On Jul 10, 2009, at 12.06, Arjen de Korte wrote:
battery.voltage: 55.00
battery.voltage.nominal: 0.00
But here we have located the problem. A 'battery.voltage.nominal'
equal to zero will mean that the calculated
'battery.voltage.minimum' and 'battery.voltage.maximum' will both be
zero. This results in a divide by zero error in the range
calculation. You can work around this by adding
override.battery.voltage.nominal = 48
in 'ups.conf' for these drivers. This will make them ignore the
reported value from the UPS and use the correct nominal value. You
can also set
default.battery.voltage.minimum = 38.4
default.battery.voltage.maximum = 55.2
to preset the minimum and maximum voltage range of the battery,
since neither are reported by the UPS.
aha - thank you, that seems to have done the trick. i suppose that
dividing by zero would also explain the floating point error.
regarding the values you've specified above for the override and
defaults - how are those determined?
What remains is the question if this is a problem in the snmp-ups
driver or the UPS. I honestly don't know.
well, if the output of snmpwalk is any indication, it appears that
snmp-ups is accurately passing on values:
snmpwalk -v1 -c xxxxxxxxxx -m '/usr/share/snmp/mibs/powernet391.mib'
ups4 .1.3.6.1.4.1 | grep -i nominal
PowerNet-MIB::upsAdvBatteryNominalVoltage.0 = INTEGER: 0
it seems this would indicate that the ups isn't interested in
providing this value, right? additionally, i don't see this
information on the ups' own web interface either.