For the record, it ends up to be a misconfiguration:
The powercom driver need the "type" variable to be correctly set.
In this case it is "type = KIN"

Fred


On Tue, 2011-08-02 at 16:23 +0200, Frédéric Bohé wrote:
> On Tue, 2011-07-26 at 15:30 +0300, Павел Гуменюк wrote:
> > After adding COM1 I've got this:
> > 
> > c:\Program Files (x86)\NUT\bin>powercom.exe -DDD -a KIN1500
> > Network UPS Tools - PowerCom protocol UPS driver 0.13
> > (2.6.1-3057:3116M)
> >    0.000000     debug level is '3'
> >    0.000000     w32_serial_open (notUsed)
> >    0.000000     could not open notUsed
> > 
> > Unable to open notUsed: Operation not permitted
> > 
> > Things to try:
> > 
> >  - Check 'port=' in ups.conf
> > 
> >  - Check owner/permissions of all parts of path
> > 
> >    0.015600     Fatal error: unusable configuration
> > 
> > c:\Program Files (x86)\NUT\bin>powercom.exe -DDD -a KIN1500
> > Network UPS Tools - PowerCom protocol UPS driver 0.13
> > (2.6.1-3057:3116M)
> >    0.000000     debug level is '3'
> >    0.000000     w32_serial_open (COM1)
> >    0.015600     setting initial state on COM1
> >    0.015600     00000054 = w32_serial_open (COM1)
> >    0.015600     Warning: no locking method is available: No error
> > [+яхЁрЎш  єёях
> > °эю чртхЁ°хэр. ]
> >    0.031200     vmin_ 0, vtime_ 0
> >    0.140400     action 0
> >    0.140400     vtime 0, vmin 1
> > 
> >    0.140400     ReadTotalTimeoutConstant -2, ReadIntervalTimeout -1,
> > ReadTotalTi
> > meoutMultiplier -1
> >    0.140400     DTR => 0, RTS => 1
> >    0.140400     Values of arguments:
> >    0.140400      manufacturer            : 'PowerCom'
> >    0.140400      model name              : 'Unknown'
> >    0.156000      serial number           : 'Unknown'
> >    0.156000      line voltage            : '230'
> >    0.156000      type                    : 'Trust'
> >    0.156000      number of bytes from UPS: '11'
> >    0.156000      method of flow control  : 'dtr0rts1'
> >    0.156000      validation sequence: '{{5,0},{7,0},{8,0}}'
> >    0.171600      shutdown arguments: '{{0,10},n}'
> >    0.171600      frequency calculation coefficients:
> > '{0.000210,0.000209}'
> >    0.171600      load percentage calculation coefficients:
> > '{6.134300,-0.380800,
> > 4.311000,0.181100}'
> >    0.171600      battery percentage calculation coefficients:
> > '{5.000000,0.32680
> > 0,-825.000000,4.563900,-835.
> > 820007}'
> >    0.187200      voltage calculation coefficients:
> > '{0.954500,0.000000}'
> >    0.343200     data receiving error (validation check)
> >    0.343200     dstate_init: sock \\.\pipe\powercom-KIN1500 open on fd
> > 100
> >    3.432006     data receiving error (0 instead of 11 bytes)
> >    6.442811     data receiving error (0 instead of 11 bytes)
> >    9.453616     data receiving error (0 instead of 11 bytes)
> >   12.464422     data receiving error (0 instead of 11 bytes)
> >   21.668438     data receiving error (0 instead of 11 bytes)
> >   24.679243     data receiving error (0 instead of 11 bytes)
> 
> Hello Pavel,
> 
> Maybe it's a bug in serial drivers. It's hard to be sure since I don't
> have a Powercom UPS for testing. Anyway, I will privately send you an
> experimental binary. If it doesn't fix your issue, please send its
> output on this list using -DDDDD ( five D) for maximum output.
> 
> Fred
> 
> > 
> > c:\Program Files (x86)\NUT\bin>
> > 
> > 
> > 2011/7/19 Павел Гуменюк <[email protected]>
> >         I have only RS-232 on the box (meanwhile, it was manufactured
> >         on march of 2011)
> >         Here is my configs:
> >         
> >         nut.conf:
> >         
> >         
> >         MODE = netserver
> >         
> >         
> >         ups.conf:
> >         
> >         
> >         [KIN1500]
> >                driver = powercom
> >                port = notUsed
> >                desc = "Powercom KING PRO KIN-1500AP RM"
> >         
> >         
> >         
> >         upsd.conf:
> >         
> >         
> >         LISTEN 192.168.1.2 3493
> >         
> >         
> >         
> >         upsd.users:
> >         
> >         
> >         [monuser]
> >                        password = xxxxxxxx
> >                        upsmon master
> >         
> >         
> >         
> >         upsmon.conf:
> >         
> >         
> >         MONITOR [email protected] 1 monuser xxxxxxxx master
> >         MINSUPPLIES 1
> >         SHUTDOWNCMD "C:\\WINDOWS\\system32\\shutdown.exe -s -t 0"
> >         NOTIFYCMD /sbin/upssched
> >         POLLFREQ 5
> >         POLLFREQALERT 5
> >         HOSTSYNC 15
> >         DEADTIME 15
> >         POWERDOWNFLAG "C:\\killpower"
> >         NOTIFYFLAG ONLINE SYSLOG+WALL+EXEC
> >         NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC
> >         NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC
> >         RBWARNTIME 43200
> >         NOCOMMWARNTIME 300
> >         FINALDELAY 5
> >         
> >         
> >         
> >         upssched.conf:
> >         
> >         
> >         CMDSCRIPT /bin/upssched-cmd
> >         AT ONBATT * START-TIMER   onbattwarn 10
> >         AT ONLINE * CANCEL-TIMER  onbattwarn
> >         AT LOWBATT * EXECUTE      lowbattwarn
> >         AT ONBATT * START-TIMER   timeshutdown 100
> >         AT ONLINE * CANCEL-TIMER  timeshutdown
> >         
> >         
> >         After start I can see couple neutral events:
> >         upsd.exe - listening on 192.168.1.2 port 3493.
> >         upsd.exe - User [email protected] logged into UPS [KIN1500].
> >         
> >         Also, there are a lot of errors, such as "upsmon - Poll UPS
> >         [[email protected]] failed - Data stale."
> >         Anybody, please advise how to get it works.
> >         Thanks
> > 
> > _______________________________________________
> > Nut-upsuser mailing list
> > [email protected]
> > http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser
> 
> -- 
> Team Open Source Eaton - http://powerquality.eaton.com
> 
> --------------------------------------------------------------------------
> 
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

-- 
Team Open Source Eaton - http://powerquality.eaton.com

--------------------------------------------------------------------------

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to