yes, you are right. I tried the what you asked and got it working.

I overlooked the "know problems" section, but I think it is not clear
enough. I would never realize from the manual that to keep my ups from
waking up without mains I should use ondelay=0, and stayoff would make it
recycle the power.

If there were a section on the manual with something like this: if you are
having problem when restarting the UPS try to change ondelay = 0,or test
the stayoff flag.

I can write something for the special case of using a TS Shara nobreak, if
you wish.

Thanks


2018-03-02 1:34 GMT-03:00 Daniele Pezzini <[email protected]>:

> 2018-02-28 21:11 GMT+01:00 Jairo Rotava <[email protected]>:
> > Hello,
> >
> > I think that on this file nutdrv_qx_megatec.c the definition for
> > shutdown.stayoff may be wrong. In the file the definition is
> "S%sR0000\r"m
> > while on the megatec protocol description (
> > http://networkupstools.org/protocols/megatec.html) the command is just
> > "S%s\r".
>
> hmm.. no.
> In plain megatec protocol there's no such a thing as 'shutdown and
> stay off' -- the closest thing you can do is call 'SnRm' with an
> incredibly high value for the time to wait before turning on the
> device (i.e. 'SnR9999', using the allowed maximum), while the 'Sn'
> command is meant to tell the device to immediately turn on the load
> when power returns.
> Only some devices support the non-standard 'SnR0000' command and hold
> off the load indefinitely (and it's also stated in nutdrv_qx's
> manpage, 'Known problems' section).
>
> > When I changed it my system was abe to at least stay off, and stopped
> making
> > an instant power recycling.
>
> Try the following things and let's see what happens:
> - 'offdelay=30', 'ondelay=0' (the driver will send 'S.5' to the device),
> - 'offdelay=120', 'ondelay=0' (the driver will send 'S02' to the device),
> - 'offdelay=30', 'ondelay=180' (the driver will send 'S.5R0003' to the
> device),
> - 'offdelay=120', 'ondelay=180' (the driver will send 'S02R0003' to the
> device),
> - 'offdelay=30', 'stayoff' flag (the driver will send 'S.5R0000' to the
> device),
> - 'offdelay=120', 'stayoff' flag (the driver will send 'S02R0000' to
> the device).
>
> >
> > Jairo
>
_______________________________________________
Nut-upsdev mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsdev