Hello Temptanner,

Each front panel object update is called a "message" to the remote
panel server. The client has to be able to keep up with the messages
that the server is sending. There is a maximum message backlog that
the server will allow that is configured with the following setting:

RemotePanel.MaxMsgBacklog =3D n

By default, n =3D 500. You can increase this by adding the above line
manually in your server-side INI file, making n > 500. However, this
will only increase the amount of time before the failure.

The best way to solve this problem is to modify your RT code to reduce
the number of messages being generated in a given amount of time.
Each of your many property nodes generates a relatively large number
of messages. You may need to change the code to only read or write the
property when absolutely necessary, perhaps not every iteration.

Also, if you have a graph that gets updated every iteration of a loop
running at, say, 100 iterations per second, you may consider coding
this so that you accumulate 100 points of data and write it to the
graph only once per second. This actually would apply to any control
or indicator. Perhaps once per second is too slow, but generally you
will need to lower the frequency of the front panel control and
indicator access.

If none of these suggestions help, or if I=92m not correctly
understanding your issue, please post the software and versions you
are using, the applicable portions of your code, and any other
information that may help, and I=92ll be happy to look further into it.

Have a nice day!