On Jul 23, 2013, at 9:42 AM, spyros gian <sp.g...@hotmail.com> wrote:

> Dear Dr Zimmerman,
>  
> Running an OPF in matpower means that 
>  
> 1. Bus types play no role (eg slack, PV, PQ etc)
Yes.
> 2. All values for Real Power generation and reactive power generation are 
> unknown
Yes.
> 3. All values for bus_voltages and voltage phase angles in buses, are unknown 
> as well
The voltage angle of the reference bus is fixed and set to 0.
> 4. As a result, all values for real and reactive power flows are unknown. 
Yes.
> 5. Losses are unknown.
Yes.
>  
> What is known : 
> 1. The resistance, reactance, admittance per unit / per conductor 
> 2. Values for Real and Reactive demand at each bus 
> 3. Limits on voltage magnitude , limits on real and reactive power generation
> 4. MVA limits on each line
> 5. Fuel cost for each generator.
Yes for all
>  
> So my question is 
> a. Are the above correct for matpower ? 
> b. Since matpower uses a non-linear optimisation, is the result a local 
> minimum or a global minimum? 
>     (for the case of a cost-minimization OPF) ? i.e. the values for voltages, 
> reactive powers etc, are    
>     globally optimum or perhaps other optimum values for all the unknown 
> quantities exist ? 
I believe most of the optimization tools, such as fmincon in Matlab, find a 
local minimum.

Shri
>  
> Thank you,
> Spyros Gian
>  
>  

Reply via email to