Indeed. Few sounds in the data center haunt me quite as much as a sensation that the decibel level has just decreased significantly.
On Wed, Sep 15, 2021, 4:14 PM Keith Stokes <kei...@salonbiz.com> wrote: > The bigger thing to notice is the *lack* of noise as every server, switch > and storage system spins down. > > --- > > Keith Stokes > > > > On Sep 15, 2021, at 3:50 PM, Stephen Satchell <l...@satchell.net> wrote: > > In the data centers I've worked in over the decades, those Big Red Buttons > would activate a normally-closed contactor in a breaker panel. When pushed, > the contactor would open, and turn off all the circults in said breaker > panel. Not affected are lights, convenience outlets, door locks, and other > non-data loads. Resetting the contactor to the working position was done > after throwing all the breakers to the off position, and then turn on each > breaker, one at a time. > > The only noise that I have ever heard when the Big Red Button was pushed > was the loud BANG as the contactor operated. You hear a similar bang in > movies in scenes where lights in a large area are turned on and off. > > Nothing like the BANG of a 600-amp 3-phase breaker tripping -- experienced > that at University of Illinois Center for Advanced Computation. You > immediately look for the person holding a gun. > > >