The man page for Mitsub_vfd mentions the required settings. Check the scaling 
of the command.

Chris



Sent from my Galaxy



-------- Original message --------
From: Thaddeus Waldner <thadw...@gmail.com>
Date: 2024-03-01 10:59 a.m. (GMT-08:00)
To: "Enhanced Machine Controller (EMC)" <emc-users@lists.sourceforge.net>
Subject: Re: [Emc-users] Mitsubishi VFD control

I recently set up a Mitsubishi D700 to work with Mitsub_vfd

These inverters are highly flexible in how they are configured to respond to 
control commands. I spent many hours of trial and error to get the correct 
combination of parameters to even get it to respond to network commands. What 
tripped me up initially was that the drive must be reset by cycling the power 
to make any changes take effect.

It has a handy list of all the non-default parameters. I have attached them 
below. Everything appears to work, though there is some inconsistency in how 
manual seed control works in gmoccapy.


The E500 could be a whole different animal but maybe this will help.


pr      name    value
1       Maximum frequency       300
2
Minimum frequency
30
3
Base frequency
300
7       Acceleration time       2.5
8
Deceleration time
3
9
Electronic thermal O/L relay
9
13      Starting speed  20
18      High speed maximum frequency    300
19
Base frequency voltage
200
20
Acceleration/deceleration reference frequency
300
29
Acceleration/deceleration pattern selection
2
41
RUN key rotation direction selection
5
72
PWM frequency selection
15
77      Parameter write selection       2
82      Motor excitation current        80
84
Rated motor frequency
120
96
Auto tuning setting/status
21
117
PU communication station number
96
120
PU communication parity check
0
124
PU communication CR/LF selection
0
160     Extended function display selection     0
298
Frequency search gain
39
340
Communication startup mode selection
1
551
PU mode operation command source selection
4

Hope this helps!,

Thaddeus



> On Mar 1, 2024, at 7:34 AM, lloyd wilson <llwilso...@rochester.rr.com> wrote:
>
> I'm using a Mitsubishi E500 VFD for spindle drive on the VMC I'm retrofitting 
> & can't get variable speed to cooperate. The mitsub_vfd program operates 
> properly (I think)- run/stop behaves as expected, speed commands are 
> generated and accepted by the VFD, but the  motor speed stays the same. I 
> hacked in a couple of debugging statements to show the dialogs (running in 
> halcmd):
>
> setp sp.motor-cmd 50
> halcmd: 01ED11388EF   SENT: 0x5 0x30 0x31 0x45 0x44 0x31 0x31 0x33 0x38 0x38 
> 0x45 0x46
> 7!DEBUG:  ,0,1, 0x6 0x30 0x31
>
> show pins
>
> ........
>
>      4  float IN                     50  sp.motor-cmd
>
> .......
>
>  then
>
> setp sp.motor-cmd 80
> halcmd: 01ED11F40F6   SENT: 0x5 0x30 0x31 0x45 0x44 0x31 0x31 0x46 0x34 0x30 
> 0x46 0x36
> 7!DEBUG:  ,0,1, 0x6 0x30 0x31
>
> show pins
>
> ........
>
>      4  float IN                     80  sp.motor-cmd
>
> .......
>
> the messages are properly formatted per the Mitsub manual & replies show no 
> errors
>
> --but the test motor keeps running at the same speed.
>
> Anyone have a clue where to look for the solution?
>
> as always, thanks
>
> -ldw
>
>
>
> _______________________________________________
> Emc-users mailing list
> Emc-users@lists.sourceforge.net
> https://lists.sourceforge.net/lists/listinfo/emc-users


_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users

_______________________________________________
Emc-users mailing list
Emc-users@lists.sourceforge.net
https://lists.sourceforge.net/lists/listinfo/emc-users