# upscmd -l apc@localhost
Instant commands supported on UPS [apc]:

beeper.disable - Disable the UPS beeper
beeper.enable - Enable the UPS beeper
beeper.mute - Temporarily mute the UPS beeper
beeper.off - Obsolete (use beeper.disable or beeper.mute)
beeper.on - Obsolete (use beeper.enable)
load.off - Turn off the load immediately
load.off.delay - Turn off the load with a delay (seconds)
shutdown.reboot - Shut down the load briefly while rebooting the UPS
shutdown.stop - Stop a shutdown in progress
test.battery.start.deep - Start a deep battery test
test.battery.start.quick - Start a quick battery test
test.battery.stop - Stop the battery test
test.panel.start - Start testing the UPS panel
test.panel.stop - Stop a UPS panel test


On Wed, Jan 2, 2019 at 11:32 AM, Stuart D. Gathman <stu...@gathman.org> wrote:
Here is another XS model:

[root@sampson log]# upsrw apc@localhost
[input.sensitivity]
Input power sensitivity
Type: STRING
Value: medium

[input.transfer.high]
High voltage transfer point (V)
Type: STRING
Value: 139

[input.transfer.low]
Low voltage transfer point (V)
Type: STRING
Value: 88

[ups.delay.shutdown]
Interval to wait after shutdown with delay command (seconds)
Type: STRING
Value: 20

[root@sampson log]# upsc apc@localhost
battery.charge: 100
battery.charge.low: 15
battery.charge.warning: 50
battery.date: 2001/09/25
battery.mfr.date: 2017/04/26
battery.runtime: 2154
battery.runtime.low: 300
battery! .type: PbAc
battery.voltage: 27.2
battery.voltage.nominal: 24.0
device.mfr: American Power Conversion
device.model: Back-UPS XS 1300G
device.serial: 4B1717P20965
device.type: ups
driver.flag.ignorelb: enabled
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.serial: 4B1717P20965
driver.parameter.vendorid: 051d
driver.version: 2.6.5
driver.version.data: APC HID 0.95
driver.version.internal: 0.37
input.sensitivity: medium
input.transfer.high: 139
input.transfer.low: 88
input.voltage: 116.0
input.voltage.nominal: 120
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.firmware: 864.L9 .D
ups.firmware.aux: L9
ups.load: 16
!
ups.mfr: American Power Conversion
ups.mfr.date: 2017/04/26
ups.model: Back-UPS XS 1300G
ups.productid: 0002
ups.realpower.nominal: 780
ups.serial: 4B1717P20965
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: 0
ups.timer.shutdown: -1
ups.vendorid: 051d


On Wed, Jan 2, 2019 at 9:08 AM, Charles Lepple <clep...@gmail.com> wrote:


Given that we don't have a Back-UPS NS in the compatibility list, and that you have two of the three categories of information on the list already, would you mind if we added this to the DDL? The output of upsrw would be useful for completeness. Also, if you know any of the values from upsc are incorrect, we can note that. For instance, I'm assuming that "battery.date" is incorrect, and the real dates are under "battery.mfr.date" and "ups.mfr.date". Other reports: http://new.networkupstools.org/ddl/APC/


_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to