubleshoot faster and improve end-user experience. Signup Now!
>>>> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
>>>> _______________________________________________
>>>> Emc-users mailing list
>>>> [email protected]
>>>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>> ------------------------------------------------------------------------------
>>> Site24x7 APM Insight: Get Deep Visibility into Application Performance
>>> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
>>> Monitor end-to-end web transactions and take corrective actions now
>>> Troubleshoot faster and improve end-user experience. Signup Now!
>>> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
>>> _______________________________________________
>>> Emc-users mailing list
>>> [email protected]
>>> https://lists.sourceforge.net/lists/listinfo/emc-users
>>>
>>
>> ------------------------------------------------------------------------------
>> Site24x7 APM Insight: Get Deep Visibility into Application Performance
>> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
>> Monitor end-to-end web transactions and take corrective actions now
>> Troubleshoot faster and improve end-user experience. Signup Now!
>> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
>> _______________________________________________
>> Emc-users mailing list
>> [email protected]
>> https://lists.sourceforge.net/lists/listinfo/emc-users
>
> ------------------------------------------------------------------------------
> Site24x7 APM Insight: Get Deep Visibility into Application Performance
> APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
> Monitor end-to-end web transactions and take corrective actions now
> Troubleshoot faster and improve end-user experience. Signup Now!
> http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
> _______________________________________________
> Emc-users mailing list
> [email protected]
> https://lists.sourceforge.net/lists/listinfo/emc-users

------------------------------------------------------------------------------
Site24x7 APM Insight: Get Deep Visibility into Application Performance
APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
Monitor end-to-end web transactions and take corrective actions now
Troubleshoot faster and improve end-user experience. Signup Now!
http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to