David,

Here are some suggestions.

1. For triggering an analog input on every 10th pulse, here is what
you could do.

You could use a counter of the PCI-MIO-16E-1 to generate a pulse train
and use the encoder's signal as the source.  You could use the
'Generate Pulse Train (DAQ-STC) VI' and set the source specification
to 'default PFI line' and set the delay(edges) of the raw counts
control to 5 and the pulse (edges) to 5.  This will basically divide
down the frequency of your signal by 10.  Output pulse train of
counter will be low for 5 periods of your signal and high for 5
periods of your signal.  With regards to connections, you will connect
the encoder signal to the source of the counter you're using.

Now, you can use the pulse train being generated by the counter as an
external clock for your data acquisition.  You can directly connect
the output of the counter to PFI 7 and configure the analog input
acquisition to use an extenal clock.  Refer to the 'Cont Acq&Graph
ExtScanClk VI' example for how to use an external scan clock with
analog input.

With these two examples, for every 10th pulse of the encoder signal,
you will acquire an analog reading from any channel in the scan list.

2. For the frequency measurement, the VI you're using uses two
counters, and so you won't be able to do this along with my first
suggestion.  You could just use the 'Measure Period (DAQ-STC) VI' and
attach the encoder input to the gate of the selected counter.  This VI
will use the internal 20 MHz timebase as a source and will count the
number of 20 MHz pulses between two rising edges of your signal.  So
you could take 20 MHz divided by the count return to determine the
frequency of your signal.

With these two suggestions you should be able to get a good start on
your application.

Let me know if you have any questions.

Regards,

Todd D.
NI Applications Engineer