chrisdutz commented on issue #1626:
URL: https://github.com/apache/plc4x/issues/1626#issuecomment-2427564421

   Sorry for the late response ... I was stuck in pre-conference work and just 
noticed that you had asked.
   
   So I got some additional information and it seems as if the maximum size of 
a request read from an ADS device is considered to be  16384 bytes. This is not 
defined in the spec itself, but seems to be used throughout multiple 
implementations. 
   So my guess might have been correct, that we need to chunk large symbol- and 
data-type-tables.
   
   I am actually currently working on a new implementation of the ADS driver, 
which is greatly reworked, supports this chunking and which should also support 
lazy resolution of types (so no need to load the entire tables on startup)
   
   However, will this driver most probably not become part of the open-source 
project too soon. If you are still considering using PLC4X you should probably 
ping me directly and I could tell you how we could reach an agreement.
   


-- 