On 3/23/23 10:29, Gert Doering wrote:

"typical" data centres over here have 2 primary feeds, either one
with UPS and one with generator, or both with (different) UPSes - but
depending on the load drawn by a rack, might be presented as multiple
circuits with 16A each, and individual circuit breakers.

Same here, and also what we have seen at most of the larger data centres we work with.


Now, if another device next to your MX960 has a PSU failure and kicks
one of the circuit breakers, what do you want your MX960 to do...  as
well, what do you want to happen if the UPS fails, and one of the primary
feeds goes down.

We typically deploy a full power complement in all our routers to protect against issues such as these, even when we may not necessarily need all that power Day 1.


We do not have MX960s, but we did have other devices with 3 PSUs that
needed 2 to fully power all line cards, and this was quite a bit annoying
- "it says redundant PSUs, but no full feed A / feed B resiliency"...

Even with the 2nd generation high-capacity AC power supplies, the MX960 requires at least 2 power supplies at a minimum, to power the 2 zones in the system.

These power supplies have 2 receptacles per unit, to allow you to drive a full chassis running at speed with just 2 of them in the box. Otherwise, with just a single receptacle per power supply, you only get about half of the energy out of the power supply.

Mark.