On Thu, 13 Aug 2020, Todd Benivegna wrote:

So I finally got a test in after I changed my RPi to the master and everything else (including my Synology) to slaves.  Before I did that though, I timed the shutdown of my Synology since it is the slowest slave to shutdown.  It took 40 seconds to shutdown, so I changed HOSTSYNC in upsmon.conf on the master (“Proton”) to 60.  I then did a test ("sudo upsmon -c fsd”). The slaves shutdown, then eventually the master, but the Synology never powered down and the UPS powered off which cut the power to it while it was still on.

In Synology's upsmon.conf, they have SHUTDOWNCMD "". Perhaps for correct slave operation this should be SHUTDOWNCMD "shutdown -h +0" or maybe one of the variants which also displays the UPS status and charge such as

 SHUTDOWNCMD "logger -t upsmon.conf \"UPS status at shutdown [$( upsc <myups> ups.status )]:$( 
upsc <myups> battery.charge )\" ; /sbin/shutdown -h +0"

Roger