Since we are telling power horror stories…

How about the call from the night operator that arrived at 10:00pm asking “Is 
there any reason there is no power in the data center?”

Turns out someone had plugged in a new high end workgroup laser printer to the 
outside wall of the datacenter. The power receptacle was wired into the data 
center’s UPS and completely smoked the UPS. Luckily the static transfer 
switched worked, but the three mainframes weren’t’ happy…


Or

Our building had a major ground fault issue that took years to find and 
resolve. We got hit with lightning that caused the mainframe to fault and 
recycle…and two minutes in, we got hit by lightning again. When the system 
failed to start, we called IBM support. When we explained what happened there 
was a very long pause…then some mumbling off phone, then the manager got on the 
line and said someone would be flying out and be onsite within 12 hours. We 
were down for 3 days, and got fined $250,000 by the insurance regulators since 
we couldn’t pay claims.

Matthew Huff | Director of Technical Operations | OTA Management LLC

Office: 914-460-4039
mh...@ox.com<mailto:mh...@ox.com> | www.ox.com<http://www.ox.com>
...........................................................................................................................................

From: Chris Kane <ccie14...@gmail.com>
Sent: Friday, September 10, 2021 3:16 PM
To: Christopher Morrow <morrowc.li...@gmail.com>
Cc: Matthew Huff <mh...@ox.com>; nanog@nanog.org
Subject: Re: Never push the Big Red Button (New York City subway failure)

True EPO story; maintenance crew carrying new drywall into the data center 
backed into the EPO that didn't have a cover on it. One of the most eerie 
sounds in networking...a completely silent data center.

-chris

On Fri, Sep 10, 2021 at 2:48 PM Christopher Morrow 
<morrowc.li...@gmail.com<mailto:morrowc.li...@gmail.com>> wrote:


On Fri, Sep 10, 2021 at 1:49 PM Matthew Huff 
<mh...@ox.com<mailto:mh...@ox.com>> wrote:
Reminds me of something that happened about 25 years ago when an elementary 
school visited our data center of the insurance company where I worked. One of 
our operators strategically positioned himself between the kids and the 
mainframe, leaned back and hit it's EPO button.

Or when your building engineering team cuts themselves a new key for the 'main 
breaker' for the facility... and tests it at 2pm on a tuesday.
Or when that same team cuts a second key (gotta have 2 keys!) and tests that 
key on the same 'main breaker' ... at 2pm on the following tuesday.

<quadruple face palm>

not fakenews, a real story from a large building full of gov't employees and 
computers and all manner of 'critical infrastructure' for the agency occupying 
said building.

Matthew Huff | Director of Technical Operations | OTA Management LLC

Office: 914-460-4039
mh...@ox.com<mailto:mh...@ox.com> | www.ox.com<http://www.ox.com>
...........................................................................................................................................

-----Original Message-----
From: NANOG <nanog-bounces+mhuff=ox....@nanog.org<mailto:ox....@nanog.org>> On 
Behalf Of Sean Donelan
Sent: Friday, September 10, 2021 12:38 PM
To: nanog@nanog.org<mailto:nanog@nanog.org>
Subject: Never push the Big Red Button (New York City subway failure)

NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
OUTAGE ISSUE ON AUGUST 29, 2021
Key Findings
September 8, 2021


https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf

Key Findings
[...]

3. Based on the electrical equipment log readings and the manufacturer’s
official assessment, it was determined that the most likely cause of RCC
shutdown was the “Emergency Power Off” button being manually activated.

Secondary Findings

1. The “Emergency Power Off” button did not have a protective cover at the
time of the shutdown or the following WSP investigation.

[...]
Mitigation Steps

1. Set up the electrical equipment Control and Communication systems
properly to stay active so that personnel can monitor RCC electrical
system operations.

[...]


--
Chris Kane