On Tuesday 02 February 2016 21:29:20 Todd Zuercher wrote:

> These are guesses from the ignorant here; bad breaker (I've bought new
> duds before) or something back feeding into it???
>
I do have a couple more breakers, those skinny duals in a single place 
package.  15's IIRC but both on the same phase.  I'll put one of those 
in tomorrow as a check. But my point is, that at the time the breaker 
trips, no power controlling has actually been done, the SSR's are still 
fired.

I'll scout around and see if I can find another handybox and put that 
power cord on its own breaker while leaving the rest of that controlbox 
on the other 15 amp breaker in that dual package.  That way everything 
will stay on the same leg of the 240 feed from the pole.  Then we'll see 
which breaker trips.  That would be educational in itself.

> ----- Original Message -----
> From: "Gene Heskett" <[email protected]>
> To: [email protected]
> Sent: Tuesday, February 2, 2016 7:14:00 PM
> Subject: Re: [Emc-users] Odd SSR behaviour?
>
> On Monday 01 February 2016 19:09:51 Gene Heskett wrote:
> > On Monday 01 February 2016 17:49:01 John Kasunich wrote:
> > > On Mon, Feb 1, 2016, at 05:31 PM, Gene Heskett wrote:
> > > > Greetings;
> > > >
> > > > Those of you reading the mail know I made a soft start circuit
> > > > for the spindle PSU.
> > > >
> > > > It basically consists of two SSR's in series, the first one
> > > > being the main switch that enables AC power to reach the
> > > > transformer by way of a 51 Ohm 200 watt inrush limiting
> > > > resistor.  And that after the filters are charged, nominally 10
> > > > seconds, a second SSR is fired to short that resistor, allowing
> > > > the supply to make full output. Controlled by a couple timers
> > > > driven by the
> > > > motion.machine_is_on signal.
> > > >
> > > > I had set the timers for a fairly speedy off, with the SSR
> > > > across te resistor being the first one turned off if I unclicked
> > > > the 2nd button, followed 5 seconds later by the first SSR being
> > > > shut down. Sort of a soft stop I guess.
> > > >
> > > > But today in playing with the pyvcp-pannel, I turned it off with
> > > > the 2nd button, and the 20 amp breaker I had put back in the
> > > > service to replace the ill eagle 30 amp dropped instantly.  And
> > > > repeated everytime I stopped it with that button, 100% of the
> > > > time.
> > > >
> > > > I cannot imagine where a momentary short might be.  So I piddled
> > > > with the setp's in the hal file so the softstart SSR was left on
> > > > for about 5 seconds, but the main SSR was disabled in about .5
> > > > seconds, so that main power was disabled before the soft-start
> > > > SSR was disabled.
> > > >
> > > > Now its not tripping the breaker, which is cool.  But the
> > > > question is, why did it trip 100% of the time before I did that?
> > > >
> > > > Other than an SSR surge internal breakdown to the case & sink, I
> > > > cannot come up with a valid reason for that behaviour.
> > >
> > > These have metal baseplates?
> >
> > Yes, bolted to the case, more for solid mounting than any need for a
> > heat sink.  No detectable heat.
> >
> > > Connected to grounded sinks?  You
> > > could rule out a breakdown to sink if you temporarily insulated
> > > the sinks from ground and went back to the old configuration.  A
> > > single breaker trip with the sinks floating would tend to rule out
> > > that possibility.
> > >
> > > Is there ANY path from incoming line to neutral (or the other
> > > phase, if this is a 240V circuit)
> >
> > Upstream of the first SSR is where the switcher supplies for the
> > axis motors are fed.  They come on with the strip switch.  Nothing
> > beyond the SSR's except the transformers, which are identical, 4 of
> > them with primaries paralleled, and each secondary has its own
> > rectifier and filter bank, which are then connected in 2 in series
> > and 2 sets of that paralleled to double the available voltage and
> > double the available current.  Available DC is in the 126 volt
> > range, available current on a 50% duty cycle is about 20-25 amps. 
> > Jon's PWM servo is the driver, set for about a 15 amp current limit.
> >  The servo amp is the only load and it would normally be disabled,
> > drawing essentially zero current when the spindle is stopped.
> >
> > > that doesn't go through the transformer?
> > > If the answer is no (it seems that way from your description), and
> > > the fault current isn't flowing thru the case of the SSR, then it
> > > must be flowing thru the transformer.  The only way the
> > > transformer should draw that kind of current is for a cycle or two
> > > at startup, or if the core saturates due to a large DC component. 
> > > Is it possible that one or both SSRs is only conducting on one
> > > half of the AC waveform?
> >
> > Both tally leds on the SSR's are nice & bright, and the same
> > brightness as its twin when both are enegized.  I haven't looked at
> > it with a scope in about a month & then I could just barely discern
> > the cross-over zero but had to really look close.
> >
> > It appears I have solved the breaker tripping, but I'd sure like to
> > know why.  I have that "waiting for the other shoe to drop" feeling.
> >
> > :(
>
> No, not fixed. The other first shoe is dropping, repeatedly.
>
> And now I am bumfuzzled.  I moved the monitors power cord to a socket
> that doesn't die when that breaker trips.  So I can now watch things
> with a halmeter while I turn it off.
>
> Then I stretched the off times of the SSR driver timers,  to 2.5
> seconds and 5 seconds after I click on the 2nd from the left axis top
> row icon.
>
> The breaker trips milliseconds after I click on the icon, regardless
> of the off times set in the two timers. I can see the breaker is
> tripped, turn my head back to the monitor and the halmeters, and watch
> the signal to both ssr's stop a from a second to 3 later.
>
> I am NOT controlling power to the steppers, they come on and go off
> with a switch on a power strip that controls this whole box full of
> stuff.
>
> I do not see the spindle motor jump, primarily because when the
> spindle is stopped, its completely stopped, disabled and has to have
> the initial bootup sequence generated by the boot module before it is
> re-enabled and capable of driving the spindle, so thats out.  I do not
> hear or see the steppers take a step, I even felt the Z drive
> coupleing, not a twitch.
>
> This whole thing, sitting idle, draws less than 3 amps, 95% of which
> would be the steppers on half power, 2.65 amps I measured once with an
> amprobe, they are just holding position, its a 20 amp breaker.  What
> the heck is tripping it?  Since it is not coincident with turning off
> an ssr, I think that rules out flaky ssr's.
>
> If I had an analog amprobe I might see the needle twitch, but both of
> mine are digital, zero chance of seeing a surge that short.
>
> So, whats the next SWAG everybody?
>
> Cheers, Gene Heskett


Cheers, Gene Heskett
-- 
"There are four boxes to be used in defense of liberty:
 soap, ballot, jury, and ammo. Please use in that order."
-Ed Howdershelt (Author)
Genes Web page <http://geneslinuxbox.net:6309/gene>

------------------------------------------------------------------------------
Site24x7 APM Insight: Get Deep Visibility into Application Performance
APM + Mobile APM + RUM: Monitor 3 App instances at just $35/Month
Monitor end-to-end web transactions and take corrective actions now
Troubleshoot faster and improve end-user experience. Signup Now!
http://pubads.g.doubleclick.net/gampad/clk?id=267308311&iu=/4140
_______________________________________________
Emc-users mailing list
[email protected]
https://lists.sourceforge.net/lists/listinfo/emc-users

Reply via email to