The point of my previous post was that the power flow was doing what you told 
it to (assuming I was correct about you specifying it as a PV bus). If you want 
the power flow to solve for the voltage at the bus, given a specified reactive 
power injection (which is what you seem to be expecting), then you have to 
specify that by changing the BUS_TYPE to PQ in the input data.

-- 
Ray Zimmerman
Senior Research Associate
B30 Warren Hall, Cornell University, Ithaca, NY 14853
phone: (607) 255-9645



On Feb 14, 2014, at 2:35 AM, Mahmoud Abdallah <mahmoud_abdallah2...@yahoo.com> 
wrote:

> dear sir
> 
> this bus has wind thus it can't produce reactive power
> 
> all reactive power comes from the network to  bus 37
> 
> thus the reactive power in the power flow output should be negative  at bus 37
> Eng. Mahmoud abdallah
> Teaching Assistant
> Ain Shams University
> Faculty of Engineering
> 
> 
> On Friday, February 14, 2014 12:53 AM, Ray Zimmerman <r...@cornell.edu> wrote:
> Presumably it is specified as a PV bus, which means that you are asking the 
> power flow program to solve for the reactive power required to maintain the 
> specified voltage magnitude.
> 
>     Ray
> 
> -- 
> Ray Zimmerman
> Senior Research Associate
> B30 Warren Hall, Cornell University, Ithaca, NY 14853
> phone: (607) 255-9645
> 
> 
> 
> On Feb 13, 2014, at 5:36 PM, Mahmoud Abdallah 
> <mahmoud_abdallah2...@yahoo.com> wrote:
> 
>>  dear sir
>> 
>> I use case 39  which has wind at bus 37
>> 
>> the wind at bus 37 has positive active power and negative reactive power
>> 
>> but when I use "runpf"   with change in active power to be 1.5 * its old 
>> value
>> 
>> I find that reactive power (of bus 37) in the result of power flow becomes 
>> positive ??? how
>> 
>> Eng. Mahmoud abdallah
>> Teaching Assistant
>> Ain Shams University