# upsrw aixapc
[input.sensitivity]
Input power sensitivity
Type: STRING
Value: medium

[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 139

[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 88

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20


On Wed, Jan 2, 2019 at 9:08 AM, Charles Lepple <clep...@gmail.com> wrote:


Given that we don't have a Back-UPS NS in the compatibility list, and that you have two of the three categories of information on the list already, would you mind if we added this to the DDL? The output of upsrw would be useful for completeness. Also, if you know any of the values from upsc are incorrect, we can note that. For instance, I'm assuming that "battery.date" is incorrect, and the real dates are under "battery.mfr.date" and "ups.mfr.date".

Either that, or APC keeps batteries on the shelf for 10 years before installing them in products...

I suspect that you cannot override the front panel load off switch from USB - but I could hope.