Have you tried putting it in different positions on the slave network?  Perhaps 
it only vanishes when downstream of a particular slave; then the problem might 
be with that slave's configuration.

Etherlab typically assumes that all slaves are configured with DL auto-open 
mode (so that slaves that are connected or rebooted are automatically brought 
into the virtual ring network), but it's possible that one of your upstream 
slaves has been configured in the explicit open mode instead.


Gavin Lambert
Senior Software Developer

[cid:logo_compac_5dcf97ef-52f5-498c-8b9b-728410ddffaf.png]
[cid:compacicon_82e8a8c7-154a-4a32-9720-a5badb6258e0.png]<http://www.compacsort.com>
 [cid:facebook_fa85b924-53b9-45cc-8162-0564f64ec3a3.png] 
<https://www.facebook.com/Compacsort>  
[cid:linkedin_4ec016ad-84fa-443c-85a3-b9615a4ccef8.png] 
<https://www.linkedin.com/company/compac-sorting-equipment/>  
[cid:youtube_32142163-fc27-4aed-b14d-e8a377f98a6d.png] 
<https://vimeo.com/compacsort>  
[cid:twitter_d89338d8-98c8-4b65-9a9e-7b1333160b0d.png] 
<https://twitter.com/compacsort>  
[cid:insta2_1cd85de9-b3a2-4971-9904-52b2481a7c82.png] 
<https://www.instagram.com/compacsort/>

COMPAC SORTING EQUIPMENT LTD | 4 Henderson Pl | Onehunga | Auckland 1061 | New 
Zealand
Switchboard: +64 96 34 00 88 | tomra.com<http://www.tomra.com>

The information contained in this communication and any attachment is 
confidential and may be legally privileged. It should only be read by the 
person(s) to whom it is addressed. If you have received this communication in 
error, please notify the sender and delete the communication.

From: Joachim Sällvin
Sent: Friday, 14 February 2020 22:34
To: etherlab-users@etherlab.org
Subject: [etherlab-users] Slave lost forever after power cycling

Hi all,

I loose contact with my TU4-ECT (freq inverter from Nord Drive) slave after 
power-cycling it when there are other slaves on the bus. This happens 
intermittently. Only a EEPROM reset (I use TwinCAT for this ) can make it 
accessible again. When it is the only slave on the bus it seems as I can 
power-cycle and always access again.

Has anyone experienced the same problem? What might cause this? Workarounds?

Example:

Before power-cycling the TU4-ECT (all slaves have been given alias addresses):


$ sudo ethercat slaves

0  1:0  PREOP  +  EK1100 EtherCAT-Koppler (2A E-Bus)

1  2:0  PREOP  +  EL2004 4K. Dig. Ausgang 24V, 0.5A

2  3:0  PREOP  +  ifm IO-Link Master AL1332

3  4:0  INIT   E  TU4-ECT



After power-cycling the TU4-ECT:



$ sudo ethercat slaves

0  1:0  PREOP  +  EK1100 EtherCAT-Koppler (2A E-Bus)

1  2:0  PREOP  +  EL2004 4K. Dig. Ausgang 24V, 0.5A

2  3:0  PREOP  +  ifm IO-Link Master AL1332

3  8:0  PREOP  +  ifm IO-Link Master AL1332



Lost!!!



I'm using Linux kernel 4.13.13-rt5, Ubuntu 18.04 and EtherCAT master 1.5.2.