On Sun, 17 Feb 2008 20:59:41 +0300, Arjen de Korte <[EMAIL PROTECTED]> wrote:
> [...] > >> Asking for UPS status [Q1]... >> get_data_krauler: index [03], prefix [(] >> -> String: UPS No Ack (len = 10/128) >> get_data_krauler: retry [UPS No Ack] >> -> String: UPS No Ack (len = 10/128) >> get_data_krauler: retry [UPS No Ack] >> - Unable to fetch string 3 >> get_data_krauler: connection failure >> Q1 => FAILED [timeout] > > The above is the source of the problems. The first two attempts fail > internally in the UPS (since it reports 'UPS No Ack', which is an > indication that the USB controller in the UPS can't read the status). > Unfortunately, on the third attempt, the USB connection times out which > seems to be handled rather ungracefully. > > The best solution would probably to ignore the first couple of failures in > the 'megatec.c' driver, before declaring data stale. Generally speaking, > one should be careful to declare data stale and only do so after a couple > of attempts to read the status (typically three in a row) have failed. > > Best regards, Arjen I like the idea of solving this in megatec.c. Both serial and usb interfaces could easily fail. -- Alexander _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser