If I understand it correctly, the units for INT change to gain/minute in
integral-only control. Therefore if you would like a gain of 0.2 to be
repeated every 4 minutes, you would set INT to 0.05.

I derived this from the following (from the block book):
In PI mode, the PID algorithm uses series:
OUT = [100/(PBAND INT s)] [(SPLLAG INT s+1) SPT - (INT s+1) MEAS]

In I-only, the PID algorithm is as follows:
OUT = [1/(INT s)] [SPT-MEAS]

Regards,
Jason

____
Jason Wright
Regional Technical Specialist
ControlSoft, Inc.
(216) 397-3900 x201

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED]]On Behalf Of JOHN E
ZIEGLER
Sent: Wednesday, August 22, 2001 10:32 AM
To: [EMAIL PROTECTED]
Subject: PIDA Blocks with I-only Control


     Could some provide some insight into using a PIDA block with I-only
     control?  Or a Foxboro reference for this information?

     My big question is how do you set the gain?  Also, I would appreciate
     any other configuration tips people might have.

     Thank you for assistance.

     Jack Ziegler
     Sunoco Chemicals
     Frankford Phenol Plant
     215-537-2455


**********************************************************************
This email and any files transmitted with it are intended
solely for the use of the individual or entity to whom they
are addressed.  If you have received this e-mail in error,
please notify the originator.
**********************************************************************

-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All
postings from this list are the work of list subscribers and no warranty
is made or implied as to the accuracy of any information disseminated
through this medium. By subscribing to this list you agree to hold the
list sponsor(s) blameless for any and all mishaps which might occur due to
your application of information received from this mailing list.

To be removed from this list, send mail to
[EMAIL PROTECTED]
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]



-----------------------------------------------------------------------
This list is neither sponsored nor endorsed by the Foxboro Company. All 
postings from this list are the work of list subscribers and no warranty 
is made or implied as to the accuracy of any information disseminated 
through this medium. By subscribing to this list you agree to hold the 
list sponsor(s) blameless for any and all mishaps which might occur due to 
your application of information received from this mailing list.

To be removed from this list, send mail to 
[EMAIL PROTECTED] 
with "unsubscribe foxboro" in the Subject. Or, send any mail to
[EMAIL PROTECTED]

Reply via email to